<div dir="ltr">All - update for those of you interested, we are starting the portal installation tomorrow (with a Sunny Island for better or worse) and ended up going with a Kohler 14RESA propane generator. This should be 2-wire start, ok at 100% duty cycle 120 v, and CARB compliant. If all goes as planned we'll be up and running next week and I'll keep you posted.<div><br></div><div><a href="http://www.kohlergenerators.com/home-generators/products/14RESA">http://www.kohlergenerators.com/home-generators/products/14RESA</a><br></div><div><br></div><div>-August</div></div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><p><b><span style="font-size:9.0pt;font-family:"Century Gothic","sans-serif"">August Goers</span></b></p><p><span style="font-size:8.0pt;font-family:"Century Gothic","sans-serif"">Luminalt Energy Corporation</span></p><p><span style="font-size:8.0pt;font-family:"Century Gothic","sans-serif"">o: 415.641.4000</span></p><p><span style="font-size:8.0pt;font-family:"Century Gothic","sans-serif"">m: 415.559.1525</span></p>
<p><span style="font-size:8.0pt;font-family:"Century Gothic","sans-serif""><a href="http://www.luminalt.com" target="_blank">www.luminalt.com</a></span></p>
<p> </p></div></div></div>
<br><div class="gmail_quote">On Fri, Jun 23, 2017 at 3:46 PM, Dave Angelini Offgrid Solar <span dir="ltr"><<a href="mailto:offgridsolar@sti.net" target="_blank">offgridsolar@sti.net</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">I did a few projects for Yosemite. Then I used the EU6500i which is now<br>
the EU7000i. Never had anyone ask. and that you will find is the issue. In<br>
my county of Mariposa they will issue a certificate of occupancy on a<br>
house running a generator for final approval. Pretty lax about it all. If<br>
I go across the county line into Tuolumne everything is hard to do. Geeze<br>
an offgrid generator...Use Honda or design so that you don't need one :)<br>
<br>
Dave Angelini / Offgrid Solar<br>
<br>
<br>
> Hi Gary and All –<br>
<span class="">><br>
><br>
><br>
> We looked into the EcoGen unit, but the 6kW is discontinued and the 15kW<br>
> EcoGen is not rated to be sold in California. Bummer.<br>
><br>
><br>
><br>
> Speaking of California, do any of you know about the CARB compliance<br>
> issues<br>
> on selecting a generator for an offgrid renewable project? We had one<br>
> generator rep tell us that only a Tier 4F CARB generators are legal for<br>
> use<br>
</span>> with offgrid in California, but I can’t find anything online to clarify.<br>
<span class="">> Since this project is in the National Parks, we need to make sure we<br>
</span>> don’t<br>
<span class="">> have any compliance issues. If anyone knows anything about what kind of<br>
</span>> CARB compliance is or isn’t required, I’d love to hear about it.<br>
><br>
><br>
><br>
> Cheers!<br>
><br>
><br>
><br>
> August<br>
><br>
><br>
><br>
> *From:* RE-wrenches [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@<wbr>lists.re-wrenches.org</a>] *On<br>
> Behalf Of *Gary Willett<br>
> *Sent:* Friday, June 16, 2017 7:58 AM<br>
> *To:* <a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.<wbr>org</a><br>
> *Subject:* Re: [RE-wrenches] Generator choice for Sunny Island<br>
<span class="">><br>
><br>
><br>
> AUGUST:<br>
><br>
> The Generac EcoGen is dual-fuel capable (NG or LP), comes in 6kW and 15kW<br>
> versions, is 2-wire start, can be field-configured for either 120V or<br>
> 240V.<br>
> It's not "portable" as it does not have wheels. It's transportable though<br>
> based on its footprint and weight. Also, it was specifically designed and<br>
> warranteed for off-grid applications.<br>
><br>
> Regards,<br>
><br>
> Gary Willett PE<br>
> Icarus Engineering LLC<br>
><br>
> On 6/16/17 9:36 AM, Kevin Pegg wrote:<br>
><br>
> You could use a 2 -> 3 wire converter such as the Atkinson GSCM module<br>
> that<br>
> will take the 2 wire output from the SI and convert to 3-wire to control a<br>
> gasoline generator such as the Honda EU7000 series, or Cummins/Onan makes<br>
> a<br>
> good line of gasoline generators. It may be very hard to find a gas<br>
> generator that has 2 wire native remote start. That is more common with<br>
> larger propane or diesel generators.<br>
><br>
><br>
><br>
> Kevin<br>
><br>
><br>
><br>
</span>> *From:* RE-wrenches [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@<wbr>lists.re-wrenches.org</a><br>
> <<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-<wbr>wrenches.org</a>>] *On Behalf Of *August Goers<br>
> *Sent:* June-16-17 7:22 AM<br>
> *To:* RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-<wbr>wrenches.org</a>><br>
> <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-<wbr>wrenches.org</a>><br>
> *Subject:* Re: [RE-wrenches] Generator choice for Sunny Island<br>
<span class="">><br>
><br>
><br>
> Thanks for the good feedback folks!<br>
><br>
><br>
><br>
> We are using a Sunny Island setup because we had access to a free Sunny<br>
> Island and Sunny Boy being scrapped from another site. Otherwise I was<br>
> definitely planning on going with a Outback DC coupled system.<br>
><br>
><br>
><br>
> I think the trick here is trying to find a portable generator that has a<br>
</span>> two-wire start option. I’m looking through the usual genny suppliers and<br>
> nothing has presented itself so far. Anyway, I’ll keep looking and will<br>
> check out Chris’ suggestion on the nexus controller and Generac propane<br>
> unit as well.<br>
><br>
><br>
><br>
> FYI, here is a link to what the portal is like. It’s going in National<br>
<span class="">> Park<br>
> land by the Golden Gate Bridge so I hope we can pull it together!<br>
> <a href="http://www.sharedstudios.com/" rel="noreferrer" target="_blank">http://www.sharedstudios.com/</a><br>
><br>
><br>
><br>
> August<br>
><br>
> Luminalt<br>
><br>
><br>
><br>
><br>
><br>
</span>> *From:* RE-wrenches [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@<wbr>lists.re-wrenches.org</a>] *On<br>
> Behalf Of *Chris Mason<br>
> *Sent:* Friday, June 16, 2017 4:56 AM<br>
> *To:* RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-<wbr>wrenches.org</a>><br>
> *Subject:* Re: [RE-wrenches] Generator choice for Sunny Island<br>
<div><div class="h5">><br>
><br>
><br>
> To my limited mind, the whole 120V sunny island setup is a disaster. Why<br>
> not install a DC coupled 8KW Outback Radian and solve all your problems.<br>
> USe any 240V generator, although finding a 2 wire start gasoline unit may<br>
> be hard. I would use a Nexus controller generac propane generator with<br>
> propane tank, all mounted on the container. I would never design anything<br>
> to use gasoline, it's too dangerous.<br>
><br>
><br>
><br>
> On Fri, Jun 16, 2017 at 7:19 AM, Matthew Sirum <<a href="mailto:matthewsirum@gmail.com">matthewsirum@gmail.com</a>><br>
> wrote:<br>
><br>
> Greetings August,<br>
><br>
> Great thoughts and comments from Brian! I would also suggest speaking<br>
> with the generator manufacturers' tech/engineering folks regarding the<br>
> 120VAC configuration and to confirm 2-wire start set up once you have<br>
> a brand and model or two in mind. Generator parts and service<br>
> availability in the region of the project may also drive brand<br>
> selection. If you need to maximize the inverter's battery charging<br>
> capabilities (depending on battery system charging requirements) you<br>
> may end up needing to look at generators in the 7.5 kW to 8.0 kW<br>
> capacity range to allow for headroom in generator output loading.<br>
><br>
> Also; I am curious how you arrived at an AC coupled design for this<br>
> project. I do not know any of the details or specific projects goals<br>
> you are working with, but I would potentially consider a DC coupled<br>
> system design... DC/DC charge controller(s) would keep the battery<br>
> system charged (and any DC loads operable) even if the Sunny Island<br>
> and/or Sunny Boy(s) have a failure or is taken offline. If most of<br>
> the AC loads are 120VAC I would consider keeping the inverter AC<br>
> output circuit 120VAC and install a dedicated transformer solely for<br>
> the 240VAC load.... Or perhaps consider a 120/240VAC inverter model.<br>
> Depending on the overall situation a DC coupled system could be more<br>
> resilient. The dedicated transformer for the 240VAC load could also<br>
> potentially help make the system more robust. Also; I have spoken<br>
> with a number of folks who have told me they wish the Sunny Island had<br>
> more/better features for generator integration. I'd like to hear more<br>
> from those who have plenty of experience designing and installing<br>
> systems with Sunny Islands and generators to learn what the current<br>
> thoughts and issues are.<br>
><br>
> I hope some of these thoughts may be helpful.<br>
><br>
> Best regards,<br>
><br>
> ----MATT<br>
><br>
> Matthew Sirum<br>
> P.O. Box 1227<br>
> Greenfield, MA 01302-1227 USA<br>
> phone: +1.413.773.0611<br>
> email: <a href="mailto:MatthewSirum@gmail.com">MatthewSirum@gmail.com</a><br>
><br>
><br>
> -------- Original Message Below --------<br>
><br>
> [RE-wrenches] Generator choice for Sunny Island<br>
> August Goers august at <a href="http://luminalt.com" rel="noreferrer" target="_blank">luminalt.com</a><br>
> Thu Jun 15 09:02:41 PDT 2017<br>
><br>
> Hi Wrenches, especially those of you who work on off-grid projects,<br>
><br>
> We have an upcoming off-grid project where we will be powering a storage<br>
> container with electronics in it. The loads are mostly 120 volt but there<br>
</div></div>> is a 240 volt heat pump that might occasionally run. We’re AC coupling<br>
> the<br>
> Sunny Island with a Sunny Boy PV inverter. So, we’ll be installing a<br>
> Outback PSX-240 autoformer to bump the Sunny Island’s output from 120 to<br>
<span class="">> 240 volt.<br>
><br>
> We need to select a generator for backup. We need a two-wire electric<br>
> start<br>
> (in order to be controlled by the Sunny Island) and preferably a generator<br>
> that is okay just running 120 volt loads since the Sunny Islands input is<br>
> only 120 volt. Something in the 3 kVA -7 kVA range should be fine.<br>
><br>
> Does anyone have experience or ideas about what kind of two-wire start<br>
> generator we might select?<br>
><br>
> Thanks,<br>
><br>
> August<br>
><br>
> Luminalt<br>
> ______________________________<wbr>_________________<br>
> List sponsored by Redwood Alliance<br>
><br>
> List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.<wbr>org</a><br>
><br>
> Change listserver email address & settings:<br>
> <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/<wbr>options.cgi/re-wrenches-re-<wbr>wrenches.org</a><br>
><br>
> List-Archive:<br>
> <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/<wbr>re-wrenches@lists.re-wrenches.<wbr>org/maillist.html</a><br>
><br>
> List rules & etiquette:<br>
> <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.<wbr>htm</a><br>
><br>
> Check out or update participant bios:<br>
> <a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
><br>
><br>
><br>
><br>
><br>
> --<br>
><br>
> Chris Mason<br>
><br>
</span>> NABCEP Certified Solar PV Installerâ„¢<br>
<span class="">><br>
> Solar Design Engineer<br>
><br>
> Generac Generators Industrial technician<br>
><br>
><br>
><br>
</span>> <a href="http://www.cometsolar.com" rel="noreferrer" target="_blank">www.cometsolar.com</a> <<a href="http://www.cometenergysystems.com" rel="noreferrer" target="_blank">http://www.<wbr>cometenergysystems.com</a>><br>
<span class="im HOEnZb">><br>
> <a href="tel:264.235.5670" value="+12642355670">264.235.5670</a><br>
><br>
> <a href="tel:869.662.5670" value="+18696625670">869.662.5670</a><br>
><br>
> Skype: netconcepts<br>
><br>
><br>
><br>
><br>
> ______________________________<wbr>_________________<br>
><br>
> List sponsored by Redwood Alliance<br>
><br>
><br>
><br>
> List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.<wbr>org</a><br>
><br>
><br>
><br>
> Change listserver email address & settings:<br>
><br>
> <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/<wbr>options.cgi/re-wrenches-re-<wbr>wrenches.org</a><br>
><br>
><br>
><br>
> List-Archive:<br>
> <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/<wbr>re-wrenches@lists.re-wrenches.<wbr>org/maillist.html</a><br>
><br>
><br>
><br>
> List rules & etiquette:<br>
><br>
> <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.<wbr>htm</a><br>
><br>
><br>
><br>
> Check out or update participant bios:<br>
><br>
> <a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
</span><span class="im HOEnZb">> ______________________________<wbr>_________________<br>
> List sponsored by Redwood Alliance<br>
><br>
> List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.<wbr>org</a><br>
><br>
> Change listserver email address & settings:<br>
> <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/<wbr>options.cgi/re-wrenches-re-<wbr>wrenches.org</a><br>
><br>
> List-Archive:<br>
> <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/<wbr>re-wrenches@lists.re-wrenches.<wbr>org/maillist.html</a><br>
><br>
> List rules & etiquette:<br>
> <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.<wbr>htm</a><br>
><br>
> Check out or update participant bios:<br>
> <a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
><br>
><br>
<br>
<br>
</span><span class="im HOEnZb">Dave Angelini Offgrid Solar<br>
"we go where powerlines don't"<br>
<a href="http://members.sti.net/offgridsolar/" rel="noreferrer" target="_blank">http://members.sti.net/<wbr>offgridsolar/</a><br>
e-mail <a href="mailto:offgridsolar@sti.net">offgridsolar@sti.net</a><br>
text <a href="tel:209%20813%200060" value="+12098130060">209 813 0060</a><br>
<br>
</span><div class="HOEnZb"><div class="h5">______________________________<wbr>_________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.<wbr>org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/<wbr>options.cgi/re-wrenches-re-<wbr>wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/<wbr>re-wrenches@lists.re-wrenches.<wbr>org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.<wbr>htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</div></div></blockquote></div><br></div>