<html><head><meta http-equiv="Content-Type" content="text/html; charset=utf-8"></head><body style="-ms-word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space;"><div><div style="font-family: Calibri,sans-serif; font-size: 11pt;">Not an LB, but  conduit body (straight).<br>This is how Backwoods Solar used to sell the class T fuseholder.<br>Also the code says splices are allowed as long as the conduit body is marked with its volume by the manufacturer.<br><br>Glenn</div></div><div dir="ltr"><hr><span style="font-family: Calibri,sans-serif; font-size: 11pt; font-weight: bold;">From: </span><span style="font-family: Calibri,sans-serif; font-size: 11pt;"><a href="mailto:tump@swnl.net">Tump</a></span><br><span style="font-family: Calibri,sans-serif; font-size: 11pt; font-weight: bold;">Sent: </span><span style="font-family: Calibri,sans-serif; font-size: 11pt;">‎4/‎28/‎2017 8:08</span><br><span style="font-family: Calibri,sans-serif; font-size: 11pt; font-weight: bold;">To: </span><span style="font-family: Calibri,sans-serif; font-size: 11pt;"><a href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</a></span><br><span style="font-family: Calibri,sans-serif; font-size: 11pt; font-weight: bold;">Subject: </span><span style="font-family: Calibri,sans-serif; font-size: 11pt;">Re: [RE-wrenches] Third Radian ---> Class T Fuse With/Without Fuse       Holder</span><br><br></div>I have seen these conduit boxes torch off, like to see and have in free air. Supporting battery cable makes more sense then the hassle of installing this is a LB.<div>T<br><div><div><blockquote type="cite"><div>On Apr 27, 2017, at 7:41 PM, Jerry Shafer <<a href="mailto:jerrysgarage01@gmail.com">jerrysgarage01@gmail.com</a>> wrote:</div><br class="Apple-interchange-newline"><div><div dir="ltr"><div>Wrenches</div><div>In the event you or some else installed a Class T fuse and you want to protect it a little more from cable stress, installing it inside a PVC C conduit body and cover and fastening the cables to the fuse inside that, this will protect the fuse from stress and metallic contact and you can put a label on it stating size and type. </div><div>Jerry</div></div><div class="gmail_extra"><br><div class="gmail_quote">On Wed, Apr 26, 2017 at 6:05 PM, Matthew Sirum <span dir="ltr"><<a href="mailto:matthewsirum@gmail.com" target="_blank">matthewsirum@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin: 0px 0px 0px 0.8ex; padding-left: 1ex; border-left-color: rgb(204, 204, 204); border-left-width: 1px; border-left-style: solid;">Greetings William,<br>
<br>
Good point.  This is something I always take into consideration.  I<br>
have used Class T Fuses in many situations with and without their fuse<br>
holders.  In the case of the installation shown in my custom DC Bus<br>
System pictures the wire/cable type and wire management avoid putting<br>
too much physical stress on the Class T Fuses.  The #4 AWG conductors<br>
are supported from above and apply very little stress on the fuses<br>
they connect to.  The 4/0 AWG cabling is Cobra X-Flex (fine stand,<br>
very flexible) and each of these conductors is secured a few inches<br>
from where they connect to their fuses.  Care was taken in making up<br>
these connection and they were all carefully adjusted and inspected to<br>
ensure they would not stress the fuses.  I feel really good about how<br>
it all came together.  The same care and attention will be needed<br>
whenever these connections are serviced and the fasteners are<br>
torqued/tightened.  When well planned and carefully assembled I do not<br>
have concern there will be any issues related to not using the fuse<br>
holder.  I also think about this another way as well...  Using the<br>
Class T Fuse Holder adds another 2 connections to the circuit.  I try<br>
to remind myself that more connections can equal more chance of<br>
issues...  Although, if a manufacturer of a Class T Fuse states the<br>
fuse holder must be used with their fuse there could be an NEC<br>
violation by not using it.<br>
<br>
One thing to note about the use of these fuses in this installation is<br>
that they are supplemental over current protection (OCP).  Each<br>
positive (ungrounded) conductor connecting to this DC Bus System has a<br>
means of primary over current protection and disconnect on its<br>
opposite end.  The battery systems, the charge controllers, and the<br>
inverter/chargers all have circuit breaker disconnects on their<br>
respective positive circuit conductors connecting to this DC Bus<br>
System.  I have seen other folks build without having the needed<br>
appropriate means of disconnect and OCP; although most folk are<br>
probably more likely to include the primary OCP, but not consider the<br>
</blockquote></div></div></div></blockquote></div></div></div><br><div>[The entire original message is not included.]</div></body></html>