    <p>Here's a thermal image from a recent inspection of 2 v Trojan
      L16REs.  Notice the normal batteries above and below, they are
      cool blue, running around 75F</p>
    <p>2 of the cells of the center battery are obviously shorted.  Cell
      voltage was 2.07 v compared to about 2.3 to 2.4 v for surrounding
      good batteries.  Dead cells are much easier to find on 6 v
      batteries.  I wouldn't have found this without the Flir 167. </p>
    <p><img src="cid:part1.380964B6.12781A76@solarray.com" alt=""></p>
    <p>About 1/4 of the batteries in this set had hot cells; 25 -30 deg
      F warmer. Obviously time for some fresh lead.   Owner couldn't
      recall how old the set was, he thought 2 to 4 years.  Rated at
      1000 cycles to 80% DOD, these Trojan RE batteries should do much
      better than that.  I have never been impressed with L16s anyway. 
      John, my experience has also been: higher Capacity = more
      premature cell failures.<br>
    </p>
    <pre class="moz-signature" cols="72">R. Ray Walters
Chief Technical Officer, RemoteSolar.com
BS Mech Engineering, 1988
Former NABCEP Certified, 2004-2016
Licensed Master ELectrician, Colorado
303 505-8760</pre>
    <div class="moz-cite-prefix">On 4/26/17 2:09 PM, John Blittersdorf
      wrote:<br>
    </div>
    <blockquote
cite="mid:CALp43SSG8vR83Qhd_HQsXV5UzLEb-on-sJ=GOpHyBaTA3hjOBg@mail.gmail.com"
      type="cite">
      <div dir="ltr">Wallace,
        <div>   I installed some Interstate RE batteries (green case)
          L16's that supposedly are made by US Battery.  As with Trojan
          and other High Capacity L16's I had several cell failures.  I
          have always felt that gleaning more amp hours from the same
          box must lead to cutting corners on robustness.  I have found
          that often when the batteries are full, they work OK for
          awhile but as the voltage drops and the current flow rises,
          the cell will eventually drop out.  Other adjacent batteries
          in the string often overcharge to compensate.  In my case with
          the green batteries, they were about 2 years old as well.  I
          took them back to my distributor and replaced them with
          standard L16's at a special pro rated price. I have found that
          all lead acid batteries that have problems seem to first have
          a cell failure somewhere along the line and finally the
          capacity diminishes to the point that it is an annoyance. 
          Seems  bad cells seem more numerous lately.</div>
        <div><br>
        </div>
        <div>John Blittersdorf</div>
        <div>Rob Stubbins Solar</div>
        <div><br>
        </div>
        <div> </div>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Wed, Apr 26, 2017 at 11:54 AM,
          Wallace Stahle <span dir="ltr"><<a moz-do-not-send="true"
              href="mailto:wstahle@pacific.net" target="_blank">wstahle@pacific.net</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">Hi Folks,<br>
            <br>
            I was called by a customer with the complaint of the MS4024
            inverter shut down and ME-ARC controller and Trimetric
            acting strange, intermittent and even even showing 29 volts
            at times.<br>
            <br>
            The batteries are four 2.5 year old US battery L16XC 380 AH
            and checking each battery showed one at 4.8 v under charge
            while the other three were at 7+ volts and no current.<br>
            <br>
            Meanwhile the specific gravity was high on all cells and
            even a week after removal are up at 1.275 on all three
            cells.<br>
            <br>
            I suspect an open in the cell interconnects with enough
            continuity to read volts but not conduct current.<br>
            <br>
            My question is what have any of you seen n this regard and
            any knowledge of cause of such a failure.<br>
            <br>
            Your insights and experience are greatly appreciated.<br>
            <br>
            They were installed by others and are out of warranty. I
            donated a serviceable used USB L16 to get her back to a
            working system.<br>
            She did recall her Ex stating along the lines of "oh this
            one has a problem but dont worry, it'll come around" as they
            were installed.<br>
            <br>
            Many thanks,<br>
            <br>
            Wallace Stahle<br>
            Future Electric Energy Co<br>
            P O Box 236<br>
            Willits, CA 95490<br>
            <a moz-do-not-send="true" href="mailto:future@pacific.net">future@pacific.net</a><br>
            CA Lic.# C10-762093<br>
            <a moz-do-not-send="true" href="tel:707-459-0474"
              value="+17074590474">707-459-0474</a><br>
            <br>
            <br>
            <br>
            <br>
            ______________________________<wbr>_________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.<wbr>org</a><br>
            <br>
            Change listserver email address & settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
              rel="noreferrer" target="_blank">http://lists.re-wrenches.org/<wbr>options.cgi/re-wrenches-re-<wbr>wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
              rel="noreferrer" target="_blank">http://www.mail-archive.com/<wbr>re-wrenches@lists.re-wrenches.<wbr>org/maillist.html</a><br>
            <br>
            List rules & etiquette:<br>
            <a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm"
              rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.<wbr>htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org" rel="noreferrer"
              target="_blank">www.members.re-wrenches.org</a><br>
            <br>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>