A 120/240 V split phase system is supplied by a center tapped 240 V
transformer. The center tap is grounded, deriving the neutral. Unbalanced
current from the two hot phase conductors return back through the
neutral. <br><br>
<br>
At 08:27 PM 11/25/2016, you wrote:<br>
<blockquote type=cite class=cite cite="">Wrenches,<br>
Is there such a thing as a "grid neutral"? I have been
providing design support to a client for a large off grid system; a
prepper, rare in these parts. He claims that utility current is carried
in part through the ground and in part through a neutral conductor, and
such a "utility neutral" is deliberately undersized. At first I
pushed back (see below). Now I just wonder what Wrenches more
knowledgeable than I am will say.<br>
Thank you,<br>
Allan<br><br>
<b>Allan Sindelar</b><br>
<a href="mailto:allan@sindelarsolar.com">allan@sindelarsolar.com</a><br>
NABCEP Certified PV Installation Professional<br>
NABCEP Certified Technical Sales Professional<br>
New Mexico EE98J Journeyman Electrician<br>
Founder (Retired), Positive Energy, Inc.<br>
<b>505 780-2738 cell</b><br><br>
-------- Forwarded Message -------- <br>
Date: Thu, 24 Nov 2016 11:25:36 -0700 <br><br>
Allan<br>
Happy thanksgiving. Sorry for the slow reply; overwhelmed here.<br>
 <br>
All wet sorry. If you look at the power lines you will see two or three
wires at top of pole and the one smaller one a little ways down the pole.
This is the power station neutral.<br>
 <br>
The hots bidirectional is an explanation that helps people understand
current but is not totally clear.<br>
Even if you use that visualization in order for the electrons on the hot
to oscillate they heed a path to oscillate into and out of<br>
That is the “neutral”. <br>
 <br>
Bottom line is from the power station and in your home you have at least
one hot and one neutral.<br>
You can actually use the hot to light up a lite bulb by connecting the
other side of the lite bulb to the earth.<br>
This one way you can get electrocuted.<br>
I touched the hot side of a 220 circuit and the current went thru me and
into the earth…not much fun.<br>
 <br>
This has been openly publicly discussed and one of the electrical
association advised the power companies to increase the size of the
neutral to solve many issues, such as cows giving less milk and problems
with electric current in homes. The power companies even openly discuss
this.<br>
 <br>
In <b>remote rural areas</b> of Australia, I have seen electricity
distribution using SWER (Single-Wire Earth Return); just one wire is fed
to the property at a high voltage, with the current returning via the
ground.  At the property, a transformer turns the high voltage into
normal residential voltages on a pair of wires (230VAC in Australia vs
2x115V in some other countries). But this SWER system is inefficient, and
the supply voltage is poorly regulated; it is a rare exception - it is
only done because of the high cost of delivering two wires in remote
areas.<br>
 <br>
In <b>metropolitan areas</b>, you will typically see 4 wires passing down
the street. This consists of three phases of "Active", plus a
"Neutral". You could <i>imagine</i> the Active carrying current
"from" the power grid, and the Neutral carrying the current
"back to" the power grid (even though the current flow is
symmetrical).<br>
 <br>
There is lots of info online if you wish to learn more about this.<br>
Take care, Robert<br>
 <br>
<b>From:</b> Allan Sindelar
[<a href="mailto:allan@sindelarsolar.com">
mailto:allan@sindelarsolar.com</a>] <br>
<b>Sent:</b> Sunday, October 23, 2016 10:18 PM<br>
 <br>
Robert,<br>
I'm neither an electrical engineer or a utility employee, so I may be all
wet here, and if so please dry me off with a straight-up explanation. But
this whole argument seems specious to me, as it addresses a "grid
neutral". <br><br>
My reasoning is this - there is no such animal as a "grid
neutral" in utility lines, so how is this issue even relevant? The
"hots" are bidirectional; only when the utility power is
stepped down at the transformer at the home is a reference neutral
created. To say that the current "cannot all go back thru the
neutral since it is not large enough BY DESIGN" seems to me an
absurd concept since there is no neutral in utility power distribution.
<br><br>
Am I missing something?<br>
Allan<br><br>
On 10/2/2016 7:51 PM, Robert wrote:<br>

<dl>
<dd>Allan <br>

<dd>Here is the info I said I would send:
<a href="https://www.youtube.com/watch?v=aJOB2FIqUiQ">
https://www.youtube.com/watch?v=aJOB2FIqUiQ</a></u>. Listen about 20
minutes at least.<br>

<dd> <br>

<dd>All current that goes “out” on the two residential or three
commercial hots goes back on the grid neutral <br>

<dd>AND thru the ground'. It cannot all go back thru the neutral since it
is not large enough  BY DESIGN. So…. That means we really don’t have
a clean ground anymore.<br>

<dd> <br>

<dd>Thank you for your time today. It is enjoyable to speak with
you.<br><br>

</dl>_______________________________________________<br>
List sponsored by Redwood Alliance<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" eudora="autourl">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote>
<br /><br />
<hr style='border:none; color:#909090; background-color:#B0B0B0; height: 1px; width: 99%;' />
<table style='border-collapse:collapse;border:none;'>
        <tr>
                <td style='border:none;padding:0px 15px 0px 8px'>
                        <a href="https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient">
                                <img border=0 src="http://static.avast.com/emails/avast-mail-stamp.png" alt="Avast logo" />
                        </a>
                </td>
                <td>
                        <p style='color:#3d4d5a; font-family:"Calibri","Verdana","Arial","Helvetica"; font-size:12pt;'>
                                This email has been checked for viruses by Avast antivirus software.
                                <br><a href="https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient">www.avast.com</a>
                        </p>
                </td>
        </tr>
</table>
<br />
</body>
</html>