Electrical noise coming in from the utility side can also cause an arc
fault code.<br><br>
At 07:32 AM 11/11/2016, you wrote:<br>
<blockquote type=cite class=cite cite="">This array is a ground mount, so
not on a roof, and no radio towers nearby.<br><br>
As for grounding, The array and the shed with the interconnection point
are in the same area.<br>
There are a couple ground rods there, which everything on the AC side is
connected to, <br>
including a #6 wire from each inverter. there is just a #10 ground coming
from the array to the inverters. <br>
The house is a couple hundred feet away and has its own grounding
electrode system.<br><br>
Jerry,<br>
The inverters are new (replaced 2 months ago), but it is a good idea to
check firmware.<br>
As for AC loads, nothing stands out as the types of things you mentioned,
although there<br>
may be a well pump. They also do have a large water storage tank for
heating, but they<br>
say that they have not needed to use it yet this year. Then there is also
the generator...<br><br>
Thanks for your recommendations.<br>
-Dave<br><br>
<br><br>
<font face="arial"><b>--<br><br>
Dave Tedeyan</font><br>
Project Engineer<br>
</b><br>
<b>Taitem Engineering, PC<br>
</b>109 S. Albany Street, Ithaca, NY 14850<br>
Voice: <a href="??">(607) 277-1118 x121</a><br>
<a href="http://www.taitem.com/">www.taitem.com</a><br>
<br>
On Thu, Nov 10, 2016 at 9:51 PM, Jerry Shafer
<<a href="mailto:jerrysgarage01@gmail.com">jerrysgarage01@gmail.com</a>
> wrote:<br>

<dl>
<dd>Dave.<br>

<dd>We have many TL-22 in the field and they will detect faults even when
they are normal contactor faults, have you made sure the SW is the
latest, last I checked it is 2.65.3R and it may have a patch in there,
you can turn off the feature for testing only and see if you melt
something down but if you do please be on site as a arc may happen. Do
you have a well, AC system with contacts, welders, compressors, anything
that has a dry contacts that brakes under load, this is another place I
would look. Every time we have had a code out it was real weather from
something normal or a wire issue. Not to brag but we have hundreds in the
field from the 3's to the 24's and as much as I dread getting a call with
this issue I can usually find the problem and it can be either AC or
DC.<font color="#888888"><br>

<dd>Jerry <br>
</font><br>

<dd>On Thu, Nov 10, 2016 at 8:14 AM, Dave Tedeyan
<<a href="mailto:dtedeyan@taitem.com">dtedeyan@taitem.com</a>>
wrote:<br>

<dl>
<dd>Hi All, <br><br>

<dd>Maybe someone will have some ideas for why a couple inverters keep
arc faulting:<br><br>

<dd>-There are two SB7000TL-22 inverters, Sunpower branded.<br>

<dd>-3 Strings of 7 SPR-327's to each inverter. Kept separate until the
inverter.<br>

<dd>-Ground mount about 50' from the shed where the inverters are located
(indoors)<br>

<dd>-Simple grid connected system, no batteries.<br>

<dd>-There is a whole house generator co-located in the shed.<br>

<dd>-We interconnect by using piercing taps on the line side of the
generator transfer switch<br>

<dd>-There has been only one power outage there since the system was
installed in April, but the generator fires up weekly.<br><br>

<dd>-The arc faults have been happening on both inverters. Sometimes only
one at a time, sometimes both will go within a day of each other.<br>

<dd>-The events have been approximately one a month, but sometimes more,
sometimes less.<br><br>

<dd>-We have already checked every single connection in the system twice,
by two different people.<br>

<dd>-We have replaced the underground wires (and they looked just
fine)<br>

<dd>-We have replaced all home runs.<br>

<dd>-We have replaced both inverters.<br>

<dd>-Arc faults are still happening.<br>

<dd>-Arc faults are not always on the same day/time of the week.<br><br>

<dd>I am wondering if this can be caused by the generator? <br>

<dd>Has anyone run into a situation like this or something
similar?<br><br>

<dd>Thanks for your help,<br>

<dd>Dave<br><br>

<dd><font face="arial">--<br><br>

<dd>Dave Tedeyan</font><br>

<dd>Project Engineer<br>
</b><br>

<dd>Taitem Engineering, PC<br>
</b>
<dd>109 S. Albany Street, Ithaca, NY 14850<br>

<dd>Voice: <a href="??">(607) 277-1118 x121</a><br>

<dd><a href="http://www.taitem.com/">www.taitem.com</a><br>
<br>

<dd>_______________________________________________<br>

<dd>List sponsored by Redwood Alliance<br><br>

<dd>List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>

<dd>Change listserver email address & settings:<br>

<dd>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>

<dd>List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>

<dd>List rules & etiquette:<br>

<dd><a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>

<dd>Check out or update participant bios:<br>

<dd><a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a><br><br>
<br>

</dl><br><br>

<dd>_______________________________________________<br>

<dd>List sponsored by Redwood Alliance<br><br>

<dd>List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>

<dd>Change listserver email address & settings:<br>

<dd>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>

<dd>List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>

<dd>List rules & etiquette:<br>

<dd><a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>

<dd>Check out or update participant bios:<br>

<dd><a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a><br><br>
<br>

</dl><br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" eudora="autourl">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote>
<br /><br />
<hr style='border:none; color:#909090; background-color:#B0B0B0; height: 1px; width: 99%;' />
<table style='border-collapse:collapse;border:none;'>
        <tr>
                <td style='border:none;padding:0px 15px 0px 8px'>
                        <a href="https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient">
                                <img border=0 src="http://static.avast.com/emails/avast-mail-stamp.png" alt="Avast logo" />
                        </a>
                </td>
                <td>
                        <p style='color:#3d4d5a; font-family:"Calibri","Verdana","Arial","Helvetica"; font-size:12pt;'>
                                This email has been checked for viruses by Avast antivirus software.
                                <br><a href="https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient">www.avast.com</a>
                        </p>
                </td>
        </tr>
</table>
<br />
</body>
</html>