<div dir="ltr"><div><div><div><div><div><div><div><div><div><div><div><div><div><div><div>Wrenches<br></div>We are getting some questions from PRMD some questions relating to 690.8 here is what we have<br></div>3 modules, 260 watts at 9 amps ISC each module is a single string which <br></div>goes into a MNPV6 disco/combiner/disconnect<br></div>combined to a 30 amp breaker, it is being replaced with a 40 amp per 690.8(A) 1<br></div>leaves there and goes to a 32 amp disconnect in our device.<br></div>here is where it gets interesting <br></div>690.8 (A) requires the 40 amp breaker but reading down to 690.8 (B) 1 we <br></div>need to up-size to 50 amps (no 45 amp is non available)<br></div>We also have added the 63 amp GFI in the disco<br></div>we have also moved up from # 10 wire to # 8 wire as a result<br></div>All this seams over kill for three modules, there are 2 exceptions but PRMD do <br></div>not feel they are relative.<br></div>Is the Midnite solar disco considered an assembly with the bus bars inside if we install the breakers<br></div>Any ideas would be helpful<br></div>Jerry<br><div><div><div><br><div><div><div><div> <br></div></div></div></div></div></div></div></div>