<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;">I realize this is potentially a stupid question, and one that is long overdue, but here goes:</div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;"> </div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;">Why in 690(B) are we setting a minimum threshold on OCPD when we're protecting <span style="text-decoration: underline;">against</span> over current?</div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;"> </div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;">Shouldn't we be setting a maximum threshold...as is done in pretty much all other cases? The way I see it, we should take the array/inverter max output AC current and multiply by 125% to set our min ampacity on <span style="text-decoration: underline;">wire</span>,</div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;">and then calc down to find the breaker trade size that lands between the max AC output current and max AC output current times 125%. That way, we avoid nuisance tripping but achieve the max overcurrent protection possible.</div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;">By following 690(B) we're actually decreasing OCP: Literally, 690(B) is stating that we can have a breaker 100x over the circuit rating, so long as it's not under the circuit rating times 1.25. To me this seems antilogical.</div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;"> </div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;">Mr. Brooks?</div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;"> </div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;">690.9(B) Overcurrent Device Ratings. Overcurrent device ratings</div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;"><span style="text-decoration: underline;">shall be not less than 125 percent</span> of the maximum</div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;">currents calculated in 690.8(A).</div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;"> </div>
<div class="gmail_default" style="color: #222222; font-family: garamond, serif; font-size: large; background-color: #ffffff;">
<div class="gmail_default">455.7(B)...The overcurrent protection determined</div>
<div class="gmail_default">from this section <span style="text-decoration: underline;">shall not exceed 125 percent</span> of the</div>
<div class="gmail_default">phase converter nameplate single-phase input amperes.</div>
<div class="gmail_default"> </div>
<div class="gmail_default">
<div class="gmail_default">
<div class="gmail_default">450.4(A)...Such overcurrent device</div>
<div class="gmail_default">shall be rated or set at <span style="text-decoration: underline;">not more than 125 percent</span> of</div>
<div class="gmail_default">the rated full-load input current of the autotransformer.</div>
</div>
<div class="gmail_default"> </div>
<div class="gmail_default">450.5(A)(2) Overcurrent Protection. An overcurrent sensing device</div>
<div class="gmail_default">shall be provided that will cause the main switch or commontrip</div>
<div class="gmail_default">overcurrent protection referred to in 450.5(A)(1) to open if</div>
<div class="gmail_default">the load on the autotransformer <span style="text-decoration: underline;">reaches or exceeds 125 percent</span></div>
<div class="gmail_default">of its continuous current per-phase or neutral rating.</div>
<div class="gmail_default"> </div>
<div class="gmail_default">450.5(B)(2)(b) Ampere Rating. The overcurrent protection shall be</div>
<div class="gmail_default">rated or set at a current <span style="text-decoration: underline;">not exceeding 125 percent</span> of the </div>
<div class="gmail_default">autotransformer continuous per-phase current rating or</div>
<div class="gmail_default">
<div class="gmail_default">42 percent of the continuous-current rating of any seriesconnected</div>
<div class="gmail_default">devices in the autotransformer neutral connection.</div>