    <p>Maverick:</p>
    <p>Thanks for responding. You've been very helpful in the past with
      my battery based solution questions.</p>
    <p>Daily load demand from the Protected Loads Panel is about 10kWh.
      <br>
    </p>
    <p>With 5 average daily peak sun hours, and 75% charging efficiency,
      the battery bank will receive about 13kWh of solar charging per
      day. The battery bank will be sized for 2 days of autonomy to 80%
      DoD (2 or 3 strings of 200RE batteries). A 6kW generator, which
      will be manually controlled, will provide charging assistance if
      the solar charging alone is not sufficient.</p>
    <p>The 10kW (ac) SE inverter and associated 10.7kWp PV array, using
      the "Power Reduction Control" function, would be limited to about
      3.5kW (ac). </p>
    <p>Sizing the inverter and battery bank is not my issue - cranking
      back the output power of the SE grid-tied inverter is what I need
      help on.</p>
    <p>The "standard" Outback GSLC solution uses one "Power Reduction
      Control" relay (100% to 0%). I want to use two Outback activated
      relays, and the SE inverter's "Power Reduction Control" function
      to:</p>
    <blockquote>
      <p>(1) reduce the SE inverter power from 100% to 30% when the grid
        is down (relay #1)<br>
      </p>
      <p>(2) reduce the SE inverter power from 30% to 0% when the Radian
        wants to totally shut down the SE inverter (relay #2)<br>
      </p>
    </blockquote>
    <p>If this two-relay solution is possible, I do not have to kluge up
      a way to disconnect 70% of the PV array when the grid is down to
      keep the SE10000A-US inverter from overloading the 4kW Radian
      inverter and its battery bank.</p>
    <p>Regards,<br class="">
      <br class="">
      Gary Willett<br class="">
      Icarus Engineering / Solar Services LLC</p>
    <div class="moz-cite-prefix">On 10/18/16 9:23 AM, Maverick Brown
      wrote:<br>
    </div>
    <blockquote
      cite="mid:893D41E1-B97A-479D-A966-7404C37154AB@mavericksolar.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      How many kWh are you shooting for?
      <div class=""><br class="">
      </div>
      <div class=""> <br class="">
        <div>
          <blockquote type="cite" class="">
            <div class="">On Oct 17, 2016, at 9:54 PM, Gary Willett <<a
                moz-do-not-send="true"
                href="mailto:Gary@icarussolarservices.com" class="">Gary@IcarusSolarServices.com</a>>
              wrote:</div>
            <br class="Apple-interchange-newline">
            <div class="">
              <meta http-equiv="content-type" content="text/html;
                charset=windows-1252" class="">
              <div bgcolor="#FFFFFF" text="#000000" class=""> Esteemed
                Wrenches:<br class="">
                <br class="">
                Anyone have experience setting up AC coupling with
                SolarEdge and the Outback Radian?<br class="">
                <br class="">
                I have a client with a SolarEdge SE10000A-US inverter,
                equipped with 31 SunPower X21-345 modules (10.7kWp) and
                associated SolarEdge P400 DC optimizers. The DC
                optimizers are arranged into two strings of series
                connected optimizers: #1 = 16;  #2 = 15.<br class="">
                <br class="">
                The client wants to add a limited battery backup
                solution, and a 4kW inverter will serve the needs of the
                requisite protected loads panel.<br class="">
                <br class="">
                I am considering using the Outback Radian GS4048A
                inverter in conjunction with the GSLC175-AC-120/240
                AC-Coupling Center.<br class="">
                <br class="">
                I want to make a slight change to the PRI programming on
                the SolarEdge inverter, and add another relay contact to
                the Radian, to accommodate a 4kW Outback inverter AC
                coupled to a 10kW SolarEdge inverter.<br class="">
                <br class="">
                This is my first AC coupling project with these systems.
                The analysis below is based solely on review of
                available documents on the Outback and SolarEdge web
                sites. <br class="">
                <br class="">
                Any help or guidance will be greatly appreciated.<br
                  class="">
                <br class="">
                Regards,<br class="">
                <br class="">
                Gary Willett<br class="">
                Icarus Engineering / Solar Services LLC<br class="">
                <br class="">
                <u class="">References</u>:<br class="">
                <blockquote class="">(1) <u class="">Outback
                    Application Note "</u><u class=""><i class="">AC
                      Coupling OutBack Power Radian Inverters with
                      SolarEdge N. American Inverters</i></u><u class="">"</u><br
                    class="">
                  <a moz-do-not-send="true"
                    class="moz-txt-link-freetext"
href="http://www.outbackpower.com/downloads/documents/technotes/ac_coupling_tech_note.pdf">http://www.outbackpower.com/downloads/documents/technotes/ac_coupling_tech_note.pdf</a><br
                    class="">
                  <br class="">
                  (2) <u class="">Outback Application Note "</u><u
                    class=""><i class="">Adding the battery back-up
                      power option to existing grid-tied PV/solar
                      systems</i>"</u><br class="">
                  <a moz-do-not-send="true"
                    class="moz-txt-link-freetext"
href="http://www.outbackpower.com/downloads/documents/flexcoupled/app_note_acc_new.pdf">http://www.outbackpower.com/downloads/documents/flexcoupled/app_note_acc_new.pdf</a><br
                    class="">
                  <br class="">
                  <meta http-equiv="Content-Type" content="text/html;
                    charset=windows-1252" class="">
                  <title class=""></title>
                  (3) <u class="">SolarEdge Application Note </u><i
                    class=""><u class="">"SolarEdge Inverters, Power
                      Control Options"</u></i><br class="">
                  <a moz-do-not-send="true"
                    class="moz-txt-link-freetext"
href="http://www.solaredge.com/sites/default/files/application_note_power_control_configuration.pdf">http://www.solaredge.com/sites/default/files/application_note_power_control_configuration.pdf</a><br
                    class="">
                </blockquote>
                <u class=""><u class="">REF (2); Page 9 of 14</u> -
                  Outback's AC Coupling Guideline Number Two</u>: <br
                  class="">
                <blockquote class="">The OutBack inverter power rating
                  should be 1.25% of the GT inverter power rating. This
                  guideline ensures that the GT inverter does not
                  overwhelm the charging circuitry in the OutBack
                  inverter if the load demand goes to zero and all
                  available GT inverter power is flowing to the OutBack
                  inverter.<br class="">
                  <br class="">
                  With the 4kW GS4048A inverter, the PV power rating is
                  therefore limited to 3.2kW. This is 30% of the
                  nameplate rating of the PV array (3.2/10.7).<br
                    class="">
                </blockquote>
                <u class="">REF (3); Page 4 of 5</u><u class=""> - </u><u
                  class="">SolarEdge/OutBack Radian Wiring Diagram</u>:<br
                  class="">
                <blockquote class="">On the male connector that fits
                  into the PRI connector on the SolarEdge PCB, two wires
                  are connected from the OutBack GSLC load center 12V
                  relay (OBR-16-DIN). <br class="">
                </blockquote>
                <blockquote class=""> When activated, a normally open
                  contact (NO) of the Outback OBR-16-DIN 12V relay
                  supplies +5V from "pin 8" to "pin 6" of the SolarEdge
                  inverter's "Power Reduction Interface (PRI) port". <br
                    class="">
                </blockquote>
                <u class="">REF (1); Page 3 of 5</u><u class=""> - </u><u
                  class="">SolarEdge Setup / Programming</u>:<br
                  class="">
                <blockquote class="">Per the App Note, when the Radian
                  wants to shut down the SolarEdge, the OBR-16-DIN 12V
                  relay is activated and a "1" is applied to bit 1 of
                  the PRI. This takes the SolarEdge output power, in a
                  gradual manner, from 100% to 0%.<br class="">
                </blockquote>
                <blockquote class="">
                  <blockquote class=""><u class="">"DEFAULT" SolarEdge
                      Programming</u><br class="">
                    0000 <100,1,00,Y> ----meaning = 100% power,
                    1.00 power factor, point is active<br class="">
                    0001 <0,1.00,Y> ----meaning = 0% power, 1.00
                    power factor, point is active<br class="">
                  </blockquote>
                  For my project, when the grid is down, the SolarEdge
                  inverter must be limited to 30% power. I want to use
                  the second NO/NC contact on the OBR-16-DIN 12V relay
                  to accomplish this. Not yet sure exactly how to
                  accomplish this in the Radian programming, but here's
                  how I want it to function:<br class="">
                  <blockquote class="">(a) when the grid is down, the
                    second OBR contact, connected to bit 2 of the PRI,
                    is activated and a "1" is applied to bit 2. This
                    takes the SolarEdge output power, in a gradual
                    manner, from 100% to 30%.<br class="">
                    <br class="">
                    (b) when the Radian wants to shut down the
                    SolarEdge, a "1" is applied to bit 1. This takes the
                    SolarEdge output power, in a gradual manner, from
                    30% to 0%.</blockquote>
                  <blockquote class=""><u class="">"PROPOSED" SolarEdge
                      Programming</u><br class="">
                    0000 <100,1,00,Y> ----meaning = 100% power,
                    1.00 power factor, point is active<br class="">
                    0001 <0,1.00,Y> ----meaning = 0% power, 1.00
                    power factor, point is active<br class="">
                    0010 <30,1.00,Y> ----meaning = 30% power, 1.00
                    power factor, point is active<br class="">
                    0011 <0,1.00,Y> ----meaning = 0% power, 1.00
                    power factor, point is active<br class="">
                  </blockquote>
                  Is this doable?<br class="">
                  <br class="">
                </blockquote>
                <br class="">
              </div>
              _______________________________________________<br
                class="">
              List sponsored by Redwood Alliance<br class="">
              <br class="">
              List Address: <a moz-do-not-send="true"
                href="mailto:RE-wrenches@lists.re-wrenches.org" class="">RE-wrenches@lists.re-wrenches.org</a><br
                class="">
              <br class="">
              Change listserver email address & settings:<br
                class="">
              <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                class="">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br
                class="">
              <br class="">
              List-Archive:
<a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br
                class="">
              <br class="">
              List rules & etiquette:<br class="">
              <a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br class="">
              <br class="">
              Check out or update participant bios:<br class="">
              <a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br class="">
              <br class="">
            </div>
          </blockquote>
        </div>
        <br class="">
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>