<div dir="ltr">Hey Wrenches-<div>Just a heads up on the SMA Tripower - I like the inverter, but you gotta read the install manual!</div><div><br></div><div>Spec sheet says 24 A continuous output current for the 20 kW Tripower.  Install manual (and tech support) says 24.1.  That  extra .1 A takes you from a 30 A to a 35 A breaker.</div><div><br></div><div>Of course you should follow the install manual not the specs.  But what about the label on the side of the inverter?  Well I've seen more than a handful that are labeled with a flat-out 24 Aac output current.  What's an installer or inspector to do besides hope mfg's can get their numbers in order?</div><div><br></div><div>Upon closer examination, most of the STPs are 0.1 A higher than their spec sheet per the install manual - it doesn't really make a difference on the 12 or 15 kW models - just the 20 where you have to go up 1 standard OCPD size.  Pretty sure there's lots of 20 kW units out there backfeeding a 30 A breaker.  Hmmmmm....<br clear="all"><div><div class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><br></div><div>Brian Mehalic <br>NABCEP Certified Solar PV Installation Professional™ R031508-59</div><div>520.204.6639<br><div><br></div><div><div><div>Solar Energy International<br><a href="http://www.solarenergy.org" target="_blank">http://www.solarenergy.org</a></div></div></div></div><div><br></div><div>SEI Professional Services</div><div><a href="http://www.seisolarpros.com" target="_blank"><span style="font-size:12.8px">http://www.s</span>eisolarpros.com</a><br></div><div><br></div></div></div></div></div></div></div></div>