You can isolate the neural bar and ground the equipment grounding system
to a grounding electrode. <br><br>
At 06:46 PM 6/11/2016, you wrote:<br>
<blockquote type=cite class=cite cite="">Since you don't name the
inverter OEM, I'm just guessing, but.....the ground to neutral bond thing
can indeed fry what I call "truck top" AKA "portable"
inverters. The puzzling thing in my experience is it can take 6
months......1 month.....1 week......1 second for the failure. Or it might
work fine (but not be to code).<br><br>
My rule....to connect to a standard AC load panel (no matter how small)
the inverter has to have actual hard-wired AC Out terminals...hot,
neutral and ground. If the only way to connect it to the house AC system
is a 120V AC extension cord with the female end chopped off and hard
wired to the load panel, you are asking for trouble and have left NEC far
behind. I got well-zapped by one these in the past....<br><br>
Dan Fink<br>
Adjunct Professor of Solar Energy Technology, Ecotech Institute<br>
IREC Certified Instructor™ for: <<br>
~ PV Installation Professional<br>
~ Small Wind Installer<br>
Executive Director, Buckville Energy<br>
NABCEP Registered Continuing Education Providers™<br>
<a href="tel:970.672.43422">970.672.4342</a><br><br>
 <br><br>
On Sat, Jun 11, 2016 at 12:58 PM, Travis Jordan
<<a href="mailto:travis@jordansolar.net">travis@jordansolar.net</a>
> wrote:<br>

<dl>
<dd>Just a thought, but some of the old or cheap inverters don't take
nicely to bonding the ground to neutral. You may try leaving the ground
wire disconnected from the inverter for a test and see if that changes
anything.... Also make sure you don't have moisture or a short of some
sort in your output cable to the house, I got involved with a job once
that had normal Romex buried outside and it got wet and caused issues
with the inverter not working properly. It ohmed out fine, but when I
hooked it up it didn't play nice with the inverter. I would suspect
something with the site wiring from what I am understanding from your
post. <br><br>

<dd>Good luck!<br>
<font color="#888888"><br>

<dd>Travis Jordan<br>

<dd><a href="mailto:travis@jordansolar.net">travis@jordansolar.net</a><br>

<dd><a href="mailto:travis@mtsolar.us">travis@mtsolar.us</a><br><br>
<br>

<dd>-- <br>

<dd>Travis Jordan</b><br>

<dd><a href="mailto:travis@jordansolar.net">travis@jordansolar.net</a><br>

<dd><a href="??">877-215-8431, Ext. 104</a></b><br>

<dd>Cell: <a href="??">406-274-1230</a></b><br>

<dd>Jordan Solar</b><br>

<dd><a href="http://www.jordansolar.net/">jordansolar.net</a></b><br>

<dd><a href="http://www.jordansolar.net/">
<img src="http://www.jordansolar.net/wp-content/uploads/2012/08/certified-solar-installer-nabcep.jpg" width=110 height=90 alt="Jordan Solar Logo">
</a><br>

<dd><a href="http://www.nabcep.org/">Solar PV Installer #
031409-69</a><br>

<dd>MT EL License # ELE-EJ-LIC-9886<br>

<dd>WA EL License# TRAVIJE901PK<br>

<dd>ID EL Masters # 010810<br><br>
</font><br>

<dd>_______________________________________________<br>

<dd>List sponsored by Redwood Alliance<br><br>

<dd>List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>

<dd>Change listserver email address & settings:<br>

<dd>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>

<dd>List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>

<dd>List rules & etiquette:<br>

<dd><a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>

<dd>Check out or update participant bios:<br>

<dd><a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a><br><br>
<br>

</dl><br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" eudora="autourl">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br><br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote></body>
</html>