<div dir="ltr">boB, a spongey line on a load? Done it with windmills, never with a load. Makes complete sense to me, I'll add that to the old bag of tricks.</div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><span style="font-size:12.8000001907349px">Dan Fink</span><div style="font-size:12.8000001907349px">Adjunct Professor of Solar Energy Technology, Ecotech Institute</div><div style="font-size:12.8000001907349px">IREC Certified Instructor™ for: </div><div style="font-size:12.8000001907349px">~ PV Installation Professional</div><div style="font-size:12.8000001907349px">~ Small Wind Installer</div><div style="font-size:12.8000001907349px">Executive Director, Buckville Energy</div><div style="font-size:12.8000001907349px">NABCEP Registered Continuing Education Providers™<br><a href="tel:970.672.4342" value="+19706724342" style="color:rgb(17,85,204)" target="_blank">970.672.4342</a></div><br> </div></div></div></div></div></div></div></div></div></div>
<br><div class="gmail_quote">On Mon, May 30, 2016 at 12:54 PM, <a href="mailto:bob@midnitesolar.com">bob@midnitesolar.com</a> <span dir="ltr"><<a href="mailto:bob@midnitesolar.com" target="_blank">bob@midnitesolar.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    <p><br>
    </p>
    <p>The (newer) SW5548 was harder on over current protection, mainly
      because</p>
    <p>it could put out more current than the SW4048... <br>
    </p>
    <p> One trick to try is to place a long(ish) extension cord between
      the SW and the load to give it a wee bit of series resistance.</p>
    <p>Doing this would often reduce that OCP and help motors to start.<span class="HOEnZb"><font color="#888888"><br>
    </font></span></p><span class="HOEnZb"><font color="#888888">
    <p>boB<br>
    </p></font></span><div><div class="h5">
    <br>
    <div>On 5/30/2016 11:03 AM, Dan Fink wrote:<br>
    </div>
    <blockquote type="cite">
      <div dir="ltr">Does your air compressor have an unloader valve, or
        can you install one?
        <div>That should do the trick, sounds like you are just running
          into the regular high surge current demand.</div>
        <div>Off the grid, compressors are in about the same nasty
          league as old well pumps as far as surge demand.</div>
        <div><br>
        </div>
        <div><br>
          <div><br>
          </div>
        </div>
      </div>
      <div class="gmail_extra"><br clear="all">
        <div>
          <div data-smartmail="gmail_signature">
            <div dir="ltr">
              <div>
                <div dir="ltr">
                  <div>
                    <div dir="ltr">
                      <div>
                        <div dir="ltr">
                          <div><span style="font-size:12.8000001907349px">Dan
                              Fink</span>
                            <div style="font-size:12.8000001907349px">Adjunct
                              Professor of Solar Energy Technology,
                              Ecotech Institute</div>
                            <div style="font-size:12.8000001907349px">IREC
                              Certified Instructor™ for: </div>
                            <div style="font-size:12.8000001907349px">~
                              PV Installation Professional</div>
                            <div style="font-size:12.8000001907349px">~
                              Small Wind Installer</div>
                            <div style="font-size:12.8000001907349px">Executive
                              Director, Buckville Energy</div>
                            <div style="font-size:12.8000001907349px">NABCEP
                              Registered Continuing Education Providers™<br>
                              <a href="tel:970.672.4342" value="+19706724342" style="color:rgb(17,85,204)" target="_blank">970.672.4342</a></div>
                            <br>
                             </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
        <br>
        <div class="gmail_quote">On Mon, May 30, 2016 at 10:46 AM,
          Jeremy Rodriguez <span dir="ltr"><<a href="mailto:allsolarjeremy@msn.com" target="_blank"></a><a href="mailto:allsolarjeremy@msn.com" target="_blank">allsolarjeremy@msn.com</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Hello<br>
            I've got an SW+5548 that will barley start my air
            compressor. Once it does run it shows 17 Amps on the
            inverters loads meter. During start up it reads 60+ amps.<br>
            Do you think better capacitors would help the situation?<br>
            BTW I've never ran the compressor off grid prior.<br>
            I even tried #8 from the Breaker to the pressure switch,
            about 9ft, with no benefit. The compressor will only start
            with the tank completely empty.<br>
            <br>
            Jeremy Rodriguez<br>
            Solar Installation And Design Expert<br>
            All Solar, Inc.<br>
            1463 M St<br>
            Penrose Colorado 81240<br>
            <br>
            Sent by Jeremy's iPhone. Sorry for typos and shorthand!<br>
            _______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address & settings:<br>
            <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
            <br>
            List rules & etiquette:<br>
            <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
            <br>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset></fieldset>
      <br>
      <pre>_______________________________________________
List sponsored by Redwood Alliance

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </div></div></div>

<br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div>