    <p>The (newer) SW5548 was harder on over current protection, mainly
      because</p>
    <p>it could put out more current than the SW4048... <br>
    </p>
    <p> One trick to try is to place a long(ish) extension cord between
      the SW and the load to give it a wee bit of series resistance.</p>
    <p>Doing this would often reduce that OCP and help motors to start.<br>
    </p>
    <p>boB<br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 5/30/2016 11:03 AM, Dan Fink wrote:<br>
    </div>
    <blockquote
cite="mid:CAF+3Lncg+BzMN86GdqgM7eyK8DDWB6EMqAd7VEyJiSBD8nZquA@mail.gmail.com"
      type="cite">
      <div dir="ltr">Does your air compressor have an unloader valve, or
        can you install one?
        <div>That should do the trick, sounds like you are just running
          into the regular high surge current demand.</div>
        <div>Off the grid, compressors are in about the same nasty
          league as old well pumps as far as surge demand.</div>
        <div><br>
        </div>
        <div><br>
          <div><br>
          </div>
        </div>
      </div>
      <div class="gmail_extra"><br clear="all">
        <div>
          <div class="gmail_signature" data-smartmail="gmail_signature">
            <div dir="ltr">
              <div>
                <div dir="ltr">
                  <div>
                    <div dir="ltr">
                      <div>
                        <div dir="ltr">
                          <div><span
                              style="font-size:12.8000001907349px">Dan
                              Fink</span>
                            <div style="font-size:12.8000001907349px">Adjunct
                              Professor of Solar Energy Technology,
                              Ecotech Institute</div>
                            <div style="font-size:12.8000001907349px">IREC
                              Certified Instructor™ for: </div>
                            <div style="font-size:12.8000001907349px">~
                              PV Installation Professional</div>
                            <div style="font-size:12.8000001907349px">~
                              Small Wind Installer</div>
                            <div style="font-size:12.8000001907349px">Executive
                              Director, Buckville Energy</div>
                            <div style="font-size:12.8000001907349px">NABCEP
                              Registered Continuing Education Providers™<br>
                              <a moz-do-not-send="true"
                                href="tel:970.672.4342"
                                value="+19706724342"
                                style="color:rgb(17,85,204)"
                                target="_blank">970.672.4342</a></div>
                            <br>
                             </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
        <br>
        <div class="gmail_quote">On Mon, May 30, 2016 at 10:46 AM,
          Jeremy Rodriguez <span dir="ltr"><<a
              moz-do-not-send="true"
              href="mailto:allsolarjeremy@msn.com" target="_blank"><a class="moz-txt-link-abbreviated" href="mailto:allsolarjeremy@msn.com">allsolarjeremy@msn.com</a></a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">Hello<br>
            I've got an SW+5548 that will barley start my air
            compressor. Once it does run it shows 17 Amps on the
            inverters loads meter. During start up it reads 60+ amps.<br>
            Do you think better capacitors would help the situation?<br>
            BTW I've never ran the compressor off grid prior.<br>
            I even tried #8 from the Breaker to the pressure switch,
            about 9ft, with no benefit. The compressor will only start
            with the tank completely empty.<br>
            <br>
            Jeremy Rodriguez<br>
            Solar Installation And Design Expert<br>
            All Solar, Inc.<br>
            1463 M St<br>
            Penrose Colorado 81240<br>
            <br>
            Sent by Jeremy's iPhone. Sorry for typos and shorthand!<br>
            _______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address & settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
              rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
              rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
            <br>
            List rules & etiquette:<br>
            <a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm"
              rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org" rel="noreferrer"
              target="_blank">www.members.re-wrenches.org</a><br>
            <br>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>