<p dir="ltr">I resonate with Lonus' point on generator run time without the charger being on, I see no point...</p>
<p dir="ltr">One of my many "oops" stories on this topic: I set up a customer on DC gen to "solve" a problem about ten years ago in the mountains of N Idaho and the following scenario occurred:</p>
<p dir="ltr">1) The generator charger got accidentally turned off by a "helpful" caretaker trying to reset an error on the Mate after he started the generator because the batteries were low.</p>
<p dir="ltr">2) The panels were covered with snow,</p>
<p dir="ltr">3) The customer was gone for the winter and the system was unattended</p>
<p dir="ltr">4) The DC Gen option did not have "max run time"</p>
<p dir="ltr">5) Two weeks of incessant run time later the generator got turned off manually by the caretaker, the batteries were still not charged, and the LARGE fuel tank was almost empty.</p>
<p dir="ltr">Point learned? Think through a few scenarios when I deviate from "normal" Outback generator settings in the future!</p>
<p dir="ltr">This story has obvious connections to the post earlier about what to do with batteries when the system is unattended, I followed that discussion intently and agree with what has been said... I only offer this in reference to the generator charger discussion.</p>