<div dir="ltr">Propane generator expert here - certified Generac technician.<div><br><div>Chances are the problem lies with the fuel supply. Your inverter is working better, taking more power, putting more current into the batteries. Therefore the generator, which is well within it's rating, is taking more fuel.<div>99% of propane generator problems are improperly specified or installed propane or NatGas supply. Most people don't read the manual, and the requirements are always more than people realize.</div></div></div><div>An 8KW propane unit will need a 3/4" line or more to develop full power. If the fuel is being starved, it will run rough. It will only happen under load.</div><div>Get hold of a manometer and measure the gas pressure at the internal regulator. You should see a steady 11" WC for propane or 7" WC for NatGas. Measure under load. If the pressure drops, there's your problem.</div></div><div class="gmail_extra"><br><div class="gmail_quote">On Thu, Apr 21, 2016 at 3:40 PM, Chris Daum <span dir="ltr"><<a href="mailto:chris@oasismontana.com" target="_blank">chris@oasismontana.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"> Dear people:<br>
<br>
I have an off-grid customer who has, in his system, a Magnum MS4448 and 16<br>
of the Rolls S550 batteries, a Kohler generator (and Trimetric meter and<br>
other components).  He upgraded his batteries this past March, and since<br>
he's installed his new batteries, the generator is running 'rough'.  He's at<br>
a great distance from our shop so a local business helps him from time to<br>
time. They believe that the "batteries are too  powerful for the 8.5 kw<br>
generator" and recommended  running it at 50 percent charge control. After 3<br>
hrs run, it seems to help but will mean more run time for his generator (and<br>
hence, use more fuel).  Have you ever heard of anything like this?<br>
Everything ran fund before the battery upgrade.<br>
<br>
Thanks for your input!<br>
<br>
Best,<br>
<br>
Chris Daum<br>
Oasis Montana Inc.<br>
<a href="tel:406-777-4309" value="+14067774309">406-777-4309</a><br>
<a href="tel:406-777-0830" value="+14067770830">406-777-0830</a> fax<br>
<a href="http://www.oasismontana.com" rel="noreferrer" target="_blank">www.oasismontana.com</a><br>
<br>
<br>
<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div><br><br clear="all"><div><br></div>-- <br><div class="gmail_signature"><div dir="ltr">Chris Mason<div><div style="color:rgb(136,136,136)"><span style="font-size:13px">NABCEP Certified Solar PV Installer™</span></div><div style="color:rgb(136,136,136)"><span style="color:rgb(34,34,34)">Solar Design Engineer</span></div><div style="color:rgb(136,136,136)"><span style="font-size:13px">Generac Generators Industrial technician</span></div></div><div style="color:rgb(136,136,136)"><span style="font-size:13px"><br></span></div><div><a href="http://www.cometenergysystems.com" target="_blank">www.cometsolar.com</a></div><div>264.235.5670</div><div>869.662.5670</div><div>Skype: netconcepts</div></div></div>
</div>