Bill said one thing we ALL need to listen to, that is untill someone asked it appears the renewable energy industry was not at the table. We need all to be asking why and asking for change, also asking the AHJ where it is and to clearify, sometimes thats all it takes. I bet  that of who was at the table there may have bern no one that does off grid or battery based systems and having inverter manufactures would also help. I have systems that pump water in the event of a fire, its needs to run or why is it there.<br>
Thats my additional two cents </p>
<div class="gmail_quote">On Mar 15, 2016 5:01 AM, "Ray Walters" <<a href="mailto:ray@solarray.com">ray@solarray.com</a>> wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Greetings Esteemed Wrenches:<br>
<br>
I've just heard back from our inspector here in Colorado, and we are still being required to disconnect the batteries under 690.12.  No where in 690.12 are batteries mentioned, nor in the appropriate 690.71 section that deals with batteries.  The entire reasoning behind this is based on a single article written by a single person: Bill Brooks.  I have contacted both Outback and Magnum on this issue, and their engineers are unaware that rapid shutdown applies.<br>
My interpretation is that I could install an inverter and battery system that was charged from a generator, and we would not need any rapid shutdown at all.  But according to Bill, as soon as I put a single solar module into the system, suddenly the entire system becomes PV? The problem lies with the term 'PV System circuit'  used in 690.12.  690.2 Defines 'PV Output circuit', and 'PV source circuit', but there is no 'PV system circuit' defined.  690.12 therefore uses an undefined term.<br>
Our design uses 2 inverters, so if we used Midnite's E panel with their remote trip breakers, the 2nd inverter would be more than 5 ft from the batteries.  If we used Magnum or Outback DC disconnects (that would comply with the 5 ft rule specified in 690.71) they don't offer remote trip.<br>
We have a Midnite Rapid disconnect Combiner on the roof with the Birdhouse, so we are complying with 690.12, it should not be applied to batteries though.<br>
<br>
Thanks,<br>
<br>
-- <br>
R.Ray Walters<br>
CTO, Solarray, Inc<br>
Nabcep Certified PV Installer,<br>
Licensed Master Electrician<br>
Solar Design Engineer<br>
<a href="tel:303%20505-8760" value="+13035058760" target="_blank">303 505-8760</a><br>
<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>