    Hi Pat;<br>
    <br>
    HI Pat;<br>
    <br>
    No disrespect in either direction.  I always appreciate everyone's
    views.<br>
    Larry's Gigavac solenoid looks good too, but my read of 690.71 looks
    like I still need an OCPD within 5 ft of the batteries, as well.   
    <br>
    I'm already using substantial Midnite products for the actual "PV
    Circuit" Rapid Disconnect, so I will probably do further "cobbling"
    with their RT Breakers and enclosures to meet the battery side
    requirements.  <br>
    It still is amazing that this is not being addressed by any of the
    inverter manufacturers.  But hey, I'm just some hippy Drumpf brain
    from no where's ville, so what do I know?<br>
    <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer since 1986
303 505-8760</pre>
    <div class="moz-cite-prefix">On 3/15/2016 3:54 PM, Patrick A.
      Shortell wrote:<br>
    </div>
    <blockquote
      cite="mid:1F840C6C-0A50-40E8-887D-D69BF4DF5FA3@gmail.com"
      type="cite">
      <meta http-equiv="content-type" content="text/html;
        charset=windows-1252">
      <div>Hi Ray</div>
      <div>Well you got me there</div>
      <div>I meant no disrespect to you personally.</div>
      <div>I think as a whole the code making panels do their best to
        keep up.</div>
      <div>If I missed some of the particulars</div>
      <div>Please excuse me.</div>
      <div>And I guess it would be more useful to offer a workable
        solution</div>
      <div>Maybe I've missed some of the details but doesn't mid nite
        offer a shunt trip breaker as part of their ebox that works with
        the birdhouse</div>
      <div>I've used one in the past</div>
      <div>Is it not ul listed</div>
      <div>That's all from me</div>
      <div>Pat<br>
        <br>
        <div>Patrick A. Shortell
          <div>Licensed Master Electrician</div>
          <div>Certified Solar Installer</div>
          <div>71 Oregon Street</div>
          <div>Long Beach N.Y. 11561</div>
          <div><a moz-do-not-send="true"
              href="http://www.thesolarstorehouse.com">Www.thesolarstorehouse.com</a></div>
          <div><br>
          </div>
        </div>
      </div>
      <div><br>
        On Mar 15, 2016, at 5:16 PM, Ray Walters <<a
          moz-do-not-send="true" href="mailto:ray@solarray.com"><a class="moz-txt-link-abbreviated" href="mailto:ray@solarray.com">ray@solarray.com</a></a>>
        wrote:<br>
        <br>
      </div>
      <blockquote type="cite">
        <div>
          <meta content="text/html; charset=windows-1252"
            http-equiv="Content-Type">
          So Pat, you stated "<i>There are simple ways to work around
            these issues</i>".  Actually, the major off grid inverter
          manus do not have a solution for this ( Magnum, Outback,
          Exeltech, Schneider, SMA)  <br>
          Can you show us an example of a UL listed system that has
          multiple inverters (over 8 kW cont.), with rapid disconnects
          within 5 ft?  I'm really looking for actual solutions here
          folks, and I haven't seen a single system ever built, much
          less even a simple wiring diagram that would comply with this
          new requirement. (<i>690.12(5) Equipment that performs the
            rapid shutdown shall be listed and identified</i>)<br>
          <br>
          Also, for every improvement comes a whole new set of
          problems.  Your "<i>What would I do in my own house?</i>" is
          an excellent point.  Personally, I would not want the
          neighbor's kids to be able to shut off my refrigerator or
          grandma's breathing machine with the touch of an outside
          accessible, unlockable button.<br>
          <br>
          I've been cobbling together code compliant systems for 2
          decades, so yes, I'm sure I could scavenge relays from the EV
          world to do this.  But the days of inventing custom (non UL)
          solutions to meet new requirements should be over.  If this is
          to be a national requirement, the industry should be mature
          enough to offer multiple solutions for code compliance.  I'm
          all for improving safety, but it needs to be done as an
          industry: together, incrementally.<br>
          <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
          <div class="moz-cite-prefix">On 3/15/2016 1:48 PM, Patrick
            Shortell wrote:<br>
          </div>
          <blockquote
cite="mid:CAHcXnFUCBqdavA406sYZLkEGwVZxM5B8OLmFVeJLp+6tQ1MRGQ@mail.gmail.com"
            type="cite">
            <div dir="ltr">
              <div>
                <div>
                  <div>
                    <div>
                      <div>
                        <div>
                          <div>
                            <div>Dear List,<br>
                            </div>
                            Maybe it's an over simplistic opinion, but
                            shouldnt all sources be disconnected rapidly
                            in an emergency situation.<br>
                          </div>
                          We can always do better than what the code
                          requires. I get frustrated when people go to
                          the book, (and try to hide behind the text). 
                          instead of thinking through real life
                          scenarios.<br>
                        </div>
                        There are simple ways to work around these
                        issues.<br>
                      </div>
                      I find when something is questionable, Ill call
                      the AHJ and get his approval First.<br>
                    </div>
                    What would I do in my own house?<br>
                  </div>
                  What if someone thought all the power was off when
                  they dragged a hoseline into my basement.<br>
                </div>
                My two cents<br>
              </div>
              Pat<br>
            </div>
            <div class="gmail_extra"><br>
              <div class="gmail_quote">On Tue, Mar 15, 2016 at 1:10 PM,
                <span dir="ltr"><<a moz-do-not-send="true"
                    href="mailto:billbrooks7@sbcglobal.net"
                    target="_blank">billbrooks7@sbcglobal.net</a>></span>
                wrote:<br>
                <blockquote class="gmail_quote" style="margin:0 0 0
                  .8ex;border-left:1px #ccc solid;padding-left:1ex">Ray,<br>
                  <br>
                  I guess I have to step in after that acknowledgement.
                  PV system circuit is a<br>
                  self-defined term and therefore cannot be defined
                  unless you are going to<br>
                  develop a meaning that is different from the
                  self-definition. It means ANY<br>
                  circuit in a PV system. This includes battery and
                  stand-alone circuits in<br>
                  the 2014 NEC.<br>
                  <br>
                  The language of the 2014 NEC was a compromise between
                  the fire service and<br>
                  the PV industry.  Originally, the language required
                  essentially module-level<br>
                  shutdown. I raised the concern with the PV industry to
                  get them involved<br>
                  since most were not paying attention at the time. This
                  language was<br>
                  developed and intended to cover all circuits in a PV
                  system. In the 2014<br>
                  NEC, batteries are part of a PV system and therefore
                  fall under this<br>
                  requirement.<br>
                  <br>
                  In the 2017 NEC, we were very careful to carve out all
                  batteries and loads,<br>
                  that were previously part of PV systems, and place
                  them in their own<br>
                  articles. Don't shoot the messenger on this one and
                  don't think for a minute<br>
                  that I alone made this requirement or am alone in
                  interpreting it in this<br>
                  way. I did author this compromise with other
                  representatives of the PV<br>
                  industry so I think I know what the intent was.<br>
                  <br>
                  It is understandably difficult for battery systems and
                  I would try to keep<br>
                  battery circuits as short as possible. The 5-feet was
                  intended to match the<br>
                  requirement of 690.71(H)--which is further evidence of
                  the intent of the<br>
                  2014 NEC.<br>
                  <br>
                  The 2017 NEC removes batteries from the requirement,
                  but they still cannot<br>
                  backfeed the PV array. Energy storage systems (Article
                  706) will have their<br>
                  own requirements in time--that is guaranteed.<br>
                  <br>
                  Bill.<br>
                  <div class="HOEnZb">
                    <div class="h5"><br>
                      <br>
                      -----Original Message-----<br>
                      From: RE-wrenches [mailto:<a
                        moz-do-not-send="true"
                        href="mailto:re-wrenches-bounces@lists.re-wrenches.org"><a class="moz-txt-link-abbreviated" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a></a>]
                      On<br>
                      Behalf Of Ray Walters<br>
                      Sent: Tuesday, March 15, 2016 9:02 AM<br>
                      To: RE-wrenches <<a moz-do-not-send="true"
                        href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>><br>
                      Subject: [RE-wrenches] Rapid Shutdown<br>
                      <br>
                      Greetings Esteemed Wrenches:<br>
                      <br>
                      I've just heard back from our inspector here in
                      Colorado, and we are still<br>
                      being required to disconnect the batteries under
                      690.12.  No where in 690.12<br>
                      are batteries mentioned, nor in the appropriate
                      690.71 section that deals<br>
                      with batteries.  The entire reasoning behind this
                      is based on a single<br>
                      article written by a single person: Bill Brooks. 
                      I have contacted both<br>
                      Outback and Magnum on this issue, and their
                      engineers are unaware that rapid<br>
                      shutdown applies.<br>
                      My interpretation is that I could install an
                      inverter and battery system<br>
                      that was charged from a generator, and we would
                      not need any rapid shutdown<br>
                      at all.  But according to Bill, as soon as I put a
                      single solar module into<br>
                      the system, suddenly the entire system becomes PV?
                      The problem lies with the<br>
                      term 'PV System circuit'  used in 690.12.  690.2
                      Defines 'PV Output<br>
                      circuit', and 'PV source circuit', but there is no
                      'PV system circuit'<br>
                      defined.  690.12 therefore uses an undefined term.<br>
                      Our design uses 2 inverters, so if we used
                      Midnite's E panel with their<br>
                      remote trip breakers, the 2nd inverter would be
                      more than 5 ft from the<br>
                      batteries.  If we used Magnum or Outback DC
                      disconnects (that would comply<br>
                      with the 5 ft rule specified in 690.71) they don't
                      offer remote trip.<br>
                      We have a Midnite Rapid disconnect Combiner on the
                      roof with the Birdhouse,<br>
                      so we are complying with 690.12, it should not be
                      applied to batteries<br>
                      though.<br>
                      <br>
                      Thanks,<br>
                      <br>
                      --<br>
                      R.Ray Walters<br>
                      CTO, Solarray, Inc<br>
                      Nabcep Certified PV Installer,<br>
                      Licensed Master Electrician<br>
                      Solar Design Engineer<br>
                      303 505-8760<br>
                      <br>
                      _______________________________________________<br>
                      List sponsored by Redwood Alliance<br>
                      <br>
                      List Address: <a moz-do-not-send="true"
                        href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
                      <br>
                      Change listserver email address & settings:<br>
                      <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                        rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                      <br>
                      List-Archive:<br>
                      <a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                        rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                      <br>
                      List rules & etiquette:<br>
                      <a moz-do-not-send="true"
                        href="http://www.re-wrenches.org/etiquette.htm"
                        rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
                      <br>
                      Check out or update participant bios:<br>
                      <a moz-do-not-send="true"
                        href="http://www.members.re-wrenches.org"
                        rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
                      <br>
                      _______________________________________________<br>
                      List sponsored by Redwood Alliance<br>
                      <br>
                      List Address: <a moz-do-not-send="true"
                        href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
                      <br>
                      Change listserver email address & settings:<br>
                      <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                        rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                      <br>
                      List-Archive: <a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                        rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                      <br>
                      List rules & etiquette:<br>
                      <a moz-do-not-send="true"
                        href="http://www.re-wrenches.org/etiquette.htm"
                        rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
                      <br>
                      Check out or update participant bios:<br>
                      <a moz-do-not-send="true"
                        href="http://www.members.re-wrenches.org"
                        rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
                      <br>
                    </div>
                  </div>
                </blockquote>
              </div>
              <br>
              <br clear="all">
              <br>
              -- <br>
              <div class="gmail_signature">
                <div dir="ltr">
                  <div>
                    <div dir="ltr">
                      <div dir="ltr">Patrick A. Shortell
                        <div><i>Licensed Master Electrician</i></div>
                        <div><i>Certified Solar Installer</i></div>
                        <div>71 Oregon Street</div>
                        <div>Long Beach N.Y. 11561</div>
                        <div>cell: 516-477-0221</div>
                        <div><br>
                        </div>
                        <div><br>
                        </div>
                        <div><br>
                        </div>
                        <div><br>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
            <br>
            <fieldset class="mimeAttachmentHeader"></fieldset>
            <br>
            <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
          </blockquote>
          <br>
        </div>
      </blockquote>
      <blockquote type="cite">
        <div><span>_______________________________________________</span><br>
          <span>List sponsored by Redwood Alliance</span><br>
          <span></span><br>
          <span>List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br>
          <span></span><br>
          <span>Change listserver email address & settings:</span><br>
          <span><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br>
          <span></span><br>
          <span>List-Archive: <a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a></span><br>
          <span></span><br>
          <span>List rules & etiquette:</span><br>
          <span><a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></span><br>
          <span></span><br>
          <span>Check out or update participant bios:</span><br>
          <span><a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></span><br>
          <span></span><br>
        </div>
      </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>