    Rebekah and Jerry,<br>
    <br>
    If I'm understanding R's post below, at that particular install you
    could kill the disco for the inverter and still have 12 kV at 1 amp
    running around.  Call me a worry-wort but that sounds like a <u>pretty
      important blind spot</u> for us mortals to be aware of.  Maybe the
    fact that it was a 5 MW installation would keep less experienced
    people from getting hurt but I'd sure like to see some good sized
    placards mounted on the front gate and at the disconnects, inverters
    etc. warning of the risk present even with a locked out/tagged out
    disco.<br>
    <br>
    Greatly appreciate you posting this Rebekah, I doubt I would have
    thought of this otherwise.<br>
    <br>
    Greg Egan<br>
    Remote Power Inc.<br>
    <blockquote
cite="mid:mailman.1.1456425988.10236.re-wrenches-re-wrenches.org@lists.re-wrenches.org"
      type="cite">
      <pre wrap="">Hey Jerry,
If I remember correctly - it was about five years ago -   it was a little
complicated because the utility was doing the witness test where they pull
one phase and leave the other two connected, then test that there is no
current on any phase (because the inverters should shut off when one phase
drops). So two phases were still fully connected to the utility power, and
there was current flowing on those conductors, not from the PV array but
induced from the higher voltage lines. The inverter did shut off, but the
utility was still measuring over 1A  (at 12.47kV). I don't think we would
have noticed except that the utility was specifically looking for the lack
of current on the lines at that moment. I don't know what the high voltage
lines were, maybe 100 kV and not that far above the PV system lines?