    <div class="moz-cite-prefix">Daniel...<br>
      <br>
      This one is kind of unusual...  Especially tripping only in the
      morning.<br>
      <br>
      Temperature ?  Something moving or shaking the breaker box ?<br>
      <br>
      Have you tried changing the circuit breaker ?<br>
      <br>
      What is the approximate maximum current output from the Classic in
      the morning ?<br>
      <br>
       You can access recent power info before the trip in the LOGS menu
      or the main status menu by hitting<br>
      the STATUS button a few times...  Four hits I think, until you see
      the graph of power vs. time show up.<br>
      There are other items logged and can be seen by pressing the UP
      button.   Logging is done around every<br>
      5 or 10 minutes and the most recent log will be on the right side
      of the graph.<br>
      To move the cursor to the right to get this value, press the RIGHT
      arrow key.  LEFT key moves it<br>
      backward in time and right to more recent time.    If the MNGP
      (display) time and date is set correctly,<br>
      the logs should present the actual logging time correctly.<br>
      <br>
      The daily logs won't save the maximum power data because the
      Classic will reset before that info is saved<br>
      when the breaker tripped.  That usually happens at midnight.<br>
      <br>
        I know you don't usually get the nameplate rating out of an
      array but  18*245W adds<br>
      up to 4400 watts or so and would be around 90+ amps at 48V if it
      should ever<br>
      put out that much power.<br>
      <br>
      This list is going to have some great ideas but if we can also
      help, give us a ring at<br>
      360-403-7207.  OR, at any time day or night, you can start a
      support ticket that<br>
      immediately gets sent to all of the support people by going to...<br>
      <br>
      <a href="http://www.midnitesolar.com/help">http://www.midnitesolar.com/help</a><br>
      <br>
      The ticket method is kinda cool because it gets people thinking
      about the problem<br>
      as soon as they see it.<br>
      <br>
      boB Gudgel<br>
      <br>
      <br>
      <br>
      On 10/26/2015 6:30 PM, Daniel Tittmann wrote:<br>
    </div>
    <blockquote
cite="mid:CAKfSoE9ahs5unCZioOx6ULjDx+v1D44bLKL3=koyfHiwgYumnQ@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hive mind-
        <div>hoping you all can help me solve this mystery issue.</div>
        <div><br>
        </div>
        <div>System:</div>
        <div>Magnum double panel with Parallel stacked 2x4448 pae
          inverters.</div>
        <div>Classic 150 charge controller wired with an NMEPV 50 (din
          rail) and NMEPV100 </div>
        <div>18 - 245 watt solar modules (6x3). (not over powered)</div>
        <div><br>
        </div>
        <div>Issue:</div>
        <div>every morning the 100 amp din rail breaker is tripping.
           from what I can gather simultaneously the magnum RTR shows
          the AGS go into error.  Re set the breaker and the solar works
          fine for the rest of the day.  </div>
        <div><br>
        </div>
        <div>Not 100% sure the AGS has worked (under normal operation)
          at all other than at commissioning and recent testing. </div>
        <div><br>
        </div>
        <div>Of course on site i cant get it to fail.</div>
        <div><br>
        </div>
        <div>Tested the AGS by setting start voltage to 48.2 vdc and put
          the system under load....... voltage drops and generator
          turned on with no pv-> Batt breaker issue. </div>
        <div><br>
        </div>
        <div>last visit, chasing one theory, I re routed the battery +
          from the mnpv100 directly to the battery  + terminal as
          opposed to the battery + bus bar in the inverter panel still
          didn't solve the problem.<br>
        </div>
        <div><br>
        </div>
        <div>I cant figure out if it the classic causing the issue or if
          it is the inverters and the AGS.</div>
        <div><br>
        </div>
        <div>Any input would be appreciated.</div>
        <div>Thanks</div>
        <div>Daniel</div>
        <div><br clear="all">
          <div>
            <div class="gmail_signature">
              <div dir="ltr">Daniel Tittmann 
                <div>CTO</div>
                <div>Greenwired</div>
                <div><a moz-do-not-send="true"
                    href="http://www.greenwired.com" target="_blank">www.greenwired.com</a></div>
                <div><a moz-do-not-send="true"
                    href="mailto:daniel@greenwired.com" target="_blank">daniel@greenwired.com</a></div>
                <div>707-923-2001 (office)</div>
                <div>707-206-5088 (Cell)</div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
    </blockquote>
    <br>
  </body>
</html>