<p dir="ltr">I cant see this working well without some battery based inverter<br>
Jerry</p>
<div class="gmail_quote">On Aug 17, 2015 10:10 AM, "Ray Walters" <<a href="mailto:ray@solarray.com">ray@solarray.com</a>> wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">HI Esteemed Wrenches:<br>
<br>
I am consulting on a system I have never seen, that consists of a 6.7Kw Enphase roof mounted system, and 2 backup generators.  Each generator has an automatic 200 amp transfer switch to back up its own 200 amp panel.  Both 200 amp panels are fed by a 400 amp service from the grid.<br>
The Enphase PV backfeeds a subpanel in another building which then is fed by a 2 pole 60 amp breaker in one of the 200 amp panels.<br>
Currently they are having issues with the generators kicking out because of the Enphase inverters.  That part I understand: you can't backfeed a generator, or its voltage regulation freaks out.<br>
<br>
Now we get to the fun part: they want to create a third critical load subpanel with loads selected from both 200 amp panels to be powered by batteries and an inverter.<br>
I am considering the Sunny Island since it makes the most sense with its ability to signal the Enphase inverters to shut off when the batteries are full.  I also see this as a partial solution to the generator issue, since normally the Enphase will be connected to the output side of the Sunny Island.  However, when the generator is used to charge, we will be back to directly coupling the generator output to the Enphase.<br>
<br>
Here are some possible solutions I'm considering:<br>
1) Use a separate charger for the generator so that it will only feed DC to the batteries, and not be AC coupled.<br>
2) convert the PV back to DC with charge controllers, but that would involve ditching and adding another conduit run between buildings.<br>
3)  Put the Enphase PV on a relay that would disconnect the PV when charging with the generator.<br>
4) Something I haven't thought of that one of you clever folks can suggest......<br>
<br>
As always, thanks in advance for all you responses,<br>
<br>
-- <br>
R.Ray Walters<br>
CTO, Solarray, Inc<br>
Nabcep Certified PV Installer,<br>
Licensed Master Electrician<br>
Solar Design Engineer<br>
<a href="tel:303%20505-8760" value="+13035058760" target="_blank">303 505-8760</a><br>
<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>