<div dir="ltr">I made myself a guinea pig on Iron Edison NiFe cells this year, before I try to install them for any customer. I have now about 90 days on them.<div>1.65 volts per cell charging is what they want and need. PV controllers MPPT type are fine with this. just change the settings (assuming the sun is shining) </div><div>. Inverter/chargers are not fine, at least not my Magnum OMG! over 1.6v per cell!! Overvoltage! Shut down!</div><div>So I have rewired battery bank as recommended by Mrf with 9 cells at 1.2v instead of 10 cells. And now with my 10.8v battery bank I get surge low voltage wonky waveform hits from the fridge turning on, etc. that reboot  the satellite internet, tv etc.</div><div>My plan is to add another 1kw of solar here for an increase of 50% and rely more on the incoming PV that can bring it all up to 1.65v per cell rather than the generator that can't do it thanks to the inverter firmware.</div><div> I think my new NiFe batteries will do just great in the long run. But their charge/discharge behavior is a continuing lesson. And I am SO glad to learn these lessons myself, instead of in front of a critical customer. </div><div><div><br><div><br></div></div></div></div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature"><div dir="ltr">Dan Fink<div>Buckville Energy</div><div>IREC Certified Instructor™ for: </div><div>~ PV Installation Professional</div><div>~ Small Wind Installer</div><div>NABCEP / IREC / ISPQ Accredited Continuing Education Providers™<br>970.672.4342<br><br> </div></div></div></div>
<br><div class="gmail_quote">On Sun, Jul 26, 2015 at 6:55 PM, jay <span dir="ltr"><<a href="mailto:jay.peltz@gmail.com" target="_blank">jay.peltz@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">HI Tom,<br>
<br>
They are considered 1.2v nominal.<br>
<br>
Charge range is up to 1.7v per cell.<br>
For a 24v system usually you pull out 1 cell or 19 cells 19 x 1.7 = 32.3v<br>
For a 48, usually 2 or 3 , or 37-38 cells.<br>
<br>
If you use much less, then the voltage swings really low, if you go more the voltage is too high for most inverters.<br>
The Iota isn’t going to charge them up fully with that low a voltage.  But I don’t know if that version Iota is adjustable, many of the older ones had a internal pot you could turn up.<br>
<br>
But heck give it a try and play with it.<br>
<br>
jay<br>
<br>
peltz power<br>
<div class="HOEnZb"><div class="h5"><br>
<br>
<br>
<br>
> On Jul 26, 2015, at 4:34 PM, Tom Lane <<a href="mailto:tom@ecs-solar.com">tom@ecs-solar.com</a>> wrote:<br>
><br>
> I have a friend who has forty ( 40 ) Iron Edison Batteries , he says they are each 1.5 volts and wants to use them for a backup to his aquatics business's . Continuous load 24/7 is only 365 watts with surges to 1200 watts . My guess is that ___# of batteries ( maybe 32 to 36 ? ) can be wire as a 48 volt system ? Any suggestion on charge controllers - Morningstar or MidNite ? . .? A Samplex pure sign wave inverter 2000 watts at 48 volts and an Iota 54 volt battery charger is my guess that it might be the way to power the load - any suggestions  . Anyone have experience with Iron Edison .any suggestions appreciated !  Gator tom PS : any suggested websites ?<br>
><br>
> Sent from my iPad<br>
> _______________________________________________<br>
> List sponsored by Redwood Alliance<br>
><br>
> List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
><br>
> Change listserver email address & settings:<br>
> <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
><br>
> List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
><br>
> List rules & etiquette:<br>
> <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
><br>
> Check out or update participant bios:<br>
> <a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
><br>
<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</div></div></blockquote></div><br></div>