    <font size="+1"><tt>The reason behind this rule, going back through
        some history, was to reduce the possibility of a nail
        penetrating hidden conduit (conduit behind a wall). Since the
        conduit is exposed/visible, the chances of that action happening
        are small to none. So, the installer is saying that a literal
        interpretation is not consistent with the intent of the NEC. May
        have to ask the AHJ for their position. </tt></font><br>
    <br>
    <div class="moz-cite-prefix">On 7/13/2015 1:01 PM, Dana wrote:<br>
    </div>
    <blockquote cite="mid:001b01d0bd8d$8f168300$ad438900$@com"
      type="cite">
      <pre wrap="">Your assumption is the rule here. Metal inside a building envelope and it cannot transition at the penetration it must be metal before entry.

----------------------------------------------------------------------------
Dana Orzel 
Great Solar Works, Inc -  NABCEP # 051112-136
E - <a class="moz-txt-link-abbreviated" href="mailto:dana@solarwork.com">dana@solarwork.com</a>  - Web - solarwork.com 
O - 970.626.5253  C - 208.721.7003
"Responsible Technologies for Responsible People since 1988"  
 Please consider the environment before printing this email.



-----Original Message-----
From: RE-wrenches [<a class="moz-txt-link-freetext" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of Christopher Warfel
Sent: Monday, July 13, 2015 10:59 AM
To: <a class="moz-txt-link-abbreviated" href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>
Subject: [RE-wrenches] DC conductors in metallic raceway/conduit

I was under the assumption that dc conductors could only be run inside a building when in metallic raceway/conduit (up to a readily accessible 
disconnect switch) .  The building being occupied/residence.    A 
contractor ran 5 feet of pvc from the wall penetration to the charge controller in a concrete block garage.  I don't see anything that allows this by what I find in the NEC. Has anyone have a reference that permits this?  Thank you for any assistance.



--
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978


_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978</pre>
  </body>
</html>