<font size="+1"><tt>The reason behind this rule, going back through
some history, was to reduce the possibility of a nail
penetrating hidden conduit (conduit behind a wall). Since the
conduit is exposed/visible, the chances of that action happening
are small to none. So, the installer is saying that a literal
interpretation is not consistent with the intent of the NEC. May
have to ask the AHJ for their position. </tt></font><br>
<br>
<div class="moz-cite-prefix">On 7/13/2015 1:01 PM, Dana wrote:<br>
</div>
<blockquote cite="mid:001b01d0bd8d$8f168300$ad438900$@com"
type="cite">
<pre wrap="">Your assumption is the rule here. Metal inside a building envelope and it cannot transition at the penetration it must be metal before entry.
----------------------------------------------------------------------------
Dana Orzel
Great Solar Works, Inc - NABCEP # 051112-136
E - <a class="moz-txt-link-abbreviated" href="mailto:dana@solarwork.com">dana@solarwork.com</a> - Web - solarwork.com
O - 970.626.5253 C - 208.721.7003
"Responsible Technologies for Responsible People since 1988"
Please consider the environment before printing this email.
-----Original Message-----
From: RE-wrenches [<a class="moz-txt-link-freetext" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of Christopher Warfel
Sent: Monday, July 13, 2015 10:59 AM
To: <a class="moz-txt-link-abbreviated" href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>
Subject: [RE-wrenches] DC conductors in metallic raceway/conduit
I was under the assumption that dc conductors could only be run inside a building when in metallic raceway/conduit (up to a readily accessible
disconnect switch) . The building being occupied/residence. A
contractor ran 5 feet of pvc from the wall penetration to the charge controller in a concrete block garage. I don't see anything that allows this by what I find in the NEC. Has anyone have a reference that permits this? Thank you for any assistance.
--
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
_______________________________________________
List sponsored by Redwood Alliance
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978</pre>
</body>
</html>