<div dir="ltr">Kirpal<div><br></div><div>True there is no current control, but more like a rough Pulse width modulated control through motorized breaker that does maintain the proper voltage level for a multistage charging at Bulk Absorb and Float settings.</div><div><br></div><div>Bill</div></div><div class="gmail_extra"><br><div class="gmail_quote">On Wed, Jul 1, 2015 at 5:59 AM, Kirpal Khalsa <span dir="ltr"><<a href="mailto:solarworks@gmail.com" target="_blank">solarworks@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><p dir="ltr">Hey Bill...my understanding of the Outback AC coupled solution is that it does not offer multi stage charging from the grid tied inverter as it does not have any way to regulate the amount of power coming in  from that inverter...based on the state of charge of the batteries and at pre set voltage set points it can operate the remote breaker but it does not have the ability to taper the amount of in coming power from the grid tied inverter..   This is why the frequency shift AC coupling such as found with SMA and others is a nice solution as the amount of incoming power from the grid tied inverters is regulated allowing for healthy multi stage charging.  <br>
Another thing to consider if using the Outback Ac coupled solution is that your DC coupling options becomes limited in the same load center....<br>
Cheers<span class="HOEnZb"><font color="#888888"><br>
Kirpal</font></span></p><div class="HOEnZb"><div class="h5">
<div class="gmail_quote">On Jun 30, 2015 9:01 AM, "Bill Hoffer" <<a href="mailto:sunengser@gmail.com" target="_blank">sunengser@gmail.com</a>> wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr">Kirpal<div><br></div><div>Actually the Radian system does adjust the battery voltage point that it disconnects the grid inverter based on the stage of the charge timers using the 3 stage inverter charger set points.  The FNDC will also over ride the timers if all fully charged parameters are met.  It has the advantage of being able to safely use a back up generator in the system and will physically disconnect from grid and the AC coupled inverter before connecting the generator.  So there are some advantages over a SMA AC coupled system too!</div><div><br></div><div>Even though there is no official application notes on AC coupling a Radian and Solaredge, I have seen it done with good results.  The nice thing about an AC coupled Radian is it should work with any grid tie inverter system out there.</div><div><br></div><div>Bill</div></div><div class="gmail_extra"><br><div class="gmail_quote">On Tue, Jun 30, 2015 at 6:45 AM, Kirpal Khalsa <span dir="ltr"><<a href="mailto:solarworks@gmail.com" target="_blank">solarworks@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr">Tom....I haven't AC coupled Solaredge and Outback, but I have AC Coupled Outback with various other inverter manufacturers and their Radian AC Coupled Load center will work with any AC source....It doesn't directly communicate with any other inverter but its remote operated circuit breakers allow it to disconnect AC Power from any other inverter when batteries reach a preset voltage....It is not as elegant as a sunny island/sunnyboy system because it doesn't provide multistage charging buy it is easy to implement and install.....You should be able to find all the information on the Outback Radian site.  You would need the GSLC-AC-120/240 load center and it comes pre wired with the remote operated circuit breaker which makes it a breeze to install....<div><br></div></div><div class="gmail_extra"><br clear="all"><div><div><div dir="ltr"><div><div dir="ltr">Sunny Regards,<br>Kirpal Khalsa<br>NABCEP Certified PV Installation Professional<br>Oregon Solarworks LLC<br><a href="http://www.oregonsolarworks.com" target="_blank">www.oregonsolarworks.com</a><br><a href="tel:541-218-0201" value="+15412180201" target="_blank">541-218-0201</a> m<br><a href="tel:541-299-0402" value="+15412990402" target="_blank">541-299-0402</a> o</div></div></div></div></div>
<br><div class="gmail_quote">On Tue, Jun 30, 2015 at 3:40 AM, Tom Lane <span dir="ltr"><<a href="mailto:tom@ecs-solar.com" target="_blank">tom@ecs-solar.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Has anyone AC Coupled an Outback System with SolarEdge ? I would like to see a wiring diagram and know what components from Outback you used with SolarEdge . I have been told variously that SolarEdge does not approve AC Coupling and that they have approve it , depending on who I get on the phone . SolarEdge and Outback have no official diagrams or components list that I can find . I would like some help here as we are in Hurricane season in Gator Land !<br>
<br>
Sent from my iPad<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div><br></div>
<br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br><div><div dir="ltr"><div>William Hoffer <br></div>161 SE Fourth Ave<br><div>P.O. Box 1823<br>White Salmon, WA 98672-1823<br><a href="mailto:bhoffer@sunergyengineeringservices.com" target="_blank">sunengser@gmail.com</a><br><br></div></div></div>
</div>
<br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div>
</div></div><br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br><div class="gmail_signature"><div dir="ltr"><div>William Hoffer <br></div>161 SE Fourth Ave<br><div>P.O. Box 1823<br>White Salmon, WA 98672-1823<br><a href="mailto:bhoffer@sunergyengineeringservices.com" target="_blank">sunengser@gmail.com</a><br><br></div></div></div>
</div>