<html><head><meta http-equiv="Content-Type" content="text/html; charset=UTF-8"></head><body ><div>Wrenches</div><div>We always try to minimize in connection cables as well as home run cables to the shorted length possible, restating batteries to aid this should always be considered as well as positive and negative runs</div><div>Jerry</div><div><br></div><div><br></div><div><div style="font-size:9px;color:#575757">Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone</div></div><br><br><div>-------- Original message --------</div><div>From: Ray Walters <ray@solarray.com> </div><div>Date:06/29/2015  12:05 PM  (GMT-10:00) </div><div>To: RE-wrenches <re-wrenches@lists.re-wrenches.org> </div><div>Subject: Re: [RE-wrenches] Battery Bank to Inverter Wiring </div><div><br></div>
    This is fascinating because while I knew the DC cables had an AC 
    component, I never realized how much inductance played in the volt
    drop to the inverter.  Thanks for bringing this to our attention
    Jarmo.  <br>
    Which brings up another question based on Benn's question:  isn't
    the battery itself part of the inductive loop?  and would the lead
    inside and steel cases act to increase the inductance?  Should we
    consider changing battery layouts not just to shorten cable lengths,
    but to counter inductance in the batteries themselves?  If needed,
    we could actually wire the batteries to "twist" by putting every
    other 2 v cell in the opposite row.  <br>
    My guess is that it wouldn't be worth it, but I've been wrong many
    times.......<br>
    <br>
    <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
    <div class="moz-cite-prefix">On 6/29/2015 3:55 PM, Benn Kilburn
      wrote:<br>
    </div>
    <blockquote cite="mid:A86E9CED-086A-49F8-A48D-E2DDE53CC893@skyfireenergy.com" type="cite">
      <meta http-equiv="content-type" content="text/html;
        charset=windows-1252">
      <div>What about when you have the (+) and (-) terminals at
        opposite ends of a larger battery bank?  Sure you can run the
        conductors side-by-side once they meet up on their way to the
        inverter, but would you consider the distance between the end
        terminals a "large loop"? </div>
      <div>Ideally the battery string is laid out so the end terminals
        are close together and close to the inverter, but this isn't
        always the case. <br>
        <br>
        <div>Benn Kilburn</div>
        <div>SkyFire Energy Inc. </div>
        <div>780-906-7807</div>
        <div><br>
        </div>
      </div>
      <div><br>
        On Jun 29, 2015, at 10:28 AM, <a moz-do-not-send="true" href="mailto:Jarmo.Venalainen@schneider-electric.com">Jarmo.Venalainen@schneider-electric.com</a>
        wrote:<br>
        <br>
      </div>
      <blockquote type="cite">
        <div><font face="sans-serif" size="2">Hi:</font>
          <br>
          <br>
          <font face="sans-serif" size="2">From the comments so far, it
            appears
            that within the wrenches group, good practices are the rule
            and DC cables
            are kept side by side, so the problem I mentioned hasn't
            come up much.</font>
          <br>
          <br>
          <font face="sans-serif" size="2">I have seen "large loop"
            battery
            cables a couple of times in solar installs myself out on
            islands way down
            south.  Also on boats/RV's/motor homes.</font>
          <br>
          <br>
          <font face="sans-serif" size="2">Please keep the cable loop in
            mind when
            you do bench tests of inverters, as it may screw up the
            results and make
            it seem like there is something wrong with the inverter.</font>
          <br>
          <br>
          <font face="sans-serif" size="2">JARMO<br>
          </font><font color="#008000" size="3">_____________________________________________________________________________________</font><font size="3">
            <br>
          </font><font face="Arial" size="1"><b><br>
              Jarmo Venalainen</b>  |  </font><font color="#008000" face="Arial" size="1"><b>
              Schneider Electric </b></font><font face="Arial" size="1"><b> 
              |  Xantrex
              Brand</b>  |   <b>CANADA</b>  |   <b>Sales Application
              Engineer</b> <b><br>
              Phone:</b> +604-422-2528  |   <b>Tech Support:</b>
            800-670-0707
             |   <b>Mobile:</b> +604-505-0291 <b><br>
              Email:</b> </font><a moz-do-not-send="true" href="mailto:jarmo.venalainen@schneider-electric.com"><font color="blue" face="Arial" size="1"><u>jarmo.venalainen@schneider-electric.com</u></font></a><font face="Arial" size="1">
             |   <b>Site:</b></font><a moz-do-not-send="true" href="http://www.xantrex.com/" target="_blank"><font color="blue" face="Arial" size="1"><u>
                www.Xantrex.com</u></font></a><font face="Arial" size="1">  |  
            <b>Address:</b> 3700 Gilmore Way, Burnaby, BC V5G4M1 <br>
          </font>
          <table>
            <tbody>
              <tr>
                <td colspan="4"><a moz-do-not-send="true" href="http://www.xantrexrebate.com/" target="_blank"><mime-attachment.gif></a>
                </td>
              </tr>
              <tr>
                <td><a moz-do-not-send="true" href="http://www.xantrex.com/" target="_blank"><mime-attachment.gif></a>
                </td>
                <td><a moz-do-not-send="true" href="https://www.facebook.com/Xantrex" target="_blank"><mime-attachment.gif></a>
                </td>
                <td><a moz-do-not-send="true" href="https://twitter.com/Xantrex" target="_blank"><mime-attachment.gif></a>
                </td>
                <td><a moz-do-not-send="true" href="https://twitter.com/Xantrex" target="_blank"><mime-attachment.gif></a></td>
              </tr>
            </tbody>
          </table>
          <br>
          <br>
          <font color="#00a000" face="Arial" size="1"><br>
            *** Please consider the environment before printing this
            e-mail</font><font size="3"><br>
          </font>
          <br>
          <br>
          <br>
          <table width="100%">
            <tbody>
              <tr valign="top">
                <td><font color="#5f5f5f" face="sans-serif" size="1">From:</font>
                </td>
                <td><font face="sans-serif" size="1">"<a moz-do-not-send="true" href="mailto:boB@midnitesolar.com">boB@midnitesolar.com</a>"
                    <<a moz-do-not-send="true" href="mailto:boB@midnitesolar.com">boB@midnitesolar.com</a>></font>
                </td>
              </tr>
              <tr valign="top">
                <td><font color="#5f5f5f" face="sans-serif" size="1">To:</font>
                </td>
                <td><font face="sans-serif" size="1">RE-wrenches <<a moz-do-not-send="true" href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>>,
                  </font>
                </td>
              </tr>
              <tr valign="top">
                <td><font color="#5f5f5f" face="sans-serif" size="1">Date:</font>
                </td>
                <td><font face="sans-serif" size="1">06/28/2015 10:30 PM</font>
                </td>
              </tr>
              <tr valign="top">
                <td><font color="#5f5f5f" face="sans-serif" size="1">Subject:</font>
                </td>
                <td><font face="sans-serif" size="1">Re: [RE-wrenches]
                    Battery Bank to Inverter
                    Wiring</font>
                </td>
              </tr>
              <tr valign="top">
                <td><font color="#5f5f5f" face="sans-serif" size="1">Sent
                    by:</font>
                </td>
                <td><font face="sans-serif" size="1">"RE-wrenches" <<a moz-do-not-send="true" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>></font></td>
              </tr>
            </tbody>
          </table>
          <br>
          <hr noshade="noshade">
          <br>
          <br>
          <br>
          <font size="3"><br>
            On 6/28/2015 9:20 AM, Allan Sindelar wrote:<br>
            >>>>I'm not an EE, but I can't see what
            difference twisting
            would make in<br>
            the absence of a building/collapsing field as is normal with
            AC.<<<<<br>
            <br>
            It is little known that with the typical inverters that use
            the heavy power
            transformers,<br>
            have a lot of AC 120 Hz (or 100 Hz for 50 Hz systems)
            current mixed in
            with that DC battery current.<br>
            <br>
            The AC output current reflects back to the input as ripple
            current. 
            This is why you want to<br>
            have at least short as possible Sbattery cable runs AND keep
            the wires
            as close together as possible.<br>
            <br>
            Twisting the battery cables may help a bit but that is
            probably overkill.<br>
            <br>
            The problem has to do with inductance in the battery
            cables.  You
            can use as big of cable<br>
            as you can fit in to reduce resistance, but that will not
            help to lower
            the inductance.<br>
            The problems you can sometimes have with high inductance is
            that L-C resonance
            at the<br>
            inverter can raise the peak voltages seen at the inverter
            input terminals
            and can be hard on<br>
            the inverter.<br>
            <br>
            Then again,  the high frequency, lighter weight inverters
            will typically
            keep most of that ripple<br>
            inside,  between the DC input and AC output and battery
            cable inductance
            will not be as much<br>
            of a problem on the battery cables.<br>
            <br>
            boB Gudgel<br>
            <br>
            <br>
            <br>
            <br>
            On 6/28/2015 9:20 AM, Allan Sindelar wrote:</font>
          <br>
          <font size="3">As a matter of course I have always run the
            positive and
            negative conductors of high-current cable pairs together,
            but have never
            deliberately twisted them, and have never known of any
            related problems.
            <br>
            The most obvious example of this would be 4/0
            battery/inverter cables in
            a 24V system, with a 250A GJ-class breaker or (prior to
            that) a 300A or
            400A Class T fuse. It's pretty tough to thread a twisted
            pair of 4/0 USE/RHH/RHW
            cables through a 2" elbow or LB from inverter enclosure to
            battery
            enclosure.<br>
            I'm not an EE, but I can't see what difference twisting
            would make in the
            absence of a building/collapsing field as is normal with AC.
            <br>
            I have twisted AC conductors together in the past when
            clients have expressed
            concerns about EMF from their equipment and wiring, but only
            AC.<br>
            Allan<br>
          </font>
          <p><font size="3"><b>Allan Sindelar</b></font><font color="blue" size="2"><u><br>
              </u></font><a moz-do-not-send="true" href="mailto:allan@sindelarsolar.com"><font color="blue" size="2"><u>allan@sindelarsolar.com</u></font></a><font size="2"><br>
              NABCEP Certified PV Installation Professional<br>
              NABCEP Certified Technical Sales Professional<br>
              New Mexico EE98J Journeyman Electrician<br>
              Founder (Retired), Positive Energy, Inc.<b><br>
                505 780-2738 cell</b><br>
            </font>
          </p>
          <p><font size="3"> </font>
          </p>
          <p><font size="3">On 6/27/2015 2:40 AM, John wrote:</font>
            <br>
            <font face="Cambria" size="2">That is why for years we have
              been twisting
              those leads around each other.  I was told it was to
              cancel out the
              opposing fields on the wires, but for whatever the correct
              technical reason
              is,  we have always twisted those heavy wires.        
              John V.</font>
            <br>
            <font face="Cambria" size="2"> </font>
            <br>
            <font face="Tahoma" size="2"><b>From:</b> RE-wrenches [</font><a moz-do-not-send="true" href="mailto:re-wrenches-bounces@lists.re-wrenches.org"><font color="blue" face="Tahoma" size="2"><u>mailto:re-wrenches-bounces@lists.re-wrenches.org</u></font></a><font face="Tahoma" size="2">]
              <b>On Behalf Of </b></font><a moz-do-not-send="true" href="mailto:Jarmo.Venalainen@schneider-electric.com"><font color="blue" face="Tahoma" size="2"><u>Jarmo.Venalainen@schneider-electric.com</u></font></a><font face="Tahoma" size="2"><b><br>
                Sent:</b> Saturday, 27 June 2015 5:45 a.m.<b><br>
                To:</b> RE-wrenches<b><br>
                Subject:</b> [RE-wrenches] Battery Bank to Inverter
              Wiring</font>
            <br>
            <font face="Times New Roman" size="3"> </font>
            <br>
            <font face="Arial" size="2">Hi:</font><font face="Times New
              Roman" size="3">
              <br>
            </font><font face="Arial" size="2"><br>
              From time to time over the years I've come across systems
              where the routing
              of DC cables between the batteries and the inverter has
              been the cause
              of  issues.</font><font face="Times New Roman" size="3"> <br>
            </font><font face="Arial" size="2"><br>
              I'm not referring to wire thickness or quality of
              terminations.  For
              the purposes of this discussion, just assume that wire
              thickness and terminations
              are perfect.</font><font face="Times New Roman" size="3">
              <br>
            </font><font face="Arial" size="2"><br>
              What I am referring to is the routing of the positive and
              negative battery
              cables.  In particular, the loop area within the + and -
              cables as
              shown in the image below,</font><font face="Times New
              Roman" size="3"> <br>
            </font><font face="Arial" size="2"><br>
              The problem I've seen in systems with a large loop in the
              setup is that
              the inverter does not provide good surge power and can
              even go into low
              voltage shutdown during large surges.</font><font face="Times New Roman" size="3">
              <br>
            </font><font face="Arial" size="2"><br>
              Recently this happened again and I wanted to get a better
              feel for it,
              so I did some math.  </font><font face="Times New Roman" size="3"> <br>
            </font><font face="Arial" size="2"><br>
              For a cable length of about 12', the loop is an inductor
              which has a value
              of inductance of about 1 uH for side by side cables and as
              much as 6 uH
              for cables about 1 foot apart.  </font><font face="Times
              New Roman" size="3">
              <br>
            </font><font face="Arial" size="2"><br>
              This inductance is greatly multiplied by any ferrous metal
              in the loop
              and can easily be in the range of 10's to 100's of uH.
               Examples being
              cables which run in steel conduits or along the steel
              frame of a motor
              home.</font><font face="Times New Roman" size="3"> <br>
            </font><font face="Arial" size="2"><br>
              Inductance causes a voltage drop proportional to the rate
              at which the
              current is changing.  To get an idea of how large that
              rate can be
              for typical inverters, I did surge tests with a 5kW
              inverter and found
              that the rate of change of current can be as high as 100A
              per milli-second
              or 100,000 Amps/second.</font><font face="Times New Roman" size="3"> <br>
            </font><font face="Arial" size="2"><br>
              Given that, the voltage drop of the wire inductance is
              then , Vdrop = (rate
              of change of current) x (inductance), </font><font face="Times New Roman" size="3"><br>
            </font><font face="Arial" size="2"><br>
              Vdrop for 1 uH = (100,000 A/s) x (0.000001 H) = 0.1V</font><font face="Times New Roman" size="3">
            </font><font face="Arial" size="2"><br>
              Vdrop for 10 uH = (100,000 A/s) x (0.000001 H) = 1.0V</font><font face="Times New Roman" size="3">
            </font><font face="Arial" size="2"><br>
              Vdrop for 100 uH = (100,000 A/s) x (0.000001 H) = 10.0V  
               clearly
              this is a problem.</font><font face="Times New Roman" size="3"> <br>
            </font><font face="Arial" size="2"><br>
              Have any of the wrenches had systems with this issue?  If
              so, how
              often.</font><font face="Times New Roman" size="3"> <br>
              <br>
            </font><font face="Arial" size="2"><br>
              JARMO</font><font face="Times New Roman" size="3"> </font>
          </p>
          <p>
            <br>
            <font size="3"><br>
              <br>
______________________________________________________________________<br>
              This email has been scanned by the Symantec Email
              Security.cloud service.<br>
______________________________________________________________________</font><tt><font size="2">_______________________________________________<br>
                List sponsored by Redwood Alliance<br>
                <br>
                List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
                <br>
                Change listserver email address & settings:<br>
              </font></tt><a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size="2">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size="2"><br>
                <br>
                List-Archive: </font></tt><a moz-do-not-send="true" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"><tt><font size="2">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</font></tt></a><tt><font size="2"><br>
                <br>
                List rules & etiquette:<br>
              </font></tt><a moz-do-not-send="true" href="www.re-wrenches.org/etiquette.htm"><tt><font size="2">www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size="2"><br>
                <br>
                Check out or update participant bios:<br>
              </font></tt><a moz-do-not-send="true" href="www.members.re-wrenches.org"><tt><font size="2">www.members.re-wrenches.org</font></tt></a><tt><font size="2"><br>
                <br>
              </font></tt>
            <br>
            <br>
          </p>
        </div>
      </blockquote>
      <blockquote type="cite">
        <div><span>_______________________________________________</span><br>
          <span>List sponsored by Redwood Alliance</span><br>
          <span></span><br>
          <span>List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br>
          <span></span><br>
          <span>Change listserver email address & settings:</span><br>
          <span><a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br>
          <span></span><br>
          <span>List-Archive: <a moz-do-not-send="true" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a></span><br>
          <span></span><br>
          <span>List rules & etiquette:</span><br>
          <span><a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></span><br>
          <span></span><br>
          <span>Check out or update participant bios:</span><br>
          <span><a moz-do-not-send="true" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></span><br>
          <span></span><br>
        </div>
      </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  

</body>