      Oooo...  Or maybe a module or more are shorted and being bypassed
      ?<br>
      <br>
      A FLIR can sometimes come in handy to look at the entire array and
      of course<br>
      detect bad/hot connections.<br>
      <br>
       But a shorted module will be almost as hot as a working module at
      MPP voltage.<br>
      <br>
      boB<br>
      <br>
      <br>
      On 6/1/2015 11:28 AM, <a class="moz-txt-link-abbreviated" href="mailto:boB@midnitesolar.com">boB@midnitesolar.com</a> wrote:<br>
    </div>
    <blockquote cite="mid:556CA466.40703@midnitesolar.com" type="cite">
      <meta content="text/html; charset=windows-1252"
        http-equiv="Content-Type">
      <div class="moz-cite-prefix"><br>
        <br>
        Partial shading will also reduce the MPP voltage and to a much
        smaller extent, the Voc.<br>
        <br>
        I don't suppose there are some new trees or something at the
        site ?<br>
        <br>
        Jarmo, I like your presentation.<br>
        <br>
        boB<br>
        <br>
        <br>
        On 6/1/2015 11:21 AM, Starlight Solar Power Systems wrote:<br>
      </div>
      <blockquote
        cite="mid:CFBA85A9-59A2-4458-A270-82AEC61DBB89@starlightsolar.com"
        type="cite">
        <meta http-equiv="Content-Type" content="text/html;
          charset=windows-1252">
        Luke,
        <div class=""><br class="">
        </div>
        <div class="">For reference, we sold/installed many hundreds of
          Uni-Solar products since 2002. I have never seen anywhere near
          that much Voc loss. </div>
        <div class=""><br class="">
        </div>
        <div class="">Since the PVL-68 has an open circuit of 23.1V
          (92.4V) but you only see 14.2V (71V), a loss of 25%, I do not
          believe degradation is the culprit even at 15 years. The rated
          degradation is 0.73% per year. That should put you at 82.3
          Voc. But, Uni-Solar consistantly outputs  at least 10% more
          than rated power, even with age it should be higher than 82
          volts.</div>
        <div class=""><br class="">
        </div>
        <div class="">Proper Uni-Solar installation required 2 screws
          into the roof up near the top. A misplaced screw and time or
          an open seam may be causing a ground fault, pulling down the
          voltage of the array. Start by using a Megger at the combiner
          to check for leakage. No one likes crawling in a hot attic but
          I think you may need to. 
          <div class=""><br class="">
          </div>
          <div class="">
            <div apple-content-edited="true" class="">
              <div style="color: rgb(0, 0, 0); letter-spacing: normal;
                orphans: auto; text-align: start; text-indent: 0px;
                text-transform: none; white-space: normal; widows: auto;
                word-spacing: 0px; -webkit-text-stroke-width: 0px;
                word-wrap: break-word; -webkit-nbsp-mode: space;
                -webkit-line-break: after-white-space;" class="">
                <div style="color: rgb(0, 0, 0); letter-spacing: normal;
                  orphans: auto; text-align: start; text-indent: 0px;
                  text-transform: none; white-space: normal; widows:
                  auto; word-spacing: 0px; -webkit-text-stroke-width:
                  0px; word-wrap: break-word; -webkit-nbsp-mode: space;
                  -webkit-line-break: after-white-space;" class="">
                  <div style="color: rgb(0, 0, 0); font-family:
                    Helvetica; font-style: normal; font-variant: normal;
                    font-weight: normal; letter-spacing: normal;
                    line-height: normal; orphans: 2; text-align:
                    -webkit-auto; text-indent: 0px; text-transform:
                    none; white-space: normal; widows: 2; word-spacing:
                    0px; -webkit-text-stroke-width: 0px; word-wrap:
                    break-word; -webkit-nbsp-mode: space;
                    -webkit-line-break: after-white-space;" class=""><br
                      class="">
                    Larry Crutcher<br class="">
                  </div>
                  <div style="color: rgb(0, 0, 0); font-family:
                    Helvetica; font-style: normal; font-variant: normal;
                    font-weight: normal; letter-spacing: normal;
                    line-height: normal; orphans: 2; text-align:
                    -webkit-auto; text-indent: 0px; text-transform:
                    none; white-space: normal; widows: 2; word-spacing:
                    0px; -webkit-text-stroke-width: 0px; word-wrap:
                    break-word; -webkit-nbsp-mode: space;
                    -webkit-line-break: after-white-space;" class=""><br
                      class="">
                  </div>
                </div>
              </div>
            </div>
            <div>
              <div class=""> <br class="">
                <br class="">
                <tt class=""><font class="" size="2">Hello Off-Grid
                    Wrenches,<br class="">
                    <br class="">
                    I recently made a periodic maintenance visit to a
                    residential off-grid system I take care of here in
                    Southern CO, and discovered an interesting problem.
                    <br class="">
                    <br class="">
                    This system has an array of 48x Uni-Solar PVL-68
                    laminate modules applied directly to standing-seam
                    metal roofing. <br class="">
                    <br class="">
                    The data logging on the controller (Outback MX-60)
                    indicated that the system was having trouble
                    completing a charge cycle and going to float.
                    Initially I assumed was due to heavy electrical use
                    by the occupants (renters). After a little checking,
                    I noticed that the module string voltage was only
                    about 0.5V above the battery voltage! <br class="">
                    This was a cool late morning, with full sun, and the
                    array was charging almost 2kW at 54.5V. The module
                    strings were running at 55V. I've noticed the module
                    voltage being lower than I'd like before, but it has
                    never been this low. I suspect this is the real
                    reason the system hasn't been able to complete a
                    charge cycle.<br class="">
                    <br class="">
                    By removing the loads I was able to get an
                    open-circuit voltage of 71V, but that still seems
                    pretty low. <br class="">
                    <br class="">
                    Has anyone else experienced a voltage degradation
                    issue with the Uni-Solar laminate? What was the
                    expected annual voltage degradation for this
                    technology? <br class="">
                    <br class="">
                    These modules do have some age on them. The system
                    was installed about 15 years ago (by a competent
                    installer who is now retired). The system was
                    installed before MPPT controllers were common, so I
                    assume the modules are wired in strings of 4 for 48V
                    nominal. <br class="">
                    <br class="">
                    Any experiences or opinions are appreciated.<br
                      class="">
                    Thanks in advance. <br class="">
                    <br class="">
                    -Luke<br class="">
                    <br class="">
                    <br class="">
                    Luke Christy<br class="">
                    <br class="">
                    NABCEP Certified PV Installation Professional™:
                    Certification #031409-25 <br class="">
                    NABCEP Certified Solar Heating Installer™:
                    Certification #ST032611-03       <br class="">
                    CoSEIA Certified PV Installer <br class="">
                    <br class="">
                    Solar Gain Services, LLC<br class="">
                    PO Box 531<br class="">
                    Monte Vista, CO. 81144<br class="">
                    <a moz-do-not-send="true"
                      href="mailto:SGSRenewables@Gmail.com" class="">SGSRenewables@Gmail.com</a><br
                      class="">
                    719.588.3044<br class="">
                  </font></tt><a moz-do-not-send="true"