<div dir="ltr">Attached is a screenshot of an example calculation from SEI for minimum modules in series for controllers, similar to Jarmo's but more system-specific. And fairly conservative because of the 1.2 factor for degradation over time (which includes voltage drop). Note there are values specific to the site, batteries, and module - this example was for a roof mounted array thus the 30ºC cell temp adder. <div>SEI recommends not going lower than 1.1 times bulk voltage for the target minimum array voltage  although 1.2 is a good target to start with. </div><div><br></div><div>One thing I'd note is that for systems without a generator or other charging source besides PV the target array voltage should be 1.2 times <b>equalize voltage</b> not bulk voltage. And of course a maximum modules in series calc has to be done too. </div><div><br></div><div><img src="cid:ii_14db0227d36e2612" alt="Inline image 1" width="560" height="409">. </div><div><br></div><div>Cheers, </div><div>Rebekah</div><div><div><br></div></div>​</div>