<div dir="ltr">Bill,<div> One clean way to do it would be to use a ConnectDER, but the max input is 11.5 kw. We have used several of these for under 10 k installations and have saved lots of install time. They are not cheap (approx $300+). Our power company sells them to installers. </div><div><br></div><div>John Blittersdorf</div><div>Central Vermont Solar & Wind</div></div><div class="gmail_extra"><br><div class="gmail_quote">On Mon, May 25, 2015 at 12:39 AM, frenergy <span dir="ltr"><<a href="mailto:frenergy@psln.com" target="_blank">frenergy@psln.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><u></u>
<div text="#000000" bgcolor="#ffffff">
<div>Wrenches,</div>
<div> </div>
<div> Customer currently has a hacked up
200 amp Sylvania meter/mains panel. He also is averaging a load of 74
KWhrs/day! which will require about 15 KW system size at this site.
Obviously a system this size cannot backfeed the busses in the load
center. Because the exiting panel is a mess anyway, I'm suggesting it gets
changed out.</div>
<div> </div>
<div> What sort of new 200 amp service
would facilitate a clean supply side connection. One thought is have
separate Utility meter socket then a 12 X 12 J-box with a monster power
distribution block in it and then a distribution panel (without the meter
socket)...this being a way to insert a means to grid-tie between the meter
and the 200 amp main breaker. A little spendy but nothing like going to
higher amp service to be able to load side connect.</div>
<div> </div>
<div> A 400 amp panel is not an option
as the existing 165' of 3" pvc underground conduit to the pole currently has 4/0
alum. The utility says it would have to be 4" for the new cable and the
cost $10K+ for the upgrade.</div>
<div> </div>
<div> Other ideas??</div>
<div> </div>
<div>Thanks in advance</div>
<div> </div>
<div>Bill</div>
<div> </div>
<div>Feather River Solar Electric</div></div>
<br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div>