Hi bill<div><br></div><div>Google solar ready load centers or pump ready load centers </div><div><br></div><div>These both have 60 amp ( is what I've seen) separate breaker spot that is not part of the main buss. </div><div>Which means you also have the 40 amp in the main for 100a total. </div><div><br></div><div>Super clean</div><div><br></div><div>Jay</div><div><br><br>On Monday, May 25, 2015, Mac Lewis <<a href="mailto:maclewis1@gmail.com">maclewis1@gmail.com</a>> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr">Hi Bill,<div><br></div><div>Square D has a nice 225A panel that may work <span style="color:rgb(119,119,119);font-family:Georgia,'Times New Roman',serif;font-size:14px;line-height:21px;white-space:nowrap">Model #</span><span style="color:rgb(119,119,119);font-family:Georgia,'Times New Roman',serif;font-size:14px;line-height:21px;white-space:nowrap"> </span><span style="color:rgb(119,119,119);font-family:Georgia,'Times New Roman',serif;font-size:14px;line-height:21px;white-space:nowrap;margin:0px;padding:0px">QO142L225PG</span>.  If you can work with a 70A backfed breaker, you could use a 200A MCB and do a load side connection.</div><div><br></div><div>Cheers</div></div><div class="gmail_extra"><br><div class="gmail_quote">On Sun, May 24, 2015 at 10:39 PM, frenergy <span dir="ltr"><<a href="javascript:_e(%7B%7D,'cvml','frenergy@psln.com');" target="_blank">frenergy@psln.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><u></u>





<div text="#000000" bgcolor="#ffffff">
<div>Wrenches,</div>
<div> </div>
<div>        Customer currently has a hacked up 
200 amp Sylvania meter/mains panel.  He also is averaging a load of 74 
KWhrs/day! which will require about 15  KW system size at this site.  
Obviously a system this size cannot backfeed the busses in the load 
center.  Because the exiting panel is a mess anyway, I'm suggesting it gets 
changed out.</div>
<div> </div>
<div>        What sort of new 200 amp service 
would facilitate a clean supply side connection.  One thought is have 
separate Utility meter socket then a 12 X 12 J-box with a monster power 
distribution block in it and then a distribution panel (without the meter 
socket)...this being a way to insert a means to grid-tie between the meter 
and the 200 amp main breaker.  A little spendy but nothing like going to 
higher amp service to be able to load side connect.</div>
<div> </div>
<div>        A 400 amp panel is not an option 
as the existing 165' of 3" pvc underground conduit to the pole currently has 4/0 
alum.  The utility says it would have to be 4" for the new cable and the 
cost $10K+ for the upgrade.</div>
<div> </div>
<div>        Other ideas??</div>
<div> </div>
<div>Thanks in advance</div>
<div> </div>
<div>Bill</div>
<div> </div>
<div>Feather River Solar Electric</div></div>
<br>_______________________________________________<br></blockquote></div><div><br></div>-- <br><div><div><br></div><div><font color="#305A78" face="'times new roman', serif"><br></font></div><div><br></div>Mac Lewis<br><br><span style="font-family:'Times New Roman';font-size:medium;color:rgb(255,153,0)"><b><font face="Arial, Helvetica, sans-serif" size="3"><p align="left"><font color="#000000" face="Verdana, Arial, Helvetica, sans-serif"><span style="font-size:small"><span style="font-family:arial;font-weight:normal;color:rgb(48,90,120)"><font face="'times new roman', serif">"Yo solo sé que no sé nada." </font><span style="font-weight:700;color:rgb(104,104,104)"><font face="'times new roman', serif">-Sócrates</font></span></span></span></font></p></font></b></span></div>