<font size=2 face="sans-serif">Hi:</font>
<br>
<br><font size=2 face="sans-serif">The difference is in the accuracy of
revenue grade versus inverter KWh meters.  Revenue grade is typically
much more accurate.</font>
<br>
<br><font size=2 face="sans-serif">Beyond that, even if the accuracy of
both was really good at lets say +/- 0.5%, you could still get a 1% overall
difference in readings as one could be +0.5% and other -0.5%, even though
they are both working to spec.</font>
<br>
<br><font size=2 face="sans-serif">JARMO<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Jarmo Venalainen</b>  |  </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>  |  Xantrex
Brand</b>  |   <b>CANADA</b>  |   <b>Sales Application
Engineer</b> <b><br>
Phone:</b> +604-422-2528  |   <b>Tech Support:</b> 800-670-0707
 |   <b>Mobile:</b> +604-505-0291 <b><br>
Email:</b> </font><a href="mailto:jarmo.venalainen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>jarmo.venalainen@schneider-electric.com</u></font></a><font size=1 face="Arial">
 |   <b>Site:</b></font><a href=http://www.xantrex.com/ target=_blank><font size=1 color=blue face="Arial"><u>
www.Xantrex.com</u></font></a><font size=1 face="Arial">  |  
<b>Address:</b> 3700 Gilmore Way, Burnaby, BC V5G4M1 <br>
</font>
<table>
<tr>
<td colspan=4><a href=http://www.xantrexrebate.com/ target=_blank><img src=cid:_1_0AE839200AE8354C007E6BCF88257E4D width=1 height=1></a>
<tr>
<td><a href=http://www.xantrex.com/ target=_blank><img src=cid:_1_0AE83FF00AE83C1C007E6BCF88257E4D></a>
<td><a href=https://www.facebook.com/Xantrex target=_blank><img src=cid:_1_0AE8478C0AE8438C007E6BCF88257E4D></a>
<td><a href=https://twitter.com/Xantrex target=_blank><img src=cid:_1_0AE84F280AE84B28007E6BCF88257E4D></a>
<td><a href=https://twitter.com/Xantrex target=_blank><img src=cid:_1_0C3E64B80C3E60E4007E6BCF88257E4D></a></table>
<br>
<br><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">Kevin Eigel <kevin@ecohousesolar.com></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">RE-wrenches <RE-wrenches@lists.re-wrenches.org>,
</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">05/22/2015 02:38 PM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">[RE-wrenches] Discrepency between inverter
kWH reading and solar        production meter</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">"RE-wrenches" <re-wrenches-bounces@lists.re-wrenches.org></font></table>
<br>
<hr noshade>
<br>
<br>
<br><font size=3>I recently installed a Solaredge 7600 inverter and two
feet away from it installed a GE 210 solar kWh utility grade meter. Over
the course of three months the kWh production measured by the inverter
is more than 200 kWh greater then the production showing on the GE meter.
I  changed out the GE meter for the last week and the discrepancy
has continued, so it looks like it is not the meter.</font>
<br><font size=3>I am looking for any help in understanding whey there
is this large discrepancy on the kWh reading between the inverter and the
production meter, when they are so close together. The Solaredge technical
help desk has been of no use.</font>
<br>
<br><font size=3>-- </font>
<br><font size=3>Kevin Eigel</font>
<br><font size=3>President</font>
<br><font size=3>Ecohouse Solar</font>
<br><font size=3>1857 Northwest Blvd. Ste 201, Columbus, OH 43212</font>
<br><font size=3>www,</font><a href=http://ecohousesolar.com/ target=_blank><font size=3 color=blue><u>ecohousesolar.com</u></font></a>
<br><font size=3>614-805-5776</font>
<br><font size=3><br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________</font><tt><font size=2>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change listserver email address & settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"><tt><font size=2>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</font></tt></a><tt><font size=2><br>
<br>
List rules & etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out or update participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
</font></tt>
<br>
<br>