<div dir="ltr">Heating the regulator won't help if the propane is not vapourizing. You would need to heat the tank.<div>However, you do not need to heat it very much, just enough to let it vapourize. Think about putting it somewhere with a little heat, or burying it.</div></div><div class="gmail_extra"><br><div class="gmail_quote">On Fri, Apr 3, 2015 at 1:51 PM, Larry <span dir="ltr"><<a href="mailto:larry@starlightsolar.com" target="_blank">larry@starlightsolar.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div text="#000000" bgcolor="#FFFFFF">
    About the carb heat idea...LP is a liquid at -44°F. The liquid does
    not combust, it must be vaporized. As the ambient temperature drops
    closer to the LP liquid temperature, there would be a reduction in
    how fast liquid is vaporizing and therefor a reduction in volume.
    What you need in cold weather is enough volume to maintain at least
    11" wc while cranking or running the engine. You can test the vapor
    pressure with a manometer while cranking to verify if this is the
    problem. <br>
    <br>
    If this is the reason the engine does not run, my thoughts are that
    heating the LP regulator would be much more economical from an
    energy standpoint, than heating the whole engine block. Perhaps an
    insulated enclosure with silicone heaters appropriately attached
    would work. They are available in many DC or AC and at various
    voltages.<br>
    <pre cols="72">Larry Crutcher
Starlight Solar Power Systems
</pre><span class="">
    <div>On 4/2/15 10:34 PM, Allan Sindelar
      wrote:<br>
    </div>
    <blockquote type="cite">
      
      Gary,<br>
      Mac's approach is intelligent and will work well, as an automated
      system with the right hardware. We took a quite different approach
      on a somewhat similar scenario in 2009.<br>
      <br>
      This was a Kohler 8.5REZ, with the electric carb heater and AC
      charter for the starting battery. No block heater, but that could
      have been handled the same way. The inverter was a Magnum
      MS4024PAE, but that doesn't matter here. When we ran the bundle of
      gennie output conductors, we added a separate load circuit
      conductor, on its own breaker in the system E-Panel. Here's an
      excerpt from the original proposal description about our approach:<br>
      <blockquote><u></u>
          
          
          
          
          <p class="MsoNormal"><span style="font-size:12.0pt">The
              unit uses an electronic generator controller with modest
              (estimated at 200-700 mA, depending on state of operation)
              draw on the starting battery. This controller drops to
              minimal “sleep” draw automatically after 48 hours of
              non-operation. This generator does not have a starting
              battery charging coil, but rather uses a separate AC
              battery trickle charger to maintain the battery. I will
              install a 20W PV module and small charge controller on the
              generator to keep the starting battery charged. I will
              also install the AC charger to operate whenever the
              generator is running. While this combined setup has worked
              successfully for other installers with whom I have spoken,
              if this proves insufficient I can later add a switch and
              relay to allow the charger to also operate off of inverter
              AC if ever needed.<u></u><u></u></span></p>
          <p class="MsoNormal"><span style="font-size:12.0pt"><u></u> <u></u></span></p>
          <p class="MsoNormal"><span style="font-size:12.0pt">The
              unit also requires a built-in carburetor heater to operate
              during cold weather. This heater is normally controlled by
              a thermostat to conservatively come on at or below 40°F,
              which would mean that it would operate nearly continuously
              during <u></u><u></u>Taos<u></u><u></u>’
              winter months, draining the PV system. My solution is to
              put the carburetor heater on a manual mechanical one-hour
              time switch located at the generator; you will activate
              the heater through this switch 15-30 minutes before
              starting the generator. <u></u><u></u></span></p>
        <u></u></blockquote>
      This may not work for you. This is a modern doublewide serving as
      a seasonal family meeting place, rather than a full time
      residence. With our usual sunny winters, we figure that if nobody
      is there, loads are minimal, and we don't want automatic
      (unattended) generator operation. I think we used a DG WP box
      inside the generator enclosure, with a mechanical timer (maybe
      one-hour) controlling a GFCI receptacle, with carb heater and
      battery charger plugged in.<br>
      <br>
      I hope that gives you some ideas you can use.<br>
      <br>
      <div>
        
        
        
        
        
        
        
        
        
        
        <div>
          <p class="MsoNormal"><b>Allan Sindelar</b><br>
            <span style="font-size:10.0pt"><a href="mailto:allan@sindelarsolar.com" target="_blank">allan@sindelarsolar.com</a></span><br>
            <span style="font-size:10.0pt">NABCEP Certified PV
              Installation Professional<br>
              NABCEP Certified Technical Sales Professional<br>
              New Mexico EE98J Journeyman Electrician<br>
              Founder (Retired), <span>Positive Energy, Inc.</span><br>
              <b><a href="tel:505%20780-2738" value="+15057802738" target="_blank">505 780-2738</a> cell</b><br>
              <br>
              <b><u></u><u></u></b></span></p>
          <p class="MsoNormal"><u></u> <u></u></p>
        </div>
      </div>
      <br>
    </blockquote>
    <br>
  </span></div>

<br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br><div class="gmail_signature"><div dir="ltr">Chris Mason<div><div style="color:rgb(136,136,136)"><span style="font-size:13px">NABCEP Certified Solar PV Installer™</span></div><div style="color:rgb(136,136,136)"><span style="color:rgb(34,34,34)">Solar Design Engineer</span></div><div style="color:rgb(136,136,136)"><span style="font-size:13px">Generac Generators Industrial technician</span></div></div><div style="color:rgb(136,136,136)"><span style="font-size:13px"><br></span></div><div><a href="http://www.cometenergysystems.com" target="_blank">www.cometsolar.com</a></div><div>264.235.5670</div><div>869.662.5670</div><div>Skype: netconcepts</div></div></div>
</div>