<DIV><SPAN class=232323617-16032015><FONT face=Arial color=#0000ff size=2>Thanks 
for everyone's advise on this one. I've done as much as I can working with the 
caretaker remotely and will need to attend myself with some test gear to fully 
diagnose. </FONT></SPAN><SPAN class=232323617-16032015><FONT face=Arial 
color=#0000ff size=2>This site is remote (10h of driving then 1h boat ride). I 
generally make a point of avoiding Outback product so feel much better informed 
to diagnose when onsite - later in the week. Thanks. </FONT></SPAN></DIV>
<DIV><SPAN class=232323617-16032015><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=232323617-16032015><FONT face=Arial color=#0000ff 
size=2>Curious what is going on with Outback's tech support. I waited on hold 
for a bit on Wednesday, then left a message for callback and am still waiting 
for that callback 3 business days later. </FONT></SPAN></DIV>
<DIV><SPAN class=232323617-16032015><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN><SPAN class=232323617-16032015><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=232323617-16032015><FONT face=Arial color=#0000ff size=2>My 
client is most upset that Outback can't even bother to return a tech call. 
His instructions to me are if</FONT></SPAN><SPAN 
class=232323617-16032015><FONT face=Arial color=#0000ff size=2> we find multiple 
failed components in the system and not simple fixes to remove the gear and 
replace with "anything as long as it's not Outback". </FONT></SPAN></DIV>
<DIV><SPAN class=232323617-16032015><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=232323617-16032015><FONT face=Arial color=#0000ff size=2>Will 
advise the list what was discovered once onsite. </FONT></SPAN></DIV>
<DIV><SPAN class=232323617-16032015><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=232323617-16032015><FONT face=Arial color=#0000ff 
size=2>Kevin</FONT></SPAN></DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma 
  size=2>-----Original Message-----<BR><B>From:</B> RE-wrenches 
  [mailto:re-wrenches-bounces@lists.re-wrenches.org]<B>On Behalf Of 
  </B>frenergy<BR><B>Sent:</B> March 16, 2015 6:38 AM<BR><B>To:</B> 
  RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] Outback quad stack X240 
  breaker tripping<BR><BR></FONT></DIV>
  <DIV>Kevin,</DIV>
  <DIV> </DIV>
  <DIV>        Not to add any confusion but I 
  recently had to re-program the slave in a 2 VFX with Xfrmr system as it was 
  doing the same thing...the 2 pole xfrmr breaker was tripping when a moderate 
  load was on.  Granted this was not happening during charging 
  though.  I think I changed the slave from OB slave L1 to OB slave L2 and 
  all was good.  It doesn't seem likely the programming in your case would 
  have been messed with having been working well for years prior.  Curious 
  to hear though of a solution eventually.</DIV>
  <DIV> </DIV>
  <DIV>Bill</DIV>
  <DIV> </DIV>
  <DIV>Feather River Solar Electric<BR>4291 Nelson St.<BR>Taylorsville, CA  
  95983<BR>530.284.7849 / 6544 fax</DIV>
  <BLOCKQUOTE 
  style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
    <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
    <DIV 
    style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
    <A title=tump@swnl.net href="mailto:tump@swnl.net">Tump</A> </DIV>
    <DIV style="FONT: 10pt arial"><B>To:</B> <A 
    title=re-wrenches@lists.re-wrenches.org 
    href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
    <DIV style="FONT: 10pt arial"><B>Sent:</B> Monday, March 16, 2015 5:39 
    AM</DIV>
    <DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [RE-wrenches] Outback quad 
    stack X240 breaker tripping</DIV>
    <DIV><BR></DIV>Have you turned the breaker on the t240 to the off position? 
    One does NOT have to have that operational for the system to operate 
    correctly.The old t240 has about the same parasitic draw as an inverter. 
    Isolate, Isolate, Isolate. If the system functions correctly w/ the t240 off 
    and the stacking is correct on this q stack disconnect it(the t240). 
    Otherwise I would remove the inverter com cables and only connect 1 pair of 
    inverters at a time, reset the mate with the correct com cables connected to 
    P1& P2. Sometimes something so simple as disconnecting & 
    reconnection the mate can have quite a benefit. Again I would, if you are 
    really stuck on having the t240 operational, then try it with each inverter 
    as a single unit then try the second set of inverters. Disconnect the 
    #s1&2 inverters and do the same; connect #s 3&4 P1 & P2, to see 
    exactly which component may be your problem. 
    <DIV>You are more then happy to contact me off list if you choose. contact 
    info below. Tump<BR>
    <DIV>
    <DIV>
    <DIV>On Mar 15, 2015, at 5:04 PM, Jerry Shafer wrote:</DIV><BR 
    class=Apple-interchange-newline>
    <BLOCKQUOTE type="cite">
      <DIV dir=ltr>
      <DIV> Wrenches<BR>OK if the X240 blows the fuse which is on the 
      output of the inverter while the inverter is charging, excessive current 
      must be passing through from one inverter and back to the output of 
      another inverter ( a form of AC coupling gone bad). The time delay fits as 
      the inverter ramps up, I would look at the contactors in each slave as one 
      may be hanging or ther may be a bad board, easy way to test is to isolate 
      each inverter and with a amp meter connected at the X240 see if current 
      goes away in the X240 as it should not be doing much with light loads on 
      the "House" side of the inverters. The X240 is 25 amps while the inverters 
      are 50 amps. Sounds like a interesting one to 
      diagnose.<BR></DIV>Jerry<BR></DIV>
      <DIV class=gmail_extra><BR>
      <DIV class=gmail_quote>On Wed, Mar 11, 2015 at 11:59 AM, Chris Worcester 
      <SPAN dir=ltr><<A href="mailto:chris@solarwindworks.com" 
      target=_blank>chris@solarwindworks.com</A>></SPAN> wrote:<BR>
      <BLOCKQUOTE class=gmail_quote 
      style="PADDING-LEFT: 1ex; MARGIN: 0px 0px 0px 0.8ex; BORDER-LEFT: #ccc 1px solid">
        <DIV>
        <DIV>Hi Kevin, </DIV>
        <DIV>I have seen the  X240's  trip off like this when theyare 
        over loaded. When this was happening to us the slave inverters had blown 
        AC  boards and some times Control and FET boards too. We had a hard 
        time diagnosing this as their  green lights were on.  Using a 
        clamp on  amp meter on each inverter's AC IN conductor while 
        charging with the gen set allowed us to compare their charging currents 
        to each other. Typically the ones with blown  AC boards output 
        would be close to zero amps. So the X240's were doing double duty and 
        they will smoke too if the inverters aren't delta with. </DIV>
        <DIV><BR></DIV>
        <DIV><BR></DIV>Sincerely, <SPAN class=HOEnZb><FONT color=#888888> 
        <DIV>Chris Worcester</DIV>
        <DIV><A href="tel:530-448-9692" target=_blank 
        value="+15304489692">530-448-9692</A>  
        <DIV> Sent from my Galaxy S®III</DIV></DIV></FONT></SPAN><SPAN 
        class=""><BR><BR>
        <DIV>-------- Original message --------</DIV>
        <DIV>From: Kevin Pegg <U></U></DIV>
        <DIV>Date:03/11/2015 1:19 PM (GMT-08:00) </DIV>
        <DIV>To: RE-wrenches <U></U></DIV>
        <DIV>Subject: [RE-wrenches] Outback quad stack X240 breaker tripping 
        </DIV>
        <DIV><BR></DIV>Hello Wrenches, <BR><BR>Customer in remote location has a 
        strange situation come up on an existing system installed (by others) 6 
        or so years go. Quad stack VFX3648. <BR><BR>Last night gen start was 
        triggered by low voltage - a normal system operation. <BR><BR>Approx 1h 
        into charge, they lost 1/2 the circuits in house - L2 de-energized. 
        Caretaker went to check power system and noticed the X240 breakers 
        tripped. Tried to reset but it tripped out right away. So he left it as 
        is and called me in the morning. <BR><BR>Here's what I've been able to 
        determine today: <BR><BR>- The x240 is installed to bridge L1 & L2 
        on the load side. <BR>- with master inverter on, 3 slaves off, both L1 
        and L2 energized so suggests x240 is working. <BR>- within 10 seconds of 
        generator on and charging, x240 breaker trips (and makes L2 go dark). 
        <BR>- loads are minor, ~1,000 w of misc lights and such, isn't all 
        loaded up on one leg. <BR><BR>Appreciate any thoughts to remedy. I'm not 
        as familiar with this config as others. <BR><BR>Kevin Pegg<BR>EA Energy 
        Alternatives Ltd. <BR>37471 Hwy 16 E<BR>Telkwa, BC  V0J 2X2<BR><A 
        href="tel:250-846-9888" target=_blank 
        value="+12508469888">250-846-9888</A><BR><A 
        href="http://www.EnergyAlternatives.ca/" 
        target=_blank>Http://www.EnergyAlternatives.ca</A> 
        <BR><BR><BR><BR></SPAN><SPAN 
        class="">_______________________________________________<BR>List 
        sponsored by Redwood Alliance<BR><BR>List Address: <A 
        href="mailto:RE-wrenches@lists.re-wrenches.org" 
        target=_blank>RE-wrenches@lists.re-wrenches.org</A><BR><BR>Change 
        listserver email address & settings:<BR><A 
        href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" 
        target=_blank>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: 
        <A 
        href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" 
        target=_blank>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</A><BR><BR>List 
        rules & etiquette:<BR><A 
        href="http://www.re-wrenches.org/etiquette.htm" 
        target=_blank>www.re-wrenches.org/etiquette.htm</A><BR><BR>Check out or 
        update participant bios:<BR><A 
        href="http://www.members.re-wrenches.org/" 
        target=_blank>www.members.re-wrenches.org</A><BR><BR></SPAN></DIV><BR>_______________________________________________<BR>List 
        sponsored by Redwood Alliance<BR><BR>List Address: <A 
        href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Change 
        listserver email address & settings:<BR><A 
        href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" 
        target=_blank>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: 
        <A 
        href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" 
        target=_blank>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</A><BR><BR>List 
        rules & etiquette:<BR><A 
        href="http://www.re-wrenches.org/etiquette.htm" 
        target=_blank>www.re-wrenches.org/etiquette.htm</A><BR><BR>Check out or 
        update participant bios:<BR><A 
        href="http://www.members.re-wrenches.org/" 
        target=_blank>www.members.re-wrenches.org</A><BR><BR><BR></BLOCKQUOTE></DIV><BR></DIV>_______________________________________________<BR>List 
      sponsored by Redwood Alliance<BR><BR>List Address: <A 
      href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Change 
      listserver email address & settings:<BR><A 
      href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: 
      http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html<BR><BR>List 
      rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check 
      out or update participant 
    bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></DIV><BR>
    <DIV><SPAN class=Apple-style-span 
    style="WORD-SPACING: 0px; FONT: medium Times; TEXT-TRANSFORM: none; COLOR: rgb(0,0,0); TEXT-INDENT: 0px; WHITE-SPACE: normal; LETTER-SPACING: normal; BORDER-COLLAPSE: separate; orphans: 2; widows: 2; webkit-border-horizontal-spacing: 0px; webkit-border-vertical-spacing: 0px; webkit-text-decorations-in-effect: none; webkit-text-size-adjust: auto; webkit-text-stroke-width: 0px">
    <DIV>
    <BLOCKQUOTE type="cite">
      <DIV 
      style="WORD-WRAP: break-word; webkit-nbsp-mode: space; webkit-line-break: after-white-space">
      <DIV><SPAN class=Apple-style-span 
      style="WORD-SPACING: 0px; FONT: medium Times; TEXT-TRANSFORM: none; TEXT-INDENT: 0px; WHITE-SPACE: normal; LETTER-SPACING: normal; BORDER-COLLAPSE: separate; orphans: 2; widows: 2; webkit-border-horizontal-spacing: 0px; webkit-border-vertical-spacing: 0px; webkit-text-decorations-in-effect: none; webkit-text-size-adjust: auto; webkit-text-stroke-width: 0px"><SPAN 
      class=Apple-style-span 
      style="WORD-SPACING: 0px; FONT: medium Times; TEXT-TRANSFORM: none; TEXT-INDENT: 0px; WHITE-SPACE: normal; LETTER-SPACING: normal; BORDER-COLLAPSE: separate; orphans: 2; widows: 2; webkit-border-horizontal-spacing: 0px; webkit-border-vertical-spacing: 0px; webkit-text-decorations-in-effect: none; webkit-text-size-adjust: auto; webkit-text-stroke-width: 0px">
      <DIV 
      style="WORD-WRAP: break-word; webkit-nbsp-mode: space; webkit-line-break: after-white-space"><SPAN 
      class=Apple-style-span 
      style="FONT-SIZE: 12px; FONT-FAMILY: 'Times New Roman'"><B><A 
      href="blocked::mailto:Tump@swnl.net%22%20%5Co%20%22blocked::mailto:Tump@swnl.net">Tump@swnl.net</A></B><SPAN 
      style="FONT: 12px Arial"> </SPAN>          
          <A 
      href="blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/"><B>www.SWNL.net</B></A></SPAN><SPAN 
      class=Apple-style-span 
      style="FONT-SIZE: medium; WORD-SPACING: 0px; TEXT-TRANSFORM: none; TEXT-INDENT: 0px; LINE-HEIGHT: normal; FONT-STYLE: normal; FONT-FAMILY: Helvetica; WHITE-SPACE: normal; LETTER-SPACING: normal; BORDER-COLLAPSE: separate; FONT-VARIANT: normal; orphans: 2; widows: 2; webkit-border-horizontal-spacing: 0px; webkit-border-vertical-spacing: 0px; webkit-text-decorations-in-effect: none; webkit-text-size-adjust: auto; webkit-text-stroke-width: 0px"> 

      <DIV 
      style="WORD-WRAP: break-word; webkit-nbsp-mode: space; webkit-line-break: after-white-space"><SPAN 
      class=Apple-style-span 
      style="FONT-SIZE: medium; WORD-SPACING: 0px; TEXT-TRANSFORM: none; TEXT-INDENT: 0px; LINE-HEIGHT: normal; FONT-STYLE: normal; FONT-FAMILY: Helvetica; WHITE-SPACE: normal; LETTER-SPACING: normal; BORDER-COLLAPSE: separate; FONT-VARIANT: normal; orphans: 2; widows: 2; webkit-border-horizontal-spacing: 0px; webkit-border-vertical-spacing: 0px; webkit-text-decorations-in-effect: none; webkit-text-size-adjust: auto; webkit-text-stroke-width: 0px">
      <DIV 
      style="WORD-WRAP: break-word; webkit-nbsp-mode: space; webkit-line-break: after-white-space">
      <DIV>
      <DIV 
      style="MARGIN: 0px; FONT: 12px 'Times New Roman'">   <SPAN 
      style="FONT-WEIGHT: normal; COLOR: rgb(45,44,250)">      
             </SPAN><SPAN 
      style="FONT: 18px 'Times New Roman'; COLOR: rgb(45,44,250)">Solarwinds 
      Northernlights</SPAN>   <B 
      style="FONT-WEIGHT: normal"><I>    </I></B></DIV>
      <DIV style="MARGIN: 0px; FONT: 10px 'Times New Roman'"><SPAN 
      style="FONT: 12px 'Times New Roman'"><B><I>      
       Serving Mid Coast Maine & Northern 
      California</I></B></SPAN><SPAN 
      style="FONT: 10px Arial"><B><I><BR></I></B></SPAN><B><I>    
                          
       207-832-7574   Cl. 
      610-517-8401                              </I></B></DIV>
      <DIV style="MARGIN: 0px; FONT: 12px 'Times New Roman'"><SPAN 
      style="COLOR: rgb(45,44,250)"><B><I>          
                        
        </I></B></SPAN><B><I>Blair "TUMP" May</I></B></DIV>
      <P 
      style="MARGIN: 5px 0px; FONT: 12px 'Times New Roman'; COLOR: rgb(0,144,25)"><SPAN 
      style="COLOR: rgb(0,0,0)"><B><I>            
         ********  MAINE'S CHARTER 
      ********<BR> </I></B></SPAN><B><I>                  
       </I></B><SPAN style="TEXT-DECORATION: underline"><B><I>  
      NABCEP    "Certified PV Installer"</I></B></SPAN><SPAN 
      style="COLOR: rgb(0,0,0); TEXT-DECORATION: underline"><B><I> <BR></I></B></SPAN><SPAN 
      style="COLOR: rgb(0,0,0)"><B><I>   <BR>            
        ********  MAINE'S CHARTER 
      ********<BR>          </I></B></SPAN><SPAN 
      style="TEXT-DECORATION: underline"><B><I>        
      Trace Xantrex "Certified" Dealer / Installer"</I></B></SPAN></P>
      <DIV 
      style="MIN-HEIGHT: 15px; MARGIN: 0px; FONT: 12px 'Times New Roman'"><BR></DIV></DIV></DIV></SPAN></DIV></SPAN></DIV></SPAN></SPAN></DIV></DIV></BLOCKQUOTE></DIV></SPAN><BR 
    class=Apple-interchange-newline></DIV><BR></DIV></DIV>
    <P>
    <HR>

    <P></P>_______________________________________________<BR>List sponsored by 
    Redwood Alliance<BR><BR>List Address: 
    RE-wrenches@lists.re-wrenches.org<BR><BR>Change listserver email address 
    & 
    settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html<BR><BR>List 
    rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
    or update participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BLOCKQUOTE></BODY></HTML>