<font size=2 face="sans-serif">Hi:</font>
<br>
<br><font size=2 face="sans-serif">One thing to keep in mind with clipping,
(module over sizing), is that if a system has 10%-15% off clipping, that
will not affect total annual energy harvest and depending on dust and temperature
conditions will likely even improve it.</font>
<br>
<br><font size=2 face="sans-serif">Heres' a graph which shows the energy
harvest graphically for a 250W module with a 250W inverter and a and 300W
module with a 250W inverter.</font>
<br>
<br><img src=cid:_1_0C7FCB680C7FA7D000635D8188257DE8><font size=2 face="sans-serif"> 
</font>
<br><font size=2 face="sans-serif">Please note the graph does not include
any dust effects.  To compensate for dust, the modules should always
be of the order of 4% more powerful than the inverter, unless you plan
on washing modules every month.</font>
<br>
<br><font size=2 face="sans-serif">Related to this, large commercial systems
we have been supplying inverters to are 30-70% oversized as the sinking
cost of modules makes the return on investment come out as maximized in
that range of oversizing,</font>
<br>
<br><font size=2 face="sans-serif">JARMO <br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Jarmo Venalainen</b>  |  </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>  |  Xantrex
Brand</b>  |   <b>CANADA</b>  |   <b>Sales Application
Engineer</b> <b><br>
Phone:</b> +604-422-2528  |   <b>Tech Support:</b> 800-670-0707
 |   <b>Mobile:</b> +604-505-0291 <b><br>
Email:</b> </font><a href="mailto:jarmo.venalainen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>jarmo.venalainen@schneider-electric.com</u></font></a><font size=1 face="Arial">
 |   <b>Site:</b></font><a href=http://www.xantrex.com/ target=_blank><font size=1 color=blue face="Arial"><u>
www.Xantrex.com</u></font></a><font size=1 face="Arial">  |  
<b>Address:</b> 3700 Gilmore Way, Burnaby, BC V5G4M1 <br>
</font>
<table>
<tr>
<td colspan=4><a href=http://www.xantrexrebate.com/ target=_blank></a>
<tr>
<td><a href=http://www.xantrex.com/ target=_blank></a>
<td><a href=https://www.facebook.com/Xantrex target=_blank></a>
<td><a href=https://twitter.com/Xantrex target=_blank></a>
<td><a href=https://twitter.com/Xantrex target=_blank></a></table>
<br>
<br><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">Drake <drake.chamberlin@redwoodalliance.org></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">RE-wrenches <re-wrenches@lists.re-wrenches.org>,
</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">02/10/2015 06:51 AM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">Re: [RE-wrenches] 300W 72 cell micro
inverters</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">"RE-wrenches" <re-wrenches-bounces@lists.re-wrenches.org></font></table>
<br>
<hr noshade>
<br>
<br>
<br><tt><font size=2>That  would be at the 120% rating, so by rule
of <br>
thumb, OK. I have a ground mount that has a <br>
ration of 1.15% with M-190s (figuring 199 W / <br>
inverter). It has quite a bit of clipping in the <br>
spring. It has optimized tilt for the location. A <br>
ballasted roof mount with a 10 or 15 degree tilt <br>
likely wouldn't have that issue.<br>
<br>
This system went in the spring of 2010, and has <br>
only  had one M-190 failure out of 24, amazingly enough.<br>
<br>
At 10:22 AM 2/9/2015, you wrote:<br>
>What do you typically get out of a 300 watt panel for production when
you<br>
>are grid tied? I know in theory (STC) it is a 300 watt module but we<br>
>rarely if ever (except in very cold weather)see near that for an output.
I<br>
>use (as a general, 77 degrees F) design parameter, 77% for overall
power<br>
>production output output. I'm sure you would get a little clipping,
but I<br>
>guess a significant amount would depend on a number of variables on
the<br>
>site, time of the year, weather conditions, etc.<br>
><br>
>Daryl<br>
><br>
><br>
> > Yeah....if you're OK with a not insignificant amount of clipping
going on.<br>
> ><br>
> > -----Original Message-----<br>
> > From: RE-wrenches [</font></tt><a href="mailto:re-wrenches-bounces@lists.re-wrenches.org"><tt><font size=2>mailto:re-wrenches-bounces@lists.re-wrenches.org</font></tt></a><tt><font size=2>]
On<br>
> > Behalf Of penobscotsolar@midmaine.com<br>
> > Sent: Sunday, February 08, 2015 2:33 PM<br>
> > To: RE-wrenches<br>
> > Subject: Re: [RE-wrenches] 300W 72 cell micro inverters<br>
> ><br>
> > Hey Jason,<br>
> >    The M-250's work well with LG 300 watt (60 cell)
modules.<br>
> ><br>
> > Daryl<br>
> ><br>
> ><br>
> >> Hi Jason,<br>
> >><br>
> >> The Enphase C250 Microinverters for three-phase commercial<br>
> >> applications does work with 72 cell modules.<br>
> >><br>
> >> On Sun, Feb 8, 2015 at 12:58 PM, Jason Szumlanski <<br>
> >> jason@floridasolardesigngroup.com> wrote:<br>
> >><br>
> >>> The ABB micros seem to be solid and easy to install.
We have two<br>
> >>> sites with them with no issues. Unfortunately, the monitoring
system<br>
> >>> sucks compared to Enphase and was far more difficult
to set up. I<br>
> >>> really wish Enphase would come up with a good 72 cell
option because<br>
> >>> we find ourselves competing with 300W modules occasionally,
and<br>
> >>> consumers (irrationally) jump to the conclusion that
bigger is<br>
> >>> better.<br>
> >>><br>
> >>><br>
> >>> [image: Logo-Sq-80.png]<br>
> >>><br>
> >>> Jason Szumlanski<br>
> >>><br>
> >>> Principal Solar Designer<br>
> >>><br>
> >>> Florida Solar Design Group<br>
> >>><br>
> >>> (239) 491-8010 office<br>
> >>><br>
> >>> (239) 410-4985 mobile<br>
> >>><br>
> >>> Authorized Sales Agent for Fafco Solar<br>
> >>><br>
> >>> [image: Fafco-Solar-Enphase-Logo.png]<br>
> >>><br>
> >>> License CVC56701<br>
> >>><br>
> >>><br>
> >>> On Sun, Feb 8, 2015 at 3:15 PM, Bill Hennessy <bill@berkssolar.com><br>
> >>> wrote:<br>
> >>><br>
> >>>> Hi folks--<br>
> >>>><br>
> >>>> We're planning a micro inverter install using 300W
72 cell modules<br>
> >>>> for an area with a fair amount of shading. The choices
we've found<br>
> >>>> are ABB micro<br>
> >>>> 0.3 or APS YC500A.<br>
> >>>> Any stories to tell about either of these or another
suggestion?<br>
> >>>><br>
> >>>> Thanks for your time.<br>
> >>>><br>
> >>>> Bill Hennessy<br>
> >>>> Berks Solar, LLC<br>
> >>>> 371 Centennial Rd<br>
> >>>> Mertztown, PA 19539<br>
> >>>><br>
> >>>> o 610 682 4300<br>
> >>>> c 484 560 4666<br>
> >>>> NABCEP certified installer<br>
> >>>> PA contractor #44411<br>
> >>>> </font></tt><a href=www.berkssolar.com><tt><font size=2>www.berkssolar.com</font></tt></a><tt><font size=2><br>
> >>>><br>
> >>>><br>
> >>>><br>
> >>>><br>
> >>>><br>
> >>>><br>
> >>>><br>
> >>>><br>
> >>>> _______________________________________________<br>
> >>>> List sponsored by Redwood Alliance<br>
> >>>><br>
> >>>> List Address: RE-wrenches@lists.re-wrenches.org<br>
> >>>><br>
> >>>> Change listserver email address & settings:<br>
> >>>> </font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
> >>>><br>
> >>>> List-Archive:<br>
> >>>> </font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/mailli"><tt><font size=2>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/mailli</font></tt></a><tt><font size=2><br>
> >>>> st.html<br>
> >>>><br>
> >>>> List rules & etiquette:<br>
> >>>> </font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
> >>>><br>
> >>>> Check out or update participant bios:<br>
> >>>> </font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
> >>>><br>
> >>>><br>
> >>>><br>
> >>><br>
> >>> *Florida Solar Design Group is not an engineering or
architectural<br>
> >>> firm and acts only as a consultant and authorized independent
sales<br>
> >>> agent.<br>
> >>> Any<br>
> >>> advice or work product provided shall not be considered
licensed<br>
> >>> professional services provided under Florida Statute
Chapters 471,<br>
> >>> 481, or<br>
> >>> 491.*<br>
> >>> _______________________________________________<br>
> >>> List sponsored by Redwood Alliance<br>
> >>><br>
> >>> List Address: RE-wrenches@lists.re-wrenches.org<br>
> >>><br>
> >>> Change listserver email address & settings:<br>
> >>> </font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
> >>><br>
> >>> List-Archive:<br>
> >>> </font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillis"><tt><font size=2>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillis</font></tt></a><tt><font size=2><br>
> >>> t.html<br>
> >>><br>
> >>> List rules & etiquette:<br>
> >>> </font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
> >>><br>
> >>> Check out or update participant bios:<br>
> >>> </font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
> >>><br>
> >>><br>
> >>><br>
> >><br>
> >><br>
> >> --<br>
> >><br>
> >> Cordially,<br>
> >><br>
> >> Nick Soleil<br>
> >> *Enphase Energy* | Field Applications Engineer<br>
> >><br>
> >> office 707-763-4784 <%28707%29%20763.%204784> x7267
cell 07-321-2937<br>
> >><br>
> >> <</font></tt><a href=http://enphase.com/><tt><font size=2>http://enphase.com/</font></tt></a><tt><font size=2>><br>
> >><br>
> >> *Powering What’s Next*â„¢* | *The Enphase
Energy Management<br>
> >> System<br>
> >> <</font></tt><a href=http://ow.ly/HbVS3><tt><font size=2>http://ow.ly/HbVS3</font></tt></a><tt><font size=2>>
<</font></tt><a href=http://community.enphaseenergy.com/><tt><font size=2>http://community.enphaseenergy.com/</font></tt></a><tt><font size=2>><br>
> >> <</font></tt><a href=http://facebook.com/EnphaseEnergy><tt><font size=2>http://facebook.com/EnphaseEnergy</font></tt></a><tt><font size=2>><br>
> >> <</font></tt><a href=http://twitter.com/Enphase><tt><font size=2>http://twitter.com/Enphase</font></tt></a><tt><font size=2>><br>
> >> <</font></tt><a href="http://linkedin.com/company/enphase-energy"><tt><font size=2>http://linkedin.com/company/enphase-energy</font></tt></a><tt><font size=2>><br>
> >><br>
> >><br>
> >> NABCEP Certified Solar PV Installer #03262011-300<br>
> >><br>
> >> California C10 Licensed Electrician #986315<br>
> >><br>
> >> Texas Master Electrician #284451<br>
> >><br>
> >> <nsoleil@enphaseenergy.com><br>
> >><br>
> >> Ã¢â‚¬Å“Don’t get me wrong: I love nuclear energy!
It’s<br>
> >> just that I<br>
> >> prefer fusion to fission. And it just so happens that there’s
an<br>
> >> enormous fusion reactor safely banked a few million miles
from us. It<br>
> >> delivers more than we could ever use in just about 8 minutes.
And<br>
> >> it’s wireless!”<br>
> >><br>
> >> - William McDonough<br>
> >><br>
> >><br>
> >><br>
> >> This email message is for the sole use of the intended recipient(s)<br>
> >> and may contain confidential and/or privileged information.
If you are<br>
> >> not an intended recipient, you may not review, use, copy,
disclose or<br>
> >> distribute this message. If you received this message in
error, please<br>
> >> contact the sender by reply email and destroy all copies
of the original<br>
> >> message.<br>
> >><br>
> > _______________________________________________<br>
> >> List sponsored by Redwood Alliance<br>
> >><br>
> >> List Address: RE-wrenches@lists.re-wrenches.org<br>
> >><br>
> >> Change listserver email address & settings:<br>
> >> </font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
> >><br>
> >> List-Archive:<br>
> >> </font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist"><tt><font size=2>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist</font></tt></a><tt><font size=2><br>
> >> .html<br>
> >><br>
> >> List rules & etiquette:<br>
> >> </font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
> >><br>
> >> Check out or update participant bios:<br>
> >> </font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
> >><br>
> >><br>
> ><br>
> ><br>
> > _______________________________________________<br>
> > List sponsored by Redwood Alliance<br>
> ><br>
> > List Address: RE-wrenches@lists.re-wrenches.org<br>
> ><br>
> > Change listserver email address & settings:<br>
> > </font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
> ><br>
> > List-Archive:<br>
> > </font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"><tt><font size=2>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</font></tt></a><tt><font size=2><br>
> ><br>
> > List rules & etiquette:<br>
> > </font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
> ><br>
> > Check out or update participant bios:<br>
> > </font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
> ><br>
> ><br>
> > _______________________________________________<br>
> > List sponsored by Redwood Alliance<br>
> ><br>
> > List Address: RE-wrenches@lists.re-wrenches.org<br>
> ><br>
> > Change listserver email address & settings:<br>
> > </font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
> ><br>
> > List-Archive:<br>
> > </font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"><tt><font size=2>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</font></tt></a><tt><font size=2><br>
> ><br>
> > List rules & etiquette:<br>
> > </font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
> ><br>
> > Check out or update participant bios:<br>
> > </font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
> ><br>
> ><br>
><br>
><br>
>_______________________________________________<br>
>List sponsored by Redwood Alliance<br>
><br>
>List Address: RE-wrenches@lists.re-wrenches.org<br>
><br>
>Change listserver email address & settings:<br>
></font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
><br>
>List-Archive: <br>
></font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"><tt><font size=2>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</font></tt></a><tt><font size=2><br>
><br>
>List rules & etiquette:<br>
></font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
><br>
>Check out or update participant bios:<br>
></font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change listserver email address & settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"><tt><font size=2>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</font></tt></a><tt><font size=2><br>
<br>
List rules & etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out or update participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________<br>
</font></tt>
<br>
<br>