    <div class="moz-cite-prefix">Solar is just one tiny little issue
      that fire fighters have to face.<br>
      There's no placard for 5 gal propane bottles stored in the
      basement.  <br>
      I'm glad we're looking to make firefighters safer, but this has
      really gotten a bit out of control.<br>
      Whatever is planned for 2017, I hope there are some sensible
      exceptions for lower voltage, lower current, off grid, or systems
      that cover only a small percentage of the roof, short conduit
      runs, etc.<br>
      For many years, I have supported some sort of ability to
      de-energize PV closer to its source, but that was based on large,
      higher voltage systems with long virtually unprotected wire runs.<br>
      We have decades of proven safety with small off grid systems. 
      Batteries are the hazard there.<br>
      Currently, the latest code is just driving more folks to do
      un-inspected, DIY installs, and that's not helping the
      firefighters or our industry one bit.<br>
      What if instead of all these electronics on every house, we get
      the firefighters a special foam that they spray over the modules
      to smother the fire and block the sun.<br>
      That would work regardless of the vintage or design of the system.<br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 2/5/2015 9:37 PM, Jerry Shafer wrote:<br>
    </div>
    <blockquote
cite="mid:CAMUFgmV8dSxwE2V4RjXNGC3ixsiaUQGTx=FfmpCiO-YPAu5-7g@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div>
          <div>
            <div>
              <div>
                <div>Mark and the wrenches group<br>
                </div>
                You do have a point, in the many years of my PV life, we
                have had three building fires not at all related to the
                PV, on the first, all of the insulation on the wires
                inside the metal conduit was gone, the at the time
                required AC disconnect was turned off, and after all was
                over we were called in to remove our system for the
                re-construction at which time I found a glove print on
                the conduit in the attic, it was wet, smoky and had live
                wires inside shorted and all that was required was a
                solid ground which it had and worked perfect.   <br>
              </div>
              The second fire was the result of someone else and started
              under the home, right next to our EMT conduit, here they
              were able to turn off DC disconnect at the array which was
              on the ground away from the home and the conduit was
              properly grounded. again this protected the firefighters
              which I support.   <br>
            </div>
            <div>The third fire was to far back recall to much but again
              it was not PV related.<br>
            </div>
            I hesitate to say this but all the wigets and waldos will
            not protect against bad installs and some non NEC following
            related repairs, sure shutting down the array on the roof
            may help, but the first time there is a system out there
            that does not work some guy may just go and bypass it, hell
            its a cheap fix. now who thinks they are protected and they
            are not, bad deal. <br>
            We all need to remember these systems requires power and we
            are in the industry of reducing power demands not increasing
            them. home owners may in time disconnect it them selves for
            this same reason. <br>
          </div>
          We need more KIS-S<br>
        </div>
        Jerry<br>
        <div>
          <div> </div>
        </div>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Thu, Feb 5, 2015 at 5:32 PM, Dave
          Click <span dir="ltr"><<a moz-do-not-send="true"
              href="mailto:daveclick@fsec.ucf.edu" target="_blank">daveclick@fsec.ucf.edu</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">Mark-<br>
            <br>
            690.56(C) provides the placard you're looking for and
            690.56(B) tells the first responder where that 690.12 switch
            is, right?<br>
            <br>
            For 2017 there are a couple of proposals out there. One is
            trying to better educate that first responder (quickly!) as
            to what hazards exist. Another is clarifying some of the
            language for 690.12 such that we continue to have [better]
            array-level shutdown. Another is changing 690.12 to
            [basically] module-level shutdown, which has been signed
            onto by the IAFF, insurance companies, and... some
            module-level electronics vendors.<br>
            <br>
            We've installed many, many rooftop systems but we're only
            about 0.1% done with them. Regardless of how 690.12 changes,
            I think that in the next few years we'll all be revisiting
            every system we've ever worked on to make sure there's
            enough labeling to inform firefighters about the hazards.
            I'm curious how we're going to do that so that a 2027
            firefighter can quickly distinguish between 2014's Rapid
            Shutdown, 2017's Even Rapider Shutdown, 2020's
            BlockOutTheSun Shutdown, 2014's Rapid Shutdown That Actually
            Still Works, 2011's System That Will Only Shock You If You
            Cut Through a Module, and 2005's Never-Code-Compliant system
            that incorrectly has a "Rapid Shutdown" label on it because
            the homeowner noticed that their neighbor had one. Somehow
            we need to make sure firefighters know exactly what they're
            up against.<br>
            <br>
            Non-farcically,<br>
            DKC
            <div class="HOEnZb">
              <div class="h5"><br>
                <br>
                <br>
                On 2015/2/5 20:08, Mark Frye wrote:<br>
                <blockquote class="gmail_quote" style="margin:0 0 0
                  .8ex;border-left:1px #ccc solid;padding-left:1ex">
                  ...without a mandatory "Stop" switch co-located with
                  the service meter<br>
                  or main breaker?<br>
                  <br>
                  How many roof top systems have been installed to date?
                  Many, many, many,<br>
                  many.<br>
                  <br>
                  OK ,now I am a first responder showing up at a home
                  that is on fire. How<br>
                  do I know whether or not the DC has been installed
                  such that it provided<br>
                  the protections afforded by 690.12? I don't. Because
                  it is not require<br>
                  for systems conforming to 690.12 to look any different
                  to me than those<br>
                  that do not.<br>
                  <br>
                  So does the "stop" switch become the new "fire
                  fighters club" logo? If<br>
                  you have the switch the FD will save your home, if you
                  don't they will<br>
                  let it burn down, even if you have a 690.12 compliant
                  system that does<br>
                  not include an "initiator switch"?<br>
                  <br>
                  Mark Frye<br>
                  <br>
                  <br>
                  <br>
                  <br>
                  _______________________________________________<br>
                  List sponsored by Redwood Alliance<br>
                  <br>
                  List Address: <a moz-do-not-send="true"
                    href="mailto:RE-wrenches@lists.re-wrenches.org"
                    target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                  <br>
                  Change listserver email address & settings:<br>
                  <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                    target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                  <br>
                  List-Archive:<br>
                  <a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                    target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                  <br>
                  List rules & etiquette:<br>
                  <a moz-do-not-send="true"
                    href="http://www.re-wrenches.org/etiquette.htm"
                    target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
                  <br>
                  Check out or update participant bios:<br>
                  <a moz-do-not-send="true"
                    href="http://www.members.re-wrenches.org"
                    target="_blank">www.members.re-wrenches.org</a><br>
                  <br>
                  <br>
                </blockquote>
                _______________________________________________<br>
                List sponsored by Redwood Alliance<br>
                <br>
                List Address: <a moz-do-not-send="true"
                  href="mailto:RE-wrenches@lists.re-wrenches.org"
                  target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                <br>
                Change listserver email address & settings:<br>
                <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                  target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                <br>
                List-Archive: <a moz-do-not-send="true"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                  target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                <br>
                List rules & etiquette:<br>
                <a moz-do-not-send="true"
                  href="http://www.re-wrenches.org/etiquette.htm"
                  target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
                <br>
                Check out or update participant bios:<br>
                <a moz-do-not-send="true"
                  href="http://www.members.re-wrenches.org"
                  target="_blank">www.members.re-wrenches.org</a><br>
                <br>
              </div>
            </div>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>