<font size=2 face="sans-serif">Hi:</font>
<br>
<br><font size=2 face="sans-serif">From your description of the problem
and the video, I suspect the problem is due to:</font>
<br>
<br><font size=2 face="sans-serif">1. The inverter is exporting very near
full power.</font>
<br><font size=2 face="sans-serif">2. The grid voltage rises which at the
same AC current results in larger export power flow above the inverters
limit.</font>
<br><font size=2 face="sans-serif">3. The inverter stops exporting due
to reaching its power limit</font>
<br><font size=2 face="sans-serif">4. The inverter again starts exporting.....</font>
<br><font size=2 face="sans-serif">5.  Reaches power limit and stops.</font>
<br><font size=2 face="sans-serif">6.etc.......</font>
<br>
<br><font size=2 face="sans-serif">I.E. since the inverter is working close
to its power limit on a grid with  fluctuating voltage, it goes in
and out of max power limit. </font>
<br>
<br><font size=2 face="sans-serif">One way to test if this is the cause
is to reduce the Sell Amps so that you are not operating at the power limit
of the inverter.</font>
<br>
<br><font size=2 face="sans-serif">JARMO<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Jarmo Venalainen</b>  |  </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>  |  Solar
Business</b>  |   <b>CANADA</b>  |   <b>Training &
Development Specialist - Senior</b> <b><br>
Phone:</b> +604-422-2528  |   <b>Fax:</b> +604-420-1591  |
  <b>Mobile:</b> +604-505-0291 <b><br>
Email:</b> </font><a href="mailto:jarmo.venalainen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>jarmo.venalainen@schneider-electric.com</u></font></a><font size=1 face="Arial">
 |   <b>Site:</b></font><a href=http://www.sesolar.com/ target=_blank><font size=1 color=blue face="Arial"><u>
www.SEsolar.com</u></font></a><font size=1 face="Arial">  |  
<b>Address:</b> 3700 Gilmore Way, Burnaby, BC V5G4M1 <br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="http:// www.sesolar.com/"><img src=cid:_2_09951328099510380071816388257DD6></a><font size=1 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=3>
<br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">Christopher Warfel <cwarfel@entech-engineering.com></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">re-wrenches@lists.re-wrenches.org, </font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">01/23/2015 12:07 PM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">[RE-wrenches] Schneider 6048 power output
fluctuating widely</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">"RE-wrenches" <re-wrenches-bounces@lists.re-wrenches.org></font></table>
<br>
<hr noshade>
<br>
<br>
<br><tt><font size=2>We installed a XW 6048 that has wide power output
fluctuations over <br>
several seconds. Lights flicker, and the inverter squeals. It happens <br>
multiple times in a minute  The inverter was replaced to no avail.
 I <br>
suspect the local utility's poor line maintenance. When the inverter <br>
begins to drop off line, the voltage sags from 123 to 117.  This is
<br>
still within normal parameters, so I don't understand why the inverter
<br>
would begin to power down.  Here is a youtube video of it if anyone
has <br>
ever seen this before. Schneider has assisted us several times, but <br>
cannot find any reason for this happening as a result of their technology.<br>
<br>
</font></tt><a href="http://youtu.be/EqMwv44p-lc"><tt><font size=2>http://youtu.be/EqMwv44p-lc</font></tt></a><tt><font size=2><br>
<br>
<br>
</font></tt><a href="http://youtu.be/ADaL-gEbj4w"><tt><font size=2>http://youtu.be/ADaL-gEbj4w</font></tt></a><tt><font size=2><br>
<br>
<br>
Thank you, Chris<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change listserver email address & settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"><tt><font size=2>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</font></tt></a><tt><font size=2><br>
<br>
List rules & etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out or update participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
<br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________<br>
</font></tt>
<br>
<br>