<div dir="ltr">Hi Greg,<div><br></div><div><b style="font-size:12.7272720336914px">Re: SPS integrated outlet</b><br></div><div>We have not had any inspectors take issue with the SPS, and we have installed dozens of them.  The SPS is completely isolated from the electrical system of the rest of the house and the grid.  As you know, our city inspectors here have a pretty high level of attention to detail, but once it was explained to them, they had no problem with it.</div><div><br></div><div><b style="font-size:12.7272720336914px">Re: Rapid Shutdown function</b><br></div><div><span style="font-size:12.7272720336914px">We had a meeting with SMA about this last week, and we are hoping to see the introduction (with pricing and availability) by next week.  They explained that theirs may be the only rapid shutdown device on the market that uses DC instead of AC for the control circuit.  Because of this, if the grid goes down, the device will continue to operate with the NO contactors closed and thus the SPS circuit may still be utilized. Of course, if the rapid shutdown function is engaged, then the SPS will be deenergized.  Installer will need to run a communications cable up to the roof, so either 600V rated CAT5 cable in your DC conduit, or a separate conduit.</span></div><div><span style="font-size:12.7272720336914px"><br></span></div><div><span style="font-size:12.7272720336914px">I hope all is well with you down in Texas.</span></div><div><span style="font-size:12.7272720336914px"><br></span></div><div><span style="font-size:12.7272720336914px">Cheers,</span></div><div><span style="font-size:12.7272720336914px"><br></span></div><div><span style="font-size:12.7272720336914px">Mark</span></div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature"><div dir="ltr"><div dir="ltr">----<br><b>Mark Westbrock</b><br>Branch Manager & Employee-Owner<div>NM EE98J Journeyman Electrician<br>NABCEP Certified PV Installation Professional<div>NABCEP Certified PV Technical Sales<br><br><div>Positive Energy, Inc.<br></div><div><div><div>510 S. Main St.</div><div>Las Cruces, NM 88001<br>office: 575-524-2030<br>cell: 575-640-2432<br><a href="mailto:westbrock@positiveenergysolar.com" target="_blank">mw@positiveenergysolar.com</a><br><a href="http://www.positiveenergysolar.com" target="_blank">www.positiveenergysolar.com</a></div></div></div><div><br></div><div>         <br></div></div></div></div></div></div></div>
<br><div class="gmail_quote">On Fri, Jan 16, 2015 at 10:31 AM, Gregory Seelhorst <span dir="ltr"><<a href="mailto:gseelhorst@gmail.com" target="_blank">gseelhorst@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr">

<p class="MsoNormal" style="margin-bottom:12pt"><span>Wrenches -</span></p>

<p class="MsoNormal" style="margin-bottom:12pt"><span>I wanted to bring up the topic of SMA TL inverters, SPS outlets, and Rapid Shutdown function.   In light of some AHJs where the 2014 NEC is already in effect, I would appreciate how anyone has insight on how to address the topics below: <br>
<br>
<b>Re: SPS integrated outlet</b> - </span><span><span>Citing 2014 NEC
690.61 and 690.10(B), is there any resistance to SMA's Technical paper on the topic (attached) and what is being done to appease them or make corrections any notices. </span><br></span></p>

<p class="MsoNormal" style="margin-bottom:12pt"><span>Also would appreciate if you have
suggestions on warning placards (to the effect of ‘this outlet only works when the
switch is in the ‘ON’ position, inverter will not backfeed in the ‘OFF’
position), please contact me off-line if you like.<br></span></p>

<p class="MsoNormal" style="margin-bottom:12pt"><b><span>Re: Rapid Shutdown function</span></b><span>
– It has come to my attention that there is (or soon to be) a Rapid Shutdown capability function which
will comply with 690.12.  The question being, <i>can or must this be used in conjunction with the SPS?</i><span>  </span>Just wanted clarification of this functionality.  <br></span></p><p class="MsoNormal" style="margin-bottom:12pt"><span>My understanding is that if other Rapid
Shutdown devices (DC contactors, Midnite Solar relays, etc.) are used, the SPS
function can not be used.<span>  </span>My question is
that <i>if the Rapid Shutdown function is optional or a requirement when deploying the SPS
function.</i></span></p>

<p class="MsoNormal" style="margin-bottom:12pt"><span>Regards,</span> </p>

<div class="gmail_extra">Greg Seelhorst<br><br><br></div><div class="gmail_extra"><div class="gmail_quote"><div><div class="h5">On Thu, Oct 9, 2014 at 11:41 AM, Randy <span dir="ltr"><<a href="mailto:randy@positiveenergysolar.com" target="_blank">randy@positiveenergysolar.com</a>></span> wrote:<br></div></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div><div class="h5"><div link="blue" vlink="purple" lang="EN-US"><div><p class="MsoNormal"><span style="color:rgb(31,73,125)">Hi Wrenches,</span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)">We are being forced to adopt 690.12 Rapid Shutdown requirement based on several explanations given to our industry:</span></p><p><span style="color:rgb(31,73,125)"><span>1.<span style="font:7pt "Times New Roman"">       </span></span></span><span style="color:rgb(31,73,125)">otherwise we would be ignoring the life safety and put our fire fighters lives in peril </span></p><p><span style="font-size:10pt;font-family:"Tahoma","sans-serif""><span>2.<span style="font:7pt "Times New Roman"">     </span></span></span><span style="color:rgb(31,73,125)">This product can be constructed from readily available, over-the-counter code compliant components.  T</span><span style="font-size:10pt;font-family:"Tahoma","sans-serif";color:rgb(31,73,125)">his (is) to be the intent of CMP4<span> </span>when compiling the NFPA<span> </span>70.</span><span style="font-size:10pt;font-family:"Tahoma","sans-serif""></span></p><p style="margin:0in 0in 0.0001pt"><span style="font-size:10pt;font-family:"Tahoma","sans-serif""> </span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)">We do not want to act like an industry that appears to be fighting against safety. And we know there are a few products that are code compliant, micro-inverters (don’t comply with 705.12 (D) (6) because there are no products), Solaredge, and Tigo (is it approved?) yet this is not how we choose products.  </span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)">And the SMA SPS inverter is not going to work in a 690.12 environment without complications as far as I can see. </span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)">Appreciate comments that might support the right decision.</span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)">Thanks,</span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)">Randy</span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><div><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)">Randy Sadewic</span><span style="color:rgb(31,73,125)"></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)">Cell:    <a href="tel:505%20570-0137" value="+15055700137" target="_blank">505 570-0137</a></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)"><a href="mailto:Randy@PositiveEnergySolar.com" target="_blank"><span style="color:blue">Randy@PositiveEnergySolar.com</span></a></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)"><img src="cid:image001.jpg@01CFE3AD.8B51B970" alt="http://positiveenergysolar.com/admin/content/uploads/PES-logo-3.jpg" border="0" height="103" width="239"></span></p></div><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><div><div style="border-width:1pt medium medium;border-style:solid none none;border-color:rgb(181,196,223) -moz-use-text-color -moz-use-text-color;padding:3pt 0in 0in"><p class="MsoNormal"><b><span style="font-size:10pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10pt;font-family:"Tahoma","sans-serif""> RE-wrenches [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of </b>Steve Jefferson<br><b>Sent:</b> Tuesday, October 07, 2014 8:33 AM<br><b>To:</b> RE-wrenches<br><b>Subject:</b> Re: [RE-wrenches] TL Inverters</span></p></div></div><p class="MsoNormal"> </p><p class="MsoNormal"><span style="color:rgb(31,73,125)">The first gen of TL’s did have a somewhat tight window for the DC window.</span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)">However, the new SBxxxxTL-US-22 (3kW – 7700kW, with secure power supply) Start Voltage is 125, MPPT is 175-480 (max of 600Vdc)</span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)">Also, for larger needs, the STP (12kW – 24kW)  start voltage is 150, MPPT is 300-800V (max of 1000Vdc).</span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><div><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)">SMA America, LLC</span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)">Steve Jefferson</span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)">Service Line Supervisor</span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)">3925 Atherton Ave</span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)">Rocklin, CA 95765 - 3714</span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)">U.S.A.</span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)">Tel:  <a href="tel:%2B1%20916%20625%203185" value="+19166253185" target="_blank">+1 916 625 3185</a> (direct)</span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)">Fax: <a href="tel:%2B1%20916%20625%200871" value="+19166250871" target="_blank">+1 916 625 0871</a></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)">Mobile: <a href="tel:%2B1%20916%20622%204253" value="+19166224253" target="_blank">+1 916 622 4253</a></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)">Email: </span><span style="color:rgb(31,73,125)"><a href="mailto:Steve.jefferson@SMA-America.com" target="_blank"><span style="font-size:10pt;font-family:"Arial","sans-serif"">Steve.jefferson@SMA-America.com</span></a></span><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)"></span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)"><a href="http://www.sma-america.com/" target="_blank"><span style="font-size:10pt;font-family:"Arial","sans-serif"">www.SMA-America.com</span></a></span><span style="font-size:10pt;font-family:"Arial","sans-serif";color:blue"></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><a href="http://www.youtube.com/watch?v=yQWzPuyqhzo&feature=youtu.be" target="_blank"><span style="color:rgb(31,73,125);text-decoration:none"><img src="cid:image004.png@01CFE3A9.D9064A40" alt="cid:image001.png@01CF1CFA.FE18BEB0" border="0" height="90" width="432"></span></a><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)"></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="font-size:9pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)">This email and any attachments thereto may contain SMA America, LLC confidential, privileged and private material for the sole use of the intended recipient. Any review, copying, or distribution of this email (or any attachments thereto) by others is strictly prohibited. If you are not the intended recipient, please contact the sender immediately and permanently delete the original and any copies of this email and any attachments thereto. Thank you.</span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial","sans-serif";color:rgb(31,73,125)"> </span></p></div><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><div><div style="border-width:1pt medium medium;border-style:solid none none;border-color:rgb(225,225,225) -moz-use-text-color -moz-use-text-color;padding:3pt 0in 0in"><p class="MsoNormal"><b>From:</b> RE-wrenches [<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of </b>Mark Byington<br><b>Sent:</b> Tuesday, October 07, 2014 6:59 AM<br><b>To:</b> <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><b>Subject:</b> Re: [RE-wrenches] TL Inverters</p></div></div><p class="MsoNormal"> </p><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)">Just a word of caution to those not having experience with SMA TL inverters - the larger units (7-11 kW) have an extremely narrow input DC voltage window.  Depending on your module voltage and string design, all you need is a module or two to be shaded to fall out of the MPPT input voltage range.  The smaller units (3-5 kW) with the Secure Power Supply don't have this problem.  We no longer use these larger SMA TL inverters unless we can do maximum string length (e.g. strings of 8 for SunPower 96-cell) and there is zero shade at the site.</span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)">I believe SMA is in the process of adding larger units to the line that has the Secure Power Supply.  They added the 6 kW unit earlier this year, and just announced the 7 kW unit with Secure Power Supply.</span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)">Mark Byington</span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)">Cobalt Power Systems, Inc.</span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="color:rgb(31,73,125)"> </span></p><p class="MsoNormal"> </p></div></div><br></div></div><span class="">_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></span></blockquote></div><br></div></div>
<br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div></div>