<div dir="ltr">Almost all modern charge controllers and inverters etc have a low voltage threshold at about 9-10VDC.....below that they simply won't turn on, so even if the sun is out the MPPT controller won't charge, for example. There are different field-expedient solutions; but here's me jump-starting a 100-meter MET tower / 24vdc offgrid system with my truck, after lightning tripped the main PV breaker 2 weeks before. About 5 minutes on one 12vdc battery string, and the PV controller woke up to see 750 watts of sun and all was well. The client was skeptical as I explained over the phone what I was doing, but quite happy when all the expensive anemometers and web data logger magically came back online.<div><br></div></div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature"><div dir="ltr">Dan Fink<div>Buckville Energy</div><div>IREC Certified Instructor™ for: </div><div>~ PV Installation Professional</div><div>~ Small Wind Installer</div><div>NABCEP / IREC / ISPQ Accredited Continuing Education Providers™<br>970.672.4342<br><br> </div></div></div></div>
<br><div class="gmail_quote">On Wed, Dec 17, 2014 at 10:36 AM, Corey Shalanski <span dir="ltr"><<a href="mailto:cshalanski@joule-energy.com" target="_blank">cshalanski@joule-energy.com</a>></span> wrote:<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr">Clarification and Update:<div>- I believe I may have inadvertently thrown Magnum under the bus in in my initial post. <br><div hspace="streak-pt-mark" style="max-height:1px"><img style="width:0px;max-height:0px" src="https://mailfoogae.appspot.com/t?sender=aY3NoYWxhbnNraUBqb3VsZS1lbmVyZ3kuY29t&type=zerocontent&guid=dab0a56b-2f33-4542-ab89-2eb7e81192f3"><font color="#ffffff" size="1">ᐧ</font></div><div class="gmail_extra">While on site yesterday I did speak with Magnum's customer support about my findings and they advised to try to trickle charge the batteries up to the minimum threshold at which the Magnum inverters would turn back on. From there we will hopefully be able to run some more determinate tests. My question about the low-battery-cutout was more intended to explore whether others have ever experienced any similar issues with this protection feature. I am finding out that the feature is only relevant during inverting (not charging) mode and so would imply that the utility feed had been cut, which does not appear to be the case.</div><div class="gmail_extra">- Our battery distributor has lent us a 12-circuit trickle charger - one set of alligator clips per battery. I am planning to re-visit the jobsite later today to put each battery on a trickle charge, which I am told will take 1-2 weeks for any lasting change to take effect. The distributor advised to reverse the leads on the batteries with negative voltage, hoping that they may be recoverable as "reversed pole" batteries thenceforth.</div><div class="gmail_extra"><br></div><div class="gmail_extra">--</div><div class="gmail_extra">Corey<div><div class="h5"><br><div class="gmail_quote"><br></div><div class="gmail_quote"><br></div><div class="gmail_quote">On Tue, Dec 16, 2014 at 8:27 PM,  <span dir="ltr"><<a href="mailto:cshalanski@joule-energy.com" target="_blank">cshalanski@joule-energy.com</a>></span> wrote:<blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-color:rgb(204,204,204);border-left-style:solid;padding-left:1ex"><br>
Wrenches,<br>
<br>
I visited a customer today whose grid-tied battery backup system suffered<br>
some sort of catastrophic failure, and now I'm trying to play detective to<br>
figure out what happened and whose equipment/design is to blame.<br>
<br>
Here is what I know so far:<br>
- System is ac-coupled with a Sunny Boy 7000 (7.85kW array), Magnum<br>
MS4448PAE (x2), 3 strings of 4 12v batts (705Ah total)<br>
- Site visit was triggered by the Sunny Boy registering zero output via<br>
online monitoring.<br>
- SPST Solid state relay installed on Sunny Boy output, controlled via<br>
Magnum router, serves as secondary overcharge protection to Magnum's<br>
frequency shift feature. Technician who initially responded claims he<br>
measured 240v across the relay's terminals - relay manufacturer claims this<br>
is "100% impossible". We removed the relay from the circuit, and the Sunny<br>
Boy is again operational.<br>
- On arrival I found the Magnum display showing a "Low Battery Charge"<br>
message with the bank measuring ~4Vdc. The individual batteries were in<br>
various states of charge, ranging from high of 6.3v to low of -2.6v. These<br>
measurements were taken at rest, all battery cables disconnected, and yes<br>
three of the batts were registering a negative voltage.<br>
- Customer reports that he was not aware of any recent prolonged power<br>
outages.<br>
<br>
The three potential suspects would seem to be:<br>
- SS relay: The customer is convinced that this is the weak link in the<br>
system and somehow triggered this failure. I am not so convinced but would<br>
be interested to hear recommendations for properly testing its<br>
functionality.<br>
- Magnum equipment: Since there is low-battery-cutout protection, why would<br>
this feature not have activated and prevented the batteries from draining<br>
so low?<br>
- Batteries: I am not very familiar with modes of failure, but our<br>
distributor suggested that an internal short could be a possibility - what<br>
might have triggered this?<br>
<br>
Clearly I am fishing for potential leads here, so any suggestions are<br>
welcome.<br>
<br>
Thanks!<br>
--<br>
Corey Shalanski<br>
Joule Energy<br>
New Orleans, LA<br>
</blockquote></div></div></div></div></div></div>
<br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div></div>