<font size=2 face="sans-serif">Hi:</font>
<br>
<br><font size=2 face="sans-serif">Grounding, (they use the term earthing
in the IEC/Euro world), variations like this are not very common in North
America as we overwhelmingly use a TT method which means there is a dedicated
ground rod at the building.</font>
<br>
<br><font size=2 face="sans-serif">In many other parts of the world power
lines are underground and so the systems use different grounding/earthing
methods.</font>
<br>
<br><font size=2 face="sans-serif">These methods are classed as TT, TN,
TN-C, TN-C-S, and so on.......</font>
<br>
<br><font size=2 face="sans-serif">From your explanation, I think this
new building uses a variation of TN-C-S, (T is GND, N is neutral, the C-S
means single combined Neutral/GND wire to the building which separates
at the service entrance).</font>
<br>
<br><font size=2 face="sans-serif">You can find a lot of info on the net,
but here is an explanation from the IEC rules regarding TN-C-S grounding/earthing.</font>
<br>
<br>
<br><img src=cid:_1_0E9A5BF00E9A5758005A3D1888257DB0>
<br>
<br>
<br><img src=cid:_1_0E9A6A900E9A67FC005A3D1888257DB0>
<br>
<br>
<br>
<br>
<br>
<br><img src=cid:_1_0E9A87DC0E9A8548005A3D1888257DB0><img src=cid:_1_0E9A833C0E9A8548005A3D1888257DB0><font size=2 face="sans-serif">480/277
are the right voltages for a 480WYE.</font>
<br>
<br><font size=2 face="sans-serif">Since its been done, there must be some
applicable North American codes somewhere.</font>
<br>
<br><font size=2 face="sans-serif">JARMO</font>
<br>
<br><font size=2 face="sans-serif"><br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Jarmo Venalainen</b>  |  </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>  |  Solar
Business</b>  |   <b>CANADA</b>  |   <b>Training &
Development Specialist - Senior</b> <b><br>
Phone:</b> +604-422-2528  |   <b>Fax:</b> +604-420-1591  |
  <b>Mobile:</b> +604-505-0291 <b><br>
Email:</b> </font><a href="mailto:jarmo.venalainen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>jarmo.venalainen@schneider-electric.com</u></font></a><font size=1 face="Arial">
 |   <b>Site:</b></font><a href=http://www.sesolar.com/ target=_blank><font size=1 color=blue face="Arial"><u>
www.SEsolar.com</u></font></a><font size=1 face="Arial">  |  
<b>Address:</b> 3700 Gilmore Way, Burnaby, BC V5G4M1 <br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="http:// www.sesolar.com/"><img src=cid:_2_0E9943F00E9937D4005A3D1888257DB0></a><font size=1 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=3>
<br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">"Howard \"Scot\" Arey"
<scot.arey@solarcentex.com></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif"><re-wrenches@lists.re-wrenches.org>,
</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">12/15/2014 05:50 PM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">[RE-wrenches] 480 Wye or Delta for a
SolarEdge 10K 3-phase;        how can I determine
what this panel is?</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">"RE-wrenches" <re-wrenches-bounces@lists.re-wrenches.org></font></table>
<br>
<hr noshade>
<br>
<br>
<br><font size=2 face="Calibri">My challenge is determining the correct
480V configuration so I can use a 3-phase Solar Edge 10000 for a 12KW commercial
system.  The SE10K requires a 480V Wye configuration.</font>
<br><font size=2 face="Calibri"> </font>
<br><font size=2 face="Calibri">The main 480 panel looks straightforward.
 L1, L2, L3 come from below grade to three separate busbars in the
panel.  A 4<sup>th</sup> wire, not taped white, goes to what appears
to be a ground bar at the lower right of the panel.  Green and green-taped
wires come from this bar. I do not see any physical connections between
the L1, L2, L3 bus bars and the ground bar in the lower right, other than
the box itself as the ground bar appears to be bonded to the main box itself.</font>
<br><font size=2 face="Calibri"> </font>
<br><font size=2 face="Calibri">Voltage measurements depicts 480V at line
to line, and 277 Volts from each line to the ground (neutral?).</font>
<br><font size=2 face="Calibri"> </font>
<br><font size=2 face="Calibri">The overhead service at the road depicts
4 wires into the service head.  The three from the three each transformers
at the pole are taped traditional 3-phase colors.  The bare wire from
the pole to the service head is bare wire, but is taped white as it goes
into the service head with an insulated conductor (wire).  There is
no apparent ground wire at the pole or inside the building that I can see
but the service is underground and under concrete until it comes up inside
the facility at the 480 panel board.</font>
<br><font size=2 face="Calibri"> </font>
<br><font size=2 face="Calibri">My master electrician is researching to
determine the type but I wanted to post it here for comments, too.</font>
<br><font size=2 face="Calibri"> </font>
<br><font size=2 face="Calibri">My questions:</font>
<br><font size=2 face="Calibri">-          Is
it possible to have an ungrounded Wye where the “4<sup>th</sup> wire”
actually is a neutral to the lower right bus bar, and the wires leaving
that bar are in fact ground wires?</font>
<br><font size=2 face="Calibri">-          The
SE10K calls for a neutral wire in a Wye config.  If this 4<sup>th</sup>
wire is a neutral, and is bonded to ground, can I run a wire from this
to the inverter neutral, then another wire from this same bar t0 other
ground wire location in the SE10K (right beside the neutral).</font>
<br><font size=2 face="Calibri">-          Is
the white taped wire (the bare wire from the pole, then insulated and taped
white into the service head) a neutral or is that ground.</font>
<br><font size=2 face="Calibri">-          Can
anything other than a 480 Wye give the 480/277 voltages indicated above?</font>
<br><font size=2 face="Calibri">-          If
the 4<sup>th</sup> wire is a neutral (I certainly hope it is), where might
I find the ground electrode conductor (the building is relatively new,
less than 10 years I believe.).  FYI, the building is metal.</font>
<br><font size=2 face="Calibri"> </font>
<br><font size=2 face="Calibri">I look forward to your comments</font>
<br><font size=2 face="Calibri"> </font>
<br><font size=2 face="Calibri"><b>Howard “Scot” Arey</b></font>
<br><font size=2 face="Calibri">254-300-1228</font>
<br><a href=mailto:scot.arey@solarcentex.com><font size=2 color=#0082bf face="Calibri"><u>scot.arey@solarcentex.com</u></font></a>
<br><font size=2 face="Calibri"> </font>
<br><img src=cid:_2_05C7210805C71E9C005A3D1888257DB0 width=209 height=205 alt="logo from letterhead">
<br><font size=2 face="Calibri"> </font>
<p><font size=3><br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________</font><tt><font size=2>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change listserver email address & settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"><tt><font size=2>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</font></tt></a><tt><font size=2><br>
<br>
List rules & etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out or update participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
</font></tt>
<p>
<p>