<p dir="ltr">Hi jarmo,</p>
<p dir="ltr">We have verified this is split phase 120/240. My multimeter gets 120 L-N and 240 L-L.</p>
<p dir="ltr">Thanks</p>
<div class="gmail_quote">On Dec 15, 2014 10:25 AM,  <<a href="mailto:Jarmo.Venalainen@schneider-electric.com">Jarmo.Venalainen@schneider-electric.com</a>> wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><font face="sans-serif">Hi:</font>
<br>
<br><font face="sans-serif">The </font><font size="3" face="sans-serif">Generac
QT02224GNAX</font><font face="sans-serif"> ships as a three-phase
120/208 VAC.  I believe the Magnum is a 120/240 VAC.</font>
<br>
<br><font face="sans-serif">JARMO<br>
</font><font size="3" color="#008000">_____________________________________________________________________________________</font><font size="3">
<br>
</font><font size="1" face="Arial"><b><br>
Jarmo Venalainen</b>  |  </font><font size="1" color="#008000" face="Arial"><b>
Schneider Electric </b></font><font size="1" face="Arial"><b>  |  Solar
Business</b>  |   <b>CANADA</b>  |   <b>Training &
Development Specialist - Senior</b> <b><br>
Phone:</b> <a href="tel:%2B604-422-2528" value="+6044222528" target="_blank">+604-422-2528</a>  |   <b>Fax:</b> <a href="tel:%2B604-420-1591" value="+6044201591" target="_blank">+604-420-1591</a>  |
  <b>Mobile:</b> <a href="tel:%2B604-505-0291" value="+6045050291" target="_blank">+604-505-0291</a> <b><br>
Email:</b> </font><a href="mailto:jarmo.venalainen@schneider-electric.com" target="_blank"><font size="1" color="blue" face="Arial"><u>jarmo.venalainen@schneider-electric.com</u></font></a><font size="1" face="Arial">
 |   <b>Site:</b></font><a href="http://www.sesolar.com/" target="_blank"><font size="1" color="blue" face="Arial"><u>
www.SEsolar.com</u></font></a><font size="1" face="Arial">  |  
<b>Address:</b> 3700 Gilmore Way, Burnaby, BC V5G4M1 <br>
</font><font size="1" color="blue" face="Arial"><u><br>
</u></font><a href="http://%20www.sesolar.com/" target="_blank"><img src="cid:_2_0CA593D00CA253C8005FB15188257DAF"></a><font size="1" face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size="3">
<br>
</font>
<br>
<br>
<br>
<table width="100%">
<tr valign="top">
<td><font size="1" color="#5f5f5f" face="sans-serif">From:</font>
<td><font size="1" face="sans-serif">Mac Lewis <<a href="mailto:maclewis1@gmail.com" target="_blank">maclewis1@gmail.com</a>></font>
<tr valign="top">
<td><font size="1" color="#5f5f5f" face="sans-serif">To:</font>
<td><font size="1" face="sans-serif">RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>>,
</font>
<tr valign="top">
<td><font size="1" color="#5f5f5f" face="sans-serif">Date:</font>
<td><font size="1" face="sans-serif">12/15/2014 05:52 AM</font>
<tr valign="top">
<td><font size="1" color="#5f5f5f" face="sans-serif">Subject:</font>
<td><font size="1" face="sans-serif">[RE-wrenches] Generac QT series</font>
<tr valign="top">
<td><font size="1" color="#5f5f5f" face="sans-serif">Sent by:</font>
<td><font size="1" face="sans-serif">"RE-wrenches" <<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>></font></td></td></tr></td></td></tr></td></td></tr></td></td></tr></td></td></tr></table>
<br>
<hr noshade>
<br>
<br>
<br><font size="3">Hello wrenches,</font>
<br>
<br><font size="3">We have a newly installed system that has a 22 kW Generac
Quiet Source </font><font size="3" face="sans-serif">QT02224GNAX</font><font size="3"> with
a Magnum MS4448-PAE.  When we start the generator, the Magnum's
internal transformer temperature climbs to overtemp (240F) within a 2 minutes. 
The batteries are being floated at the time, and haven't seen more than
5A coming out of the generator.  We swapped the Magnum out, and we
have the exact same issue.  We then got a job-site gas generator 6500W
and ran it.  No problem whatsoever.  The problem appears to be
with the Generac, or with the interaction between the Generac & the
Magnum.  I didn't have a scope on site but the fluke multimeter doesn't
detect anything wrong with the voltage or frequency coming from the Generac.</font>
<br>
<br><font size="3">Has anyone had issues with the Generac QT?  Anyone
paired one with a Magnum PAE before?  I want to get my scope up there
and look for triplen harmonics, but I'm not sure how to filter these out. 
Any references on how to effectively do that is appreciated.</font>
<br>
<br><font size="3">Thanks in advance</font>
<br>
<br><font size="3">-- </font>
<br>
<br>
<br>
<br><font size="3">Mac Lewis<br>
</font>
<p><font color="#37605e">"Yo solo sé que no sé nada." </font><font color="#5f5f5f">-Sócrates</font>
<p><font size="3"><br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________</font><tt><font>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank"><tt><font>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font><br>
<br>
List-Archive: </font></tt><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank"><tt><font>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</font></tt></a><tt><font><br>
<br>
List rules & etiquette:<br>
</font></tt><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank"><tt><font>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font><br>
<br>
Check out or update participant bios:<br>
</font></tt><a href="http://www.members.re-wrenches.org" target="_blank"><tt><font>www.members.re-wrenches.org</font></tt></a><tt><font><br>
<br>
</font></tt>
<p>
<p></p></p></p></p><br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div>