<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    <div class="moz-cite-prefix">I don't believe the aux is PWM.  It
      should be a straight 12 v 200 mA output as I recall.  Its just
      enough to run a battery fan, or a 12 v relay.  You shouldn't need
      anything else.  Being current limited, it doesn't even need a
      fuse.<br>
      Also you need to run both leads (pos and neg) from the aux output
      to the control side of the relay.  It is its own output and you
      will probably cause unfortunate things to happen if wired in
      common with anything else.  I usually use signal wire with
      multiple conductors, so trying to get away from one control
      conductor is fool hardy anyway.<br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 12/5/2014 3:09 PM, Hugh Piggott wrote:<br>
    </div>
    <blockquote
      cite="mid:D683A8E4-679C-43B2-98B6-CD7E3CA90467@scoraigwind.co.uk"
      type="cite">Hi Hugh again
      <div>Just to clarify the set up:</div>
      <div>The SSR controls the AC power from the inverter to the
        heating load.  It switches partway through each half cycle and
        thus controls the power to the load.</div>
      <div>The input to the SSR requires a power supply 8-32 V present
        all the time it is working.  I suppose it might be feasible to
        take this from  the AUX but as this will be pulsing PWM I don't
        want to rely on that.  Its a supply voltage to the input and not
        a control signal and for that reason I want to take it from the
        main battery which happens to be a 24 volt one which is ideal.</div>
      <div>The control signal is 0-10 volts DC and this controls the
        amount of power the unit delivers smoothly.  I want to get this
        from a capacitor that charges off the aux output so that is
        turns the PWM into an analog voltage signal that controls the
        SSR and controls the load.  I do this all the time with tristar
        outputs so it does work.  I have just never done it with the AUX
        of a FM80 controller.</div>
      <div><br>
      </div>
      <div>So my question again is simply this.  Can I connect the
        ground of the AUX to the inverter batter ground negative?  Most
        likely it is already connected, but I'd like to know if
        connecting it will damage the FM80.  I am also trying the
        outback forum.</div>
      <div><br>
      </div>
      <div>thanks for any help</div>
      <div>Hugh</div>
      <div><br>
        <div>
          <div>On 5 Dec 2014, at 18:44, Hugh Piggott wrote:</div>
          <br class="Apple-interchange-newline">
          <blockquote type="cite">
            <div style="word-wrap: break-word; -webkit-nbsp-mode: space;
              -webkit-line-break: after-white-space; "><span
                class="corners-top"><span></span></span>
              <div class="postbody">
                <h3 class="first"><span class="Apple-style-span"
                    style="font-weight: normal; font-size: medium; ">hi
                    wrenches,</span></h3>
                <div class="content">I am installing some load controls
                  for a client who has a FM80 controller. I don't have
                  experience with this product. It has a 12V aux output
                  that I wish to drive an SSR but the wiring is
                  complicated by the fact that this SSR also needs a
                  power supply as well as a control signal. I want to
                  use 24V nominal system battery for the SSR power and
                  AUX for the signal. Can I connect the grounds
                  together?<br>
                  <br>
                  Additional info. I am using a phase control SSR driven
                  by a 0-10 volt signal to control an AC load with phase
                  angle shift control. I plan to put an RC filter that
                  converts the PWM output of the AUX from the CC to give
                  an analog voltage output that determines the loading
                  of the inverter. Crydom MCPC2450<br>
                  <br>
                  thanks for any help before I go on site next week<br>
                  Hugh</div>
              </div>
            </div>
            _______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address & settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive:
<a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
            <br>
            List rules & etiquette:<br>
            <a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
            <br>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>