<div dir="ltr">If you are on 2014:<div> 690.47(B) <br>
<div class="" title="Page 637">
<div class="">
<div class="">
<p><span style="font-size:10pt;font-family:Times">An ac equipment grounding system shall be permitted
</span></p>
</div>
</div>
<div class="">
<div class="">
<p><span style="font-size:10pt;font-family:Times">to be used for equipment grounding of inverters and other
</span></p>
</div>
</div>
<div class="">
<div class="">
<p><span style="font-size:10pt;font-family:Times">equipment <b>and for the ground-fault detection reference for
</b></span></p>
</div>
</div>
</div><div><span style="font-family:Times;font-size:10pt"><b>ungrounded PV systems.</b></span></div><div><br></div><div>and 690.47(C)(3) </div></div><div>
<div class="" title="Page 637">
<div class="">
<div class="">
<p><span style="font-size:10pt;font-family:Times"><b>For ungrounded systems, this con</b></span><span style="font-family:Times;font-size:10pt"><b>ductor shall be sized in accordance with 250.122 </b>and shall</span></p></div></div>
<div class="">
<div class="">
<p><span style="font-size:10pt;font-family:Times">not be required to be larger than the largest ungrounded
</span></p>
</div>
</div>
<div class="">
<div class="">
<p><span style="font-size:10pt;font-family:Times">phase conductor. </span></p>
</div>
</div>
</div></div></div><div class="gmail_extra"><br><div class="gmail_quote">On Tue, Oct 28, 2014 at 2:22 PM, Gary Willett <span dir="ltr"><<a href="mailto:Gary@icarussolarservices.com" target="_blank">Gary@icarussolarservices.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Kirk:<br>
<br>
A DC grounding electrode conductor (GEC) is not required for inverters that do NOT have a ground reference for the PV+ and PV- conductor(s) from the PV array.<br>
<br>
A GEC is not required if the string inverter is one of the new TL (transformerless) types. Also, this applies to micro-inverters such as the new Enphase M250 and later versions of the M215.<br>
<br>
Where this applies, only a properly sized equipment grounding conductor (EGC) is required.<br>
<br>
The EGC is sized according to [NEC 690.45] and can be a minimum of #14AWG when not exposed to damage, or #6AWG when exposed to potential damage.<br>
<br>
Regards,<br>
<br>
Gary Willett PE<br>
Icarus Engineering LLC<div class="HOEnZb"><div class="h5"><br>
<br>
On 10/28/14, 12:53 PM, Kirk wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Hi,<br>
I'm on a jobsite without my code book. Could someone tell me where in the code ungrounded systems do not require the inverter GEC? Basically my onsite electrician doesn't believe me. Thanks.<br>
<br>
Kirk Herander<br>
VSE<br>
______________________________<u></u>_________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.<u></u>org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>options.cgi/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/<u></u>re-wrenches@lists.re-wrenches.<u></u>org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.<u></u>htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote>
<br>
______________________________<u></u>_________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.<u></u>org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>options.cgi/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/<u></u>re-wrenches@lists.re-wrenches.<u></u>org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.<u></u>htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</div></div></blockquote></div><br><br clear="all"><div><br></div>-- <br><div dir="ltr">Tel: 336.266.8800<br><a href="http://o2energies.com/" target="_blank">http://o2energies.com/</a><br>Project Engineer<br>NABCEP Certified PV Installation Professional™ 091209-85<br>NC Licensed Electrical Contractor<br><br>This message, together with any attachments, is intended only for the named recipient(s). It may contain confidential or privileged information that may be exempt from disclosure under applicable law. If you are not the intended recipient(s), you are notified that the disclosure, dissemination, distribution, copying, storing, or other use of the contents of this message or its attachments is strictly prohibited. If you receive this message in error, or are not the named recipient(s), please notify the sender at either the email address or telephone number above and delete this email from your computer. Thank you.</div>
</div>