    <div class="moz-cite-prefix">That's an interesting idea, but all the
      failed designs they illustrate don't show the way we usually do
      it.  We don't even bother with an inlet, as most battery boxes
      have enough gap around the door to provide intake air, then the
      exhaust comes off the top with several feet of rise to prevent
      back drafting.  If its in any space that H2s may be a problem
      (living space), we always add a Zephyr Power vent which has a back
      draft preventer.  Even if the Zephyr fails, there will still be
      passive air flow up the pipe past the fan.<br>
      I see 4 problems with their setup:<br>
      1) Large Copper pipe is really expensive, and steel is hard to
      work with and fittings are expensive.<br>
      2) Metal pipe is not only thermally conductive, its also
      electrically conductive.  I try to avoid unnecessary conductors in
      the battery box.<br>
      3)  Metal pipe will corrode when exposed to H2S and battery acid. 
      That's why we always use plastic.<br>
      4) Their suggested pipe size (1" outside pipe) are way too small
      to provide venting for any more than a couple of golf cart
      batteries.<br>
      <br>
      Basically, heat exchanger = good idea, but their version = not.<br>
      <br>
      As for the battery pass through connectors: they seem to be adding
      unnecessary connections, and would also prevent using conduit. 
      I'd guess they're not UL listed, so that whole idea is also code
      compliant.  Duct seal will prevent the H2S from going up the
      conduit into the DC load center.<br>
        <br>
      They're trying to seal the box too much; the only time you could
      actually have an explosive build up of H2S is if you sealed every
      gap on the battery box.  I think its easier and safer to keep the
      gaps, and if your venting fails, at least it won't blow up or over
      heat.<br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 10/28/2014 4:28 PM, Drake wrote:<br>
    </div>
    <blockquote cite="mid:20141028222840.3DAC410066@che.dreamhost.com"
      type="cite">
      Hello Wrenches,<br>
      <br>
      A client wants to use a passive battery venting method with a heat
      exchanger to the outside for his bank of Full River AGM batteries.
      Below
      is a link to one site that recommends this method. Has anyone used
      this
      method? <br>
      <br>
       <a moz-do-not-send="true"
        href="http://www.bdbatteries.com/hydrogenventing.php">
        http://www.bdbatteries.com/hydrogenventing.php</a>  <br>
      <br>
      My main concern for about the batteries is that they not get cold
      and
      lose capacity during the short days when storage is most needed.<br>
      <br>
      He would also like to connect the terminals inside the box to a
      pass
      through jumper
      <a moz-do-not-send="true"
        href="http://www.bdbatteries.com/lugs.php?id=269"
        eudora="autourl">
        http://www.bdbatteries.com/lugs.php?id=269</a> and then run the
      cables,
      without conduit, to the inverter. As far as I know, conduit is
      always
      required on the battery cables even if fuses are used in the
      battery box.
      Has anything changed?<br>
      <br>
      Thanks,<br>
      <br>
      Drake <br>
      <br>
      Drake Chamberlin<br>
      <i>Athens Electric LLC<br>
        OH License 44810<br>
        CO License 3773<br>
        NABCEP Certified Solar PV <br>
        740-448-7328<br>
      </i><a moz-do-not-send="true" href="http://athens-electric.com/">http://athens-electric.com/</a>
      <br>
      <br>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>