    Bill, typically inverters have a max OCPD that can be installed on
    their output, and these sizes are generally not large enough to
    accommodate two same-model inverters. And manuals often note that
    you need to have a dedicated OCPD anyway. At least if I were ever to
    double-up two inverters on a single breaker, I'd want to make sure I
    had clearance from the manufacturer to do so. Or... just buy the $75
    box to combine the two.<br>
    <br>
    DKC<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 2014/10/24 11:05, frenergy wrote:<br>
    </div>
    <blockquote cite="mid:A0C12762C5704F9ABEFE740A0B8CD2DF@D8XG8YH1"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <meta content="MSHTML 6.00.2900.6550" name="GENERATOR">
      <style></style>
      <div>Wrenches,</div>
      <div> </div>
      <div>        ...its the little things.  Recently someone here
        brought up the issue of combining AC outputs prior
        to backfeeding the "solar" CB in the mains panel.  In the past
        I've run AC outs from inverters into a small AC dist
        panel, backfeeding CBs and then ran my combined AC out from a
        larger CB or the busses themselves to the backfed CB in the
        mains panel.  Is this overkill?</div>
      <div> </div>
      <div>           It does seem as though, at least for just 2
        inverters, this could be done with just split bolts in a gutter
        or dedicated J-box....or a power distribution block??  Or...?? 
        (no wire nuts, thank you) Your ideas appreciated.</div>
      <div> </div>
      <div>Bill</div>
      <div>Feather River Solar Electric</div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>