    Thanks Dan, this looks good.  We do mostly small residential
    system.  Wonder if it will be considered "likely to be energized".  
    That's another bridge. Thanks again.<br>
    <br>
    Chris<br>
    <br>
    <div class="moz-cite-prefix">On 10/14/2014 3:23 PM, Daniel Young
      wrote:<br>
    </div>
    <blockquote cite="mid:006801cfe7e4$4535fec0$cfa1fc40$@com"
      type="cite">
      <pre wrap="">I think the answer also depends on the scale of the project. Are we talking
a small residential system? Or larger commercial/utility? I'd assume
smaller, as you would likely just fence in a larger scale system, solving
the accessibility issue.

For small scale ground mounts, we'll often use the Pro-Solar Ground Trac,
and simply put a strip of aluminum sheet metal (they sell rolls of it for
making custom gutters) between certain rails, using a metal break to give it
1" wings on the side for attaching to the rails. Then we use a liquid tight
to get the PV wire from the cavity, and send it to a J-Box/Combiner/Inverter
on the array. I'm attempting to attach 2 images, hopefully they go through.
This also has the benefit of making the array look very trim.

With Regards,

Daniel Young, 
NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
NABCEP Certified Solar Heating InstallerTM: Cert #SH031409-13
 
Lead Systems Designer for:

<a class="moz-txt-link-abbreviated" href="http://www.dovetailsolar.com">www.dovetailsolar.com</a>

-----Original Message-----
From: RE-wrenches [<a class="moz-txt-link-freetext" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On
Behalf Of Christopher Warfel
Sent: Tuesday, October 14, 2014 10:02 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Wire management devices

Thanks Rob, We have been using Unirac for many years and slow to change
(since we have so much of it in inventory). I think with the difficulty of
pv module disconnects now, and good wire management, a barrier is really a
solution looking for a problem.  I'll take a look.  Thank you again.  Chris
On 10/13/2014 3:54 PM, RE Ellison wrote:
</pre>
      <blockquote type="cite">
        <pre wrap="">I have mentioned in the past, look into US Solar Mounts, The wire
</pre>
      </blockquote>
      <pre wrap="">management is built in!
</pre>
      <blockquote type="cite">
        <pre wrap="">
They have several different styles of mounts and many of them have 
wire management built into the frames

  Custom-built for each install so you tell him what you're using and 
what you need and they will tell you what will work best

Another product that's made in the USA!
Bob Ellison


Bob Ellison

</pre>
        <blockquote type="cite">
          <pre wrap="">On Oct 13, 2014, at 1:34 PM, Christopher Warfel
</pre>
        </blockquote>
      </blockquote>
      <pre wrap=""><a class="moz-txt-link-rfc2396E" href="mailto:cwarfel@entech-engineering.com"><cwarfel@entech-engineering.com></a> wrote:
</pre>
      <blockquote type="cite">
        <blockquote type="cite">
          <pre wrap="">
I am well aware of all the possibilities of danger in many aspects of
</pre>
        </blockquote>
      </blockquote>
      <pre wrap="">life.  This is not a main one in my opinion, and given that there are no
good solutions indicates to me that it is mostly an unsolvable problem
unless you wish to be impractical.  All I asked for were products that could
provide a solution. .  I have inspected in several states with solar
programs that will not enforce securing electrical enclosures in living
spaces that have access to 240 v. I even seen this situation in a children's
play room.
</pre>
      <blockquote type="cite">
        <blockquote type="cite">
          <pre wrap="">I think that is more than a little more serious issue.



</pre>
          <blockquote type="cite">
            <pre wrap="">On 10/13/2014 11:27 AM, William Miller wrote:
Christopher:

I believe strongly that the code requirement to protect PV wires 
from unauthorized personnel is justified.  Ground mount arrays are 
essentially jungle gyms and could attract children to climb.  If a 
50 pound child inadvertently swings on a PV cable across a sharp 
metal edge the insulation could easily be compromised.  The current 
limited nature of PV means the current will sink through the short 
until the short is opened, leaving up to
600 volts at fatal amperage exposed to the touch.  Inadequate ground 
fault interruption technology does little to prevent the problem.

You cannot legally install a convenience receptacle at any height 
above ground with the individual conductors exposed, so why should 
one be allowed to install PV with individual conductors readily
</pre>
          </blockquote>
        </blockquote>
      </blockquote>
      <pre wrap="">accessible?
</pre>
      <blockquote type="cite">
        <blockquote type="cite">
          <blockquote type="cite">
            <pre wrap="">
I grant you that shielding PV wiring on a ground mount is a 
difficult process.  It is very unfortunate that the industry has 
been allowed to evolve without developing decent wire management
</pre>
          </blockquote>
        </blockquote>
      </blockquote>
      <pre wrap="">hardware in the process.
</pre>
      <blockquote type="cite">
        <blockquote type="cite">
          <blockquote type="cite">
            <pre wrap="">
If you are not aware of the work we have done on wire management 
solutions, you might visit our website where we share all of our 
ideas.  We are giving away trade secrets, but I feel a moral 
obligation to help everyone in the industry deliver a safe product.

Most sincerely,

William Miller



Lic 773985
millersolar.com
805-438-5600


-----Original Message-----
From: RE-wrenches [<a class="moz-txt-link-freetext" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] 
On Behalf Of Christopher Warfel
Sent: Monday, October 13, 2014 5:56 AM
To: <a class="moz-txt-link-abbreviated" href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>
Subject: Re: [RE-wrenches] Wire management devices

Thanks all, I don't see a good solution to what I think is a 
non-existent problem.  I believe that anyone who wants to pull apart 
dc subarray conductors is attempting to vandalize. It's not easy to 
do, and you really have to be wondering why someone would even try. 
Why don't we put all electrical outlets 8 feet off the ground?
</pre>
            <blockquote type="cite">
              <pre wrap="">On 10/13/2014 2:27 AM, William Miller wrote:
Friends:

I looked at the Solarmount web site and I don't think the product
complies-- the wire management leaves leads exposed.  It's a nice 
start,
</pre>
            </blockquote>
            <pre wrap="">however.
</pre>
            <blockquote type="cite">
              <pre wrap="">I was asked by Homepower to do an article on wire management.  I 
was flattered they'd ask, but I had to decline because there is so 
few options off-the-shelf that I can recommend.

William

Lic 773985
millersolar.com
805-438-5600
</pre>
            </blockquote>
            <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: 
<a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/mailli">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/mailli</a>
st.html

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre>
          </blockquote>
          <pre wrap="">--
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978

_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: 
<a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillis">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillis</a>
t.html

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
        </blockquote>
        <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: 
<a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist</a>
.html

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>


</pre>
      </blockquote>
      <pre wrap="">
--
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978

_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive:
<a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>



-----
No virus found in this message.
Checked by AVG - <a class="moz-txt-link-abbreviated" href="http://www.avg.com">www.avg.com</a>
Version: 2012.0.2247 / Virus Database: 4031/7885 - Release Date: 10/14/14

-----
No virus found in this message.
Checked by AVG - <a class="moz-txt-link-abbreviated" href="http://www.avg.com">www.avg.com</a>
Version: 2012.0.2247 / Virus Database: 4031/7885 - Release Date: 10/14/14
</pre>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>