<div dir="ltr">Any advice on backfeeding this 400A meter/main with 108A of inverter output rating (135A per 690.8)? Doable? I'm thinking tap the mains with a 150A fusible disconnect between the lugs and one of the 200A mains. That way it's a supply side interconnection and the 120% rule does not get in the way. I don't see any other way to do it without changing the service to 600A... if the utility would even do it.<div><br></div><div>Dual 200A breakers with feeders at the top of 125A, 100A, 50A, and two at 15A.<br><div><br></div><div><br></div><div><br><div><br></div><div><img src="cid:ii_149152d33e440c1e" alt="Inline image 1" width="232" height="412"><br></div><div><br></div><div>Jason Szumlanski</div><div><br></div></div></div></div>