<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    <div class="moz-cite-prefix">Mick,<br>
      <br>
      You are in luck!<br>
      The Classic controller can be programmed to skip up to 32 days of
      bulk charging.<br>
      <br>
      Look for this in the Main menu under Charge/ Advanced/ Skip....and
      select the # of days you want to skip.<br>
      <br>
      Not sure what firmware version this goes back to but the current
      one (1849) has it.<br>
      <pre class="moz-signature" cols="72">Roy Butler
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV & wind installer
IREC Certified Master Trainer™ for Small Wind Installer
Four Winds Renewable Energy, LLC
8902 Route 46, Arkport, NY 14807
607-324-9747  <a class="moz-txt-link-abbreviated" href="http://www.four-winds-energy.com">www.four-winds-energy.com</a>

Don't miss the 11th Annual Small Wind Conference
A Gathering of Installers, Manufacturers, Dealers, & Distributors
June 15-17, 2015 in Stevens Point, Wisconsin
<a class="moz-txt-link-abbreviated" href="http://www.smallwindconference.com">www.smallwindconference.com</a>

Although no trees were killed in the sending of this message, 
a large number of electrons were terribly inconvenienced.

                
</pre>
      On 10/6/2014 10:16 AM, Mick Abraham wrote:<br>
    </div>
    <blockquote
cite="mid:CABOJ=XQDKJa8pcNqR4oQOw0QAFxLDSJoK8DF6sGjVuqz5_7UmA@mail.gmail.com"
      type="cite">
      <div dir="ltr">Greetings, Mechanics~
        <div><br>
        </div>
        <div>My client's (flooded lead acid) battery is in Float almost
          all the time, courtesy of an XW inverter stack plus public
          utility power while the system waits in standby. "Selling to
          grid" is not enabled for complicated reasons, so here's the
          problem.</div>
        <div><br>
        </div>
        <div>Each day at sunup, the Midnite charge controls implement a
          new 3 stage charge cycle including a lengthy absorption
          interval. The batteries require frequent water additions and
          there may be other deleterious effects from running a complete
          bulk/absorb charge every day on a battery that's already
          highly charged. </div>
        <div><br>
        </div>
        <div>Possible solutions: <br>
        </div>
        <div><br>
        </div>
        <div>(1) We could tweak the Midnite settings for a short
          absorption interval with less gassing...but if a prolonged
          grid outage should develop we would wish the absorption
          interval had not been shortened.</div>
        <div><br>
        </div>
        <div>(2) Your suggestions here, please. The client would be
          willing to update and/or reconfigure their Midnite software if
          that would help or the client would even consider hardware
          revisions. We chose the Midnite controllers in 2011 largely
          because of their 250 volt input ceiling, btw. </div>
        <div><br>
        </div>
        <div>++++++++++++++++++++++++++++++++++++</div>
        <div><br>
        </div>
        <div>Thinking ahead to my future but similar projects:</div>
        <div><br>
        </div>
        <div>Does any DC charge controller know that a new absorb cycle
          is not needed each day provided that the battery never dropped
          below Float the night before? A full cycle would still be
          wanted every 30 days or so just to stir things up, so that's
          almost like a 30 day equalization trigger only it would be a
          bulk trigger instead.</div>
        <div><br>
        </div>
        <div>OR: would "selling to grid" avert this problem since the
          "battery backup with grid tie" type inverter is aware that the
          battery never left the Float stage?</div>
        <div><br>
        </div>
        <div>OR: would AC coupling also avert this problem even if "sell
          to grid" is not enabled, for the same reason cited above?</div>
        <div><br>
        </div>
        <div>OR: Your suggestions here, please.</div>
        <div><br>
        </div>
        <div>Thanks & Jolliness, Mechanix. The Wrench List is the
          Bomb!</div>
        <div><br clear="all">
          <div>Mick Abraham, Proprietor<br>
            <a moz-do-not-send="true" href="http://www.abrahamsolar.com"
              target="_blank">www.abrahamsolar.com</a><br>
            <br>
            Voice: 970-731-4675</div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>