<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    <div class="moz-cite-prefix">Definitely could use some
      clarification.  The 690 definition of an array says "mechanically
      integrated", which sort of implies each roof plane is its own
      array.<br>
      However in terms of actual PV design terminology, each PV system
      has only one array which may consist of many subarrays. Even a 25
      MW plant has Only One array!<br>
      So once again, NEC is inventing its own language that is not
      consistent with actual terminology in use for over 30 years. 
      (Ugh)<br>
      My call is that you would bond each subarray to each other with
      #6, and then bring down a single GEC.  Multiple GECs sounds very
      silly, but damn that NEC language.<br>
      I would argue that "mechanically integrated" means they are all
      bolted down to the same building (one support structure)<br>
      What other electrical system would require multiple GECs for an
      installation on a single building ?<br>
      <br>
      Good Luck,<br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 9/29/2014 6:21 AM, Jason Szumlanski wrote:<br>
    </div>
    <blockquote
cite="mid:CAJJtG3oQ=rroOdT_dyxw-mckftRuF-NxnSid6=Rf4nx7iJTGwA@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div class="gmail_default"
          style="font-family:verdana,sans-serif">The definition of Array
          in 690.2 is ambiguous. Figure 690.1(A) seems to indicate that
          groups of modules on different roof surfaces could be
          considered a single array. The textual definition itself could
          be construed either way. We have successfully argued that an
          entire roof mounted system with modules on different roofs
          constitutes a single array. Therefore, if the additional
          grounding electrode required by 690.47(D) qualifies for
          Exception 2, it is not required. However, our "favorite"
          jurisdiction has just interpreted it differently, requiring a
          separate electrode and electrode conductor for each roof
          surface... and there are a lot of roof surfaces on this
          particular job. Complying will not be fun or cheap.</div>
        <div class="gmail_default"
          style="font-family:verdana,sans-serif"><br>
        </div>
        <div class="gmail_default"
          style="font-family:verdana,sans-serif">How is your
          jurisdiction interpreting this?</div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div class="gmail_default"
          style="font-family:verdana,sans-serif">Related note: Figure
          690.1(A) would effectively make each module in a microinverter
          based system a distinct array. The figure seems to imply that
          all modules that form a PV Output Circuit are a single array.
          Each module is a complete PV Output Circuit in a microinverter
          based system. It's strange that the textual definition is
          concerned with mechanical assemblies, but the figure refers to
          electrical configuration in defining Array. In fact, in the
          text an Array is defined as components forming "a
          direct-current power-producing unit." In a microinverter-based
          system, how can any group of modules be considered an array
          given that definition? </div>
        <br>
        <br>
        <div id="WISESTAMP_SIG_gmail_session"
          href="http://WISESTAMP_SIG_gmail_session">
          <div
            style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif">
            <div style="margin:0 0 8px 0">
              <p style="margin:0"><span><span>Jason Szumlanski</span></span></p>
              <p style="margin:0"><span><span></span></span></p>
              <div class="gmail_default"
                style="font-family:verdana,sans-serif;display:inline">Fafco
                Solar</div>
              <br>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>