      Bruce, August, et al,<br>
      <br>
      This is but one more example of confusing terminology. A plumbing
      vent is not an exhaust vent!<br>
      <br>
      A plumbing vent (what August calls a cold vent) is provided to
      allow the sanitary drain traps (and perhaps more) to operate
      properly. Without the properly functioning traps you would have
      sewer gas smell and sewer gas from the plumbing fixtures. This was
      commonplace when indoor plumbing was introduced to early adopters.<br>
      <br>
      An exhaust vent is another animal entirely. An exhaust vent
      carries the combustion products to a suitable exterior location
      for dilution with ambient air. With the advent of power vented
      combustion appliances, a direct vent (one that takes in combustion
      air from the outside and naturally exhausts combustion products to
      the outside) is IMHO the only responsible way to install any power
      vented appliance in a freezing climate. (Power vented appliances
      come in both condensing and non-condensing flavors-they can
      penetrate the side wall or the roof). Originally, two separate
      pipes (with two independent properly separated penetrations) was
      used. That technique is still often used today. More recently
      concentric vents have been introduced both for condensing and
      non-condensing applications. A concentric vent can simplify some
      installations by putting the exhaust pipe inside a larger air
      intake pipe allowing for one, albeit larger, penetration. As you
      might imagine if the exhaust flow is hindered/diverted/redirected
      by an inappropriately located solar module combustion gasses will
      be re-ingested into the intake air. Not good for equipment
      performance. My understanding is the power vented <u>appliance
        manufacturer</u> dictates what kind of separation/clearances are
      needed with their product. My guess is you find they want at least
      a foot of separation between the top of the " inverted cone" and
      the module. Probably not what you had in mind for an aesthetically
      pleasing installation.<br>
      <br>
      I hope this helps,<br>
      <pre class="moz-signature" cols="72">Bill Loesch
Solar 1 - Saint Louis Solar
314 631 1094</pre>
      On 23-Sep-14 6:54 PM, August Goers wrote:<br>
    </div>
    <blockquote
      cite="mid:efb8968d9a8d4c887a619f5337d6c32f@mail.gmail.com"
      type="cite">
      <pre wrap="">Bruce and All,

Sorry, I hit send before I had a chance to complete my thoughts. What I
meant to say was that I've found AHJs often allow us to cover cold
plumbing vents but I've never tried or had any luck with covering hot
vents including condensing boiler PVC vents. Once again, if in doubt you
could see what the plan checker or inspector thinks.

Best,

August

-----Original Message-----
From: August Goers [<a class="moz-txt-link-freetext" href="mailto:august@luminalt.com">mailto:august@luminalt.com</a>]
Sent: Tuesday, September 23, 2014 4:15 PM
To: 'RE-wrenches'
Subject: RE: [RE-wrenches] Modules over vents

Bruce,

I'll send you the CA plumbing code vent section offlist (attachment too
large for this list). The way I read the code is that you technically
can't cover any type of plumbing or hot vent. However, and I've run into
little resistance from AHJs in the Bay Area by covering these. You might
want to check in with your plan checker.

Best,

August

Luminalt

-----Original Message-----
From: RE-wrenches [<a class="moz-txt-link-freetext" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On
Behalf Of Bruce Leininger
Sent: Tuesday, September 23, 2014 3:49 PM
To: RE-wrenches
Subject: [RE-wrenches] Modules over vents

Hi all.  We're designing a system on a roof that is literally infested
with plumbing, exhaust and combustion vents.  The combustion vents are PVC
and none of the vents are more than 1.5' above the roof.

A racking company says that we can cover them with modules, since the
modules will be at least 4' above the roof.  They have not yet provided
any building code references to say that this is ok.  Do any of you know
if the building code allows this?

Thanks.

Bruce
_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive:
<a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm</a>
l

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>



-----
No virus found in this message.
Checked by AVG - <a class="moz-txt-link-abbreviated" href="http://www.avg.com">www.avg.com</a>
Version: 2014.0.4765 / Virus Database: 4025/8265 - Release Date: 09/23/14


</pre>
    </blockquote>
    <br>
  </body>
<a></a><p class=""avgcert"" align="left" color="#000000">No virus found in this message.<br>
Checked by AVG - <a href='http://www.avg.com'>www.avg.com</a><br>
Version: 2014.0.4765 / Virus Database: 4025/8265 - Release Date: 09/23/14</p></html>