<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto"><div>Bruce,</div><div>We routinely cut off DWV as suggested by earlier posts so that they are at least 1 inch below the surface of the back of the module.</div><div><br></div><div>To be clear these are sewage intake air vents and not exhaust vents for heating appliances. </div><div><br></div><div>We do place a quarter inch wire cloth over the cut off vent and apply a four inch stainless steel hose clamp around the pipe just to prevent foreign objects from entering the vent pipe. </div><div><br></div><div>I have never had an inspector question this method. <br><br><div><span style="background-color: rgba(255, 255, 255, 0);">With Regards</span><div><span style="background-color: rgba(255, 255, 255, 0);">Carl Adams, President</span></div><div><span style="background-color: rgba(255, 255, 255, 0);">SunRock Solar</span></div><font color="#000000"><span style="background-color: rgba(255, 255, 255, 0);"><a href="tel:513.290.9072" x-apple-data-detectors="true" x-apple-data-detectors-type="telephone" x-apple-data-detectors-result="0">513.290.9072</a> (cell)</span></font></div><div><font color="#000000"><span style="background-color: rgba(255, 255, 255, 0);"><a href="tel:513.766.6025" x-apple-data-detectors="true" x-apple-data-detectors-type="telephone" x-apple-data-detectors-result="1">513.766.6025</a> (office)</span></font></div></div><div><br>On Sep 24, 2014, at 1:37 PM, Ray Walters <<a href="mailto:ray@solarray.com">ray@solarray.com</a>> wrote:<br><br></div><div>
  
    <meta content="text/html; charset=ISO-8859-1" http-equiv="Content-Type">
  
  
    <div class="moz-cite-prefix">I agree with Kurt: you need a licensed
      plumber in your area to advise you, if you're trying to keep the
      AHJs happy .<br>
      2nd,  I'm very sure you don't want an exhaust/ combustion type
      vent under the array.  I've had several over the years, and seen
      some arrays installed over them.  They can get fairly hot and put
      quite a bit of steam out.  I would not trust the module backing
      material to a concentrated long term dose; which module is going
      to have a problem first?   <br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 9/24/2014 11:16 AM, Kurt Johnsen wrote:<br>
    </div>
    <blockquote cite="mid:CAF70bw7uVss0ES-c08W3Vv39gaLtBTBCY4QOsjFW2kJ+TLnSeQ@mail.gmail.com" type="cite">
      <div dir="ltr">
        <p class="MsoNormal"><span style="font-size:12pt;font-family:"Times New
            Roman","serif"">Should you decide to lower
            your
            plumbing vents I have found an inside pipe cutter to be an
            inexpensive and
            handy tool. Cut the vent and lead off an inch above your
            desired pipe height
            and use the inside cutter to cut the pvc pipe. Go slow and
            be careful to keep
            air space between the pvc and lead as the lead will cut very
            easily. </span><span style="font-size:12pt"></span></p>
        <p class="MsoNormal"><span style="font-size:12pt;font-family:"Times New
            Roman","serif""> </span></p>
        <p class="MsoNormal"><span style="font-size:12pt;font-family:"Times New
            Roman","serif"">Also I wouldn't rely on us
            well
            intentioned wrenches to make the call on the plumbing code
            in your
            jurisdiction. Though the state plumbing codes are usually
            based on the
            international code, there will be differences. If you can't
            pull up your state
            plumbing code online then ask your plumbing inspector. In
            Florida the minimum
            height above a roof surface is 6" (904.1). As for relocating
            905.2 states
            that “all vent and branch vent pipes shall be so graded and
            connected as to
            drain back to the drainage pipe by gravity”. Table 710.1(1)
            shows that for 1.5”
            pipe a slope of ¼” per foot is sufficient to handle 3
            fixtures. I would take
            that to indicate ¼” / foot is plenty for a 1.5” vent. </span><span style="font-size:12pt"></span></p>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Wed, Sep 24, 2014 at 11:20 AM, Dave
          Click <span dir="ltr"><<a moz-do-not-send="true" href="mailto:daveclick@fsec.ucf.edu" target="_blank">daveclick@fsec.ucf.edu</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div bgcolor="#FFFFFF" text="#000000"> Flipping through the
              '04 plumbing code I see a few slopes called out (1/4" per
              1' for fixture vents, 1" per 1' for circuit vents, 1/2"
              per 1' for combination drain/vent...). Fixture vents have
              a maximum distance of a few feet from fixture trap to
              vent, but I don't think this prevents you from then
              running that vent horizontally. 916.2 states that for
              vents other than stack vents or vent stacks if your vent
              is >40' you need to upsize the whole vent pipe (tough
              to do for an existing building, of course). Stack vents
              have a "maximum developed length" of 100' for a 1.5" vent
              which should be enough space to get away from under the
              PV. I don't see any slope requirements specifically for
              stack vents but my non-plumber's eye may be missing
              something.<br>
              <br>
              The stack vent sizing Table 916.1 appears (in part) here
              too and it looks like the tables match up to a 2.5":<br>
              <a moz-do-not-send="true" href="http://www.engineeringtoolbox.com/drainage-vents-d_1110.html" target="_blank">http://www.engineeringtoolbox.com/drainage-vents-d_1110.html</a><br>
              <br>
              DKC
              <div>
                <div class="h5"><br>
                  <br>
                  <br>
                  <br>
                  <div>On 2014/9/24 10:19, Jason Szumlanski wrote:<br>
                  </div>
                </div>
              </div>
              <blockquote type="cite">
                <div>
                  <div class="h5">
                    <div dir="ltr">
                      <div class="gmail_default" style="font-family:verdana,sans-serif">
                        <div class="gmail_default" style="font-size:12.7272720336914px">I am
                          unable to find anything in the Florida code
                          that precludes covering a plumbing vent. The
                          code does require the vent to be 6" above the
                          roof surface I believe.</div>
                        <div class="gmail_default" style="font-size:12.7272720336914px"><br>
                        </div>
                        <div class="gmail_default" style="font-size:12.7272720336914px">I was
                          unable to determine if these vents need to be
                          vertical with no bends in the attic. Obviously
                          you wouldn't want to create a trap in the
                          attic, but a couple of 45's to relocate a
                          plumbing vent to accommodate more PV seems
                          like a desirable thing to do sometimes. Does
                          anyone know if these can be relocated, i.e. to
                          an adjacent roof surface?</div>
                        <div style="font-size:12.7272720336914px"><br>
                        </div>
                        <div style="font-size:12.7272720336914px">On my
                          own home I had a vent to deal with. I broke
                          out my saws-all, split the lead like a banana
                          and peeled it back, cut the pipe at an angle,
                          and folded the lead back into the pipe after
                          applying sealant between the lead and pipe.
                          There is a 1" gap between the rim of the pipe
                          and the back of the module. My theory on this
                          working safely is that, a) there will be far
                          less rainwater falling in and around this pipe
                          with a module over it, and b) it is about 24"
                          from the roof ridge and there is a module over
                          it so there will be very little water sheeting
                          down from above the vent. Code
                          notwithstanding, I felt this was a solid
                          method on my own home, and I have inspected it
                          after 6 months of Florida downpours and found
                          no issues.</div>
                      </div>
                      <br>
                      <br>
                      <div href="http://WISESTAMP_SIG_gmail_session">
                        <div style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif">
                          <div style="margin:0px 0px 8px">
                            <p style="margin:0px"><span><span>Jason
                                  Szumlanski</span></span></p>
                            <p style="margin:0px"><span><span></span></span></p>
                            <div class="gmail_default" style="font-family:verdana,sans-serif;display:inline">Fafco

                              Solar</div>
                            <br>
                          </div>
                          <img moz-do-not-send="true" height="1" width="1" src="cid:"></div>
                      </div>
                      <div class="gmail_extra"><br>
                        <div class="gmail_quote">On Wed, Sep 24, 2014 at
                          6:38 AM, Bill Loesch <span dir="ltr"><<a moz-do-not-send="true" href="mailto:solar1online@charter.net" target="_blank">solar1online@charter.net</a>></span>
                          wrote:<br>
                          <blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px
                            #ccc solid;padding-left:1ex">
                            <div bgcolor="#FFFFFF" text="#000000">
                              <div><br>
                                Bruce, August, et al,<br>
                                <br>
                                This is but one more example of
                                confusing terminology. A plumbing vent
                                is not an exhaust vent!<br>
                                <br>
                                A plumbing vent (what August calls a
                                cold vent) is provided to allow the
                                sanitary drain traps (and perhaps more)
                                to operate properly. Without the
                                properly functioning traps you would
                                have sewer gas smell and sewer gas from
                                the plumbing fixtures. This was
                                commonplace when indoor plumbing was
                                introduced to early adopters.<br>
                                <br>
                                An exhaust vent is another animal
                                entirely. An exhaust vent carries the
                                combustion products to a suitable
                                exterior location for dilution with
                                ambient air. With the advent of power
                                vented combustion appliances, a direct
                                vent (one that takes in combustion air
                                from the outside and naturally exhausts
                                combustion products to the outside) is
                                IMHO the only responsible way to install
                                any power vented appliance in a freezing
                                climate. (Power vented appliances come
                                in both condensing and non-condensing
                                flavors-they can penetrate the side wall
                                or the roof). Originally, two separate
                                pipes (with two independent properly
                                separated penetrations) was used. That
                                technique is still often used today.
                                More recently concentric vents have been
                                introduced both for condensing and
                                non-condensing applications. A
                                concentric vent can simplify some
                                installations by putting the exhaust
                                pipe inside a larger air intake pipe
                                allowing for one, albeit larger,
                                penetration. As you might imagine if the
                                exhaust flow is
                                hindered/diverted/redirected by an
                                inappropriately located solar module
                                combustion gasses will be re-ingested
                                into the intake air. Not good for
                                equipment performance. My understanding
                                is the power vented <u>appliance
                                  manufacturer</u> dictates what kind of
                                separation/clearances are needed with
                                their product. My guess is you find they
                                want at least a foot of separation
                                between the top of the " inverted cone"
                                and the module. Probably not what you
                                had in mind for an aesthetically
                                pleasing installation.<br>
                                <br>
                                I hope this helps,<br>
                                <pre cols="72">Bill Loesch
Solar 1 - Saint Louis Solar
<a moz-do-not-send="true" href="tel:314%20631%201094" value="+13146311094" target="_blank">314 631 1094</a></pre>
                                <div>
                                  <div> On 23-Sep-14 6:54 PM, August
                                    Goers wrote:<br>
                                  </div>
                                </div>
                              </div>
                              <blockquote type="cite">
                                <pre><div><div>Bruce and All,

Sorry, I hit send before I had a chance to complete my thoughts. What I
meant to say was that I've found AHJs often allow us to cover cold
plumbing vents but I've never tried or had any luck with covering hot
vents including condensing boiler PVC vents. Once again, if in doubt you
could see what the plan checker or inspector thinks.

Best,

August

-----Original Message-----
From: August Goers [<a moz-do-not-send="true" href="mailto:august@luminalt.com" target="_blank">mailto:august@luminalt.com</a>]
Sent: Tuesday, September 23, 2014 4:15 PM
To: 'RE-wrenches'
Subject: RE: [RE-wrenches] Modules over vents

Bruce,

I'll send you the CA plumbing code vent section offlist (attachment too
large for this list). The way I read the code is that you technically
can't cover any type of plumbing or hot vent. However, and I've run into
little resistance from AHJs in the Bay Area by covering these. You might
want to check in with your plan checker.

Best,

August

Luminalt

-----Original Message-----
From: RE-wrenches [<a moz-do-not-send="true" href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On
Behalf Of Bruce Leininger
Sent: Tuesday, September 23, 2014 3:49 PM
To: RE-wrenches
Subject: [RE-wrenches] Modules over vents

Hi all.  We're designing a system on a roof that is literally infested
with plumbing, exhaust and combustion vents.  The combustion vents are PVC
and none of the vents are more than 1.5' above the roof.

A racking company says that we can cover them with modules, since the
modules will be at least 4' above the roof.  They have not yet provided
any building code references to say that this is ok.  Do any of you know
if the building code allows this?

Thanks.

Bruce</div></div></pre>
                              </blockquote>
                            </div>
                          </blockquote>
                        </div>
                        <br>
                      </div>
                    </div>
                    <br>
                    <fieldset></fieldset>
                    <br>
                  </div>
                </div>
                <span class="">
                  <pre>_______________________________________________
List sponsored by Redwood Alliance

List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a moz-do-not-send="true" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a moz-do-not-send="true" href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</pre>
                </span></blockquote>
              <br>
            </div>
            <br>
            _______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address & settings:<br>
            <a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
            <br>
            List rules & etiquette:<br>
            <a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a moz-do-not-send="true" href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
            <br>
            <br>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  

</div><div><span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br><span></span><br><span>Change listserver email address & settings:</span><br><span><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a></span><br><span></span><br><span>List rules & etiquette:</span><br><span><a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></span><br><span></span><br><span>Check out or update participant bios:</span><br><span><a href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></span><br><span></span><br></div></body></html>