<div dir="ltr">Is it possible that the UPS issue is raised voltage, causing the UPS voltage regulator to switch settings? A large amount of solar on a circuit can raise the voltage in the system at full sun. I would rent a Fluke Energy Analyzer and leave it in place for a number of days to see how the voltage, current and power factor varies with the inverter output.</div>
<div class="gmail_extra"><br><br><div class="gmail_quote">On Mon, Aug 4, 2014 at 5:11 PM, Carl Adams <span dir="ltr"><<a href="mailto:swingjunkie@gmail.com" target="_blank">swingjunkie@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr">Bob, Ray, Glenn,<div><br></div><div>Thanks for the responses.  We could cycle through the inverters and see if it is one, or some combinations of inverters, which is causing the problem.  This results in a minimum of 6 trials.  If it is a combination of inverters  many more.</div>

<div><br></div><div>Any feedback on the idea of monitoring the AC circuits; computer feed and combined inverter output?  Seems to me this might provide a one step correlation between the event and the cause.  Just not sure what equipment to suggest for this.</div>

<div><br></div><div>Could be there is some other cause, unrelated to the inverters.  AC unit kicking on, etc.  Though they do not see any lights dimiming/brightening, or any other notable change in electrical equipment at the sight.  </div>

<div><br></div></div><div class="gmail_extra"><br><br><div class="gmail_quote"><div><div class="h5">On Mon, Aug 4, 2014 at 1:03 PM, Glenn Burt <span dir="ltr"><<a href="mailto:glenn.burt@glbcc.com" target="_blank">glenn.burt@glbcc.com</a>></span> wrote:<br>

</div></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div><div class="h5">

<div>
<div>
<div style="FONT-SIZE:11pt;FONT-FAMILY:Calibri,sans-serif">I wonder if the UPS is grumbling about high voltage as the inverters push back current...<br><br>Glenn </div></div>
<div dir="ltr">
<hr>
<span style="FONT-SIZE:11pt;FONT-FAMILY:Calibri,sans-serif;FONT-WEIGHT:bold">From: </span><span style="FONT-SIZE:11pt;FONT-FAMILY:Calibri,sans-serif"><a href="mailto:swingjunkie@gmail.com" target="_blank">Carl Adams</a></span><br>

<span style="FONT-SIZE:11pt;FONT-FAMILY:Calibri,sans-serif;FONT-WEIGHT:bold">Sent: </span><span style="FONT-SIZE:11pt;FONT-FAMILY:Calibri,sans-serif">‎8/‎4/‎2014 10:29</span><br><span style="FONT-SIZE:11pt;FONT-FAMILY:Calibri,sans-serif;FONT-WEIGHT:bold">To: </span><span style="FONT-SIZE:11pt;FONT-FAMILY:Calibri,sans-serif"><a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches</a></span><br>

<span style="FONT-SIZE:11pt;FONT-FAMILY:Calibri,sans-serif;FONT-WEIGHT:bold">Subject: </span><span style="FONT-SIZE:11pt;FONT-FAMILY:Calibri,sans-serif">[RE-wrenches] UPS disturbance with SMA Inverters</span><br><br></div>

<div>
<div dir="ltr">Hello Wrenches, 
<div><br></div>
<div>I have a site which is experiencing nuisance disturbance of the computer UPS systems at the site.  The site owner "suspects" this is due to the <span>PV</span> system which is a 50 kW system using 6 <span>SMA</span> <span>SunnyBoy</span> inverters.  The nuisance disturbance is a clicking noise in the UPS units.  The disturbance is not enough to cause the UPS to engage, so it seems to be a small disturbance on the AC power.   The site owner "suspects" the inverters are the source of this disturbance since 1) It seems to only occur when we have a good solar day.  2) If the inverters are shut down the problem goes away, and if you start up the inverters the problem exhibits again.</div>


<div><br></div>
<div>The site was commissioned in March of 2012 and has had no problems till this issue last month.  In reviewing the event log on Sunny Portal there are no inverter anomalies.  <span>SMA</span> tech support had not run into this issue and had no ideas, they too agree the inverters are not reporting any anomalies.</div>


<div><br></div>
<div>The problem is not persistent but rather intermittent making this harder to troubleshoot.</div>
<div><br></div>
<div>So my questions are</div>
<div>1) Has anyone else seen this sort of issue before, related to <span>SMA</span> <span>SunnyBoy</span> inverters.</div>
<div>2) Can you recommend an AC power monitoring tool which would support  frequency and voltage monitoring on the AC line.  Perhaps one data set on the circuit feeding the computers and another on the inverter output circuit.</div>


<div><br></div>
<div>For clarity the six <span>SunnyBoys</span> feed into an AC Combiner panel which <span>backfeeds</span> into the building main distribution panel.  The service is 240V single phase.</div>
<div><br></div>
<div>With Regards</div>
<div>Carl Adams, <span>SunRock</span> Solar</div>
<div><span>NABCEP</span> Certified <span>PV</span> Installer</div></div></div></div><br></div></div><div class="">_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></div></blockquote></div><br></div>
<br>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br><div dir="ltr">Chris Mason<div><div style="color:rgb(136,136,136)"><span style="font-size:13px">NABCEP Certified Solar PV Installer™</span></div><div style="color:rgb(136,136,136)">
<span style="color:rgb(34,34,34)">Solar Design Engineer</span></div><div style="color:rgb(136,136,136)"><span style="font-size:13px">Generac Generators Industrial technician</span></div></div><div style="color:rgb(136,136,136)">
<span style="font-size:13px"><br></span></div><div><a href="http://www.cometenergysystems.com" target="_blank">www.cometsolar.com</a></div><div>264.235.5670</div><div>869.662.5670</div><div>Skype: netconcepts</div></div>
</div>