    Mac, that Island interconnects with a max 70A 1P breaker (6.7kW
    continuous), so unless they have a constant critical load draw or
    the Fronius is massively oversized, you probably don't want to AC
    couple the Fronius. The 5048 is also able to output a continuous
    5000W only when it's cooler than 77F and it derates above that
    (4500W at 95F, for example). I don't believe its surge ratings apply
    to the AC2 output back into the utility but they probably wouldn't
    be enough, anyway. I think that whenever the Fronius output reached
    about 6000W, the SI would shift its frequency to switch the Fronius
    off. Cheapest may be along the lines of your first option-- not sure
    what the PV stringing is like but maybe you could move a string or
    two off the Fronius and put it onto a new Sunny Boy with an
    autoformer. Since I imagine this system doesn't have PV WIRE on the
    module leads or home runs, officially I'd recommend a classic Sunny
    Boy. Then leave the Fronius as-is. <br>
    <br>
    Unless of course the customer thought they were buying a system with
    the full 10kW supplying critical loads when the utility is down...
    then the original contractor is stuck with buying the second SI they
    should have installed in the first place.<br>
    <br>
    DKC<br>
     <br>
    <br>
    <div class="moz-cite-prefix">On 2014/7/3, 10:46, Mac Lewis wrote:<br>
    </div>
    <blockquote
cite="mid:CAOABG4-i5ahzH6_ea5oYqv3mW-9-d9yREjNb7BrwxK2WnLmscA@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hello wrenches,
        <div><br>
        </div>
        <div>I wanted to run this scenario by the forum.  I have spoken
          with SMA about this, but want some other opinions.</div>
        <div><br>
        </div>
        <div>We were recently contracted by a fellow solar company to do
          some warranty work for them out of town on a Sunny Island
          system that they had installed about 5 years ago.  It was VERY
          poorly implemented originally and was never installed as SMA
          intended.  In fact, during a small power outage, the only
          loads that never came back on after the utility was back on
          line were the loads in the critical load panel.  Oops. </div>
        <div><br>
        </div>
        <div>Anyway, our job is to get it working properly for the least
          amount of cost possible.  They have a Fronius IG Plus 10.0 fed
          into a 400A service panel.  The Sunny Island 5048 AC Input
          also comes off of this panel and feeding a 120V only critical
          load panel.  Please note that there is no solar fed into the
          AC output side of the Sunny Island, because there is not
          120/240 available and thus there is no possible way for this
          system to utilize the solar while the grid is not present.</div>
        <div><br>
        </div>
        <div>I see two options (but there may be more): pull out
          Fronius, put in Sunny Boy inverters and an autoformer, wire
          properly.  Another option is to add second Sunny Island and
          try to AC couple the Fronius with the two Sunny Islands.  The
          second option is less expensive overall, but I'm hesitant to
          rely on AC coupling with the Fronius.</div>
        <div><br>
        </div>
        <div>I'd appreciate any thoughts on this.</div>
        <div><br>
        </div>
        <div>Thanks</div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br clear="all">
          <div><br>
          </div>
          -- <br>
          <div><br>
          </div>
          <div><font color="#305A78" face="'times new roman', serif"><br>
            </font></div>
          <div><br>
          </div>
          Mac Lewis<br>
          <br>
          <span style="font-family:'Times New
            Roman';font-size:medium;color:rgb(255,153,0)"><b><font
                face="Arial, Helvetica, sans-serif" size="3">
                <p align="left"><font color="#000000" face="Verdana,
                    Arial, Helvetica, sans-serif"><span
                      style="font-size:small"><span
                        style="font-family:arial;font-weight:normal;color:rgb(48,90,120)"><font
                          face="'times new roman', serif">"Yo solo sé
                          que no sé nada." </font><span
                          style="font-weight:700;color:rgb(104,104,104)"><font
                            face="'times new roman', serif">-Sócrates</font></span></span></span></font></p>
              </font></b></span>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>