<div dir="ltr">Thank you to all who responded to this thread - particularly Jason/Dave/Jay for pointing out the maximum OCPD requirements.<div><br></div><div>Getting back to my original question.. I would like to use Dave's "extremely small subset" example of two SB5s operating at 277V. In this case, if we were to parallel the output of each inverter onto a 50A OCPD (#6 wire), could we downsize the wire to #10 from the split going back to each individual inverter? or would we be better served (required?) to run #6 all the way back to each unit? Since we are dealing with current-limited devices I would tend to think we can downsize but wanted to get Wrenches' feedback on this.</div>
<div><br></div><div>--</div><div>Corey Shalanski</div><div>Joule Energy</div><div>New Orleans, LA<br><div hspace="streak-pt-mark" style="max-height:1px"><img style="width:0px; max-height:0px;" src="https://mailfoogae.appspot.com/t?sender=aY3NoYWxhbnNraUBqb3VsZS1lbmVyZ3kuY29t&type=zerocontent&guid=4bec5788-9903-4ff4-8f92-031ee1997a9c"><font color="#ffffff" size="1">ᐧ</font></div>
<div class="gmail_extra"><br><br><div class="gmail_quote">On Fri, Jun 27, 2014 at 12:41 PM,  <span dir="ltr"><<a href="mailto:re-wrenches-request@lists.re-wrenches.org" target="_blank">re-wrenches-request@lists.re-wrenches.org</a>></span> wrote:<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">

<br>
Message: 5<br>
Date: Fri, 27 Jun 2014 11:32:02 -0400<br>
From: Dave Click <<a href="mailto:daveclick@fsec.ucf.edu">daveclick@fsec.ucf.edu</a>><br>
To: <a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a><br>
Subject: Re: [RE-wrenches] Combining Multiple Inverters<br>
Message-ID: <<a href="mailto:53AD8E72.4080009@fsec.ucf.edu">53AD8E72.4080009@fsec.ucf.edu</a>><br>
Content-Type: text/plain; format=flowed; charset=ISO-8859-1<br>
<br>
This is an interesting conversation, but I'm not sure it's going to<br>
really impact anything.<br>
<br>
When an inverter is listed, it is tested with some "maximum output<br>
overcurrent protection" as part of its rating per UL 1741. Typically<br>
inverter manufacturers set this to be just above the inverter's max<br>
current + 25%. As you know, many inverters can work at more than one<br>
voltage, so for the SB5s their max current ratings at 277/240/208V are<br>
18/20.8/24A, respectively. The max overcurrent protection is 50A. This<br>
figure often appears in the manual but not in the data sheet. For SMA,<br>
it's in the manuals. For some manufacturers, it's only available from<br>
tech support.<br>
<br>
For the Sunny Boy line, the only way you could have more than one<br>
inverter on a shared OCPD is if you have two SB5s operating at 277V<br>
(18.1A rated current each, so 2x18.1x1.25 < 50A). The SB6, SB7, and SB8<br>
all have currents too high to make this work, as they share the 50A max<br>
OCPD. The SB3/3.8/4 have a max OCPD of 30A, which is too low to<br>
double-up since each SB3 requires an OCPD of at least 20A. The TLs don't<br>
work either, as the max for any unit is too low. I don't see it in the<br>
SMA manual, but I know that in other manuals I've seen a manufacturer<br>
requirement for a dedicated OCPD. The only inverters I know of that have<br>
a max OCPD rating far beyond their rated current are micro-inverters.<br>
<br>
As for the shared disconnect, since at least the 2005, 690.15 has noted,<br>
"A single disconnecting means in accordance with 690.17 shall be<br>
permitted for the combined ac output of one or more inverters or ac<br>
modules in an interactive system." That being said, the NEC requires ac<br>
modules and micro-inverters to have ac disconnects (connectors,<br>
typically) per 690.6 and 690.15(A). 690.15 notes that an inverter be<br>
able to be disconnected from all sources, but if doubling up these SB5s<br>
you could argue that this shared disconnect accomplishes that via the<br>
anti-islanding protection... so I agree now that this is a grey area.<br>
<br>
Anyway, it comes down to whether it's worth worrying about this for what<br>
is an extremely small subset of compatible inverter configurations, when<br>
you can just do something like install a $50 Eaton BR24L70RP (70A bus,<br>
240V, 4 spaces) with two 30A breakers and be on your way.<br>